    why 6" above flood rim of highest fixture?
    hey tom, how goes it?

    I just completed my cast to pvc conversion of my attic reomodel. I did revent all my existing fixtures up so that they are 6" above the flood rim of my 2nd floor lav. My question is why? :confused: I can't seem to come up with a decent reason. Could you enlighten me? Also, I plan on using a studor vent on my attic lav, and from applications I heve seen, they are installed only a minimum of 6 inches above the tee. What gives?

    to sum up:

    1)why do the fixtures have to be revented 6 inches above flood rim of highest fixture?

    2)why doesn't this apply if I use a studor vent on that highest fixture?

    thanks again for all of you professional advise.

    louie
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Sep 6, 2005, 06:27 AM
    Quote Originally Posted by atticguy
    hey tom, how goes it?

    i just completed my cast to pvc conversion of my attic reomodel. i did revent all my existing fixtures up so that they are 6" above the flood rim of my 2nd floor lav. my question is why? :confused: i can't seem to come up with a decent reason. could you enlighten me? also, i plan on using a studor vent on my attic lav, and from applications i heve seen, they are installed only a minimum of 6 inches above the tee. what gives?

    to sum up:

    1)why do the fixtures have to be revented 6 inches above flood rim of highest fixture?

    2)why doesn't this apply if i use a studor vent on that highest fixture?

    thanks again for all of you professional advise.

    louie

    Good morning Louie, Welcome back, How did your attic installation go? I still have the diagrams that you sent me on file.
    I'll answer your questions in order.
    (1) )why do the fixtures have to be revented 6 inches above flood rim of highest fixture?
    Because Chapter 14,(Vents and Venting) Section 1406.3(Height above fixtures) of The Standard Plumbing Code says so. And Studor AAV manufacture agrees with them in their installation specs.
    (2)why doesn't this apply if I use a studor vent on that highest fixture? Where did you get this information from? It applies to all installations,
    (3)i plan on using a studor vent on my attic lav, and from applications I heve seen, they are installed only a minimum of 6 inches above the tee. What gives? That's the MINIMUM of 6 inches, the maximum can be as high as you wish. Where did you wish to install it?

    Plumbing codes are written to address the worst possible scenario. Lay it out on paper, if you left a open vent or revent below the water level in a fixture and since water will seek its own level you will get a backflow into the vent system.

    Good luck Louie and don't be such a strainger. Tom
    atticguy's Avatar
    atticguy Posts: 36, Reputation: 1
    Junior Member
     
    #3

    Sep 6, 2005, 08:31 AM
    Attic update
    "How did your attic installation go?"

    Reasonably well. After bracing about two feet of cast below my roofline, and removed a chunk of cast to the floor. I was then able to cut the cast right below the cast tee on the first floor which was a current revent. I then lifted the stack through the wall and into the attic, it wasn't as heavy as I would have thought. Sawzalled though all connections first though. My one hang up was cutting the sink vent. The vibration threw something out of whack and I ended up with a snapped drain-thankfully not inside the wall-! Always something eh? Then converted each vent to pvc and reconnected them to the main stack in attic. I still have to run the drain line for attic lav. That is what I'm hashing out now. It is stubbed out from the stack already.

    1) the attic sink will be vented via a studor vent, this studor vent, (which must be a min. of 6" from tee), must extend upwards until it is 6" above flood rim of the same sink that it is venting right?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Sep 6, 2005, 09:24 AM
    Quote Originally Posted by atticguy
    "How did your attic installation go?"

    reasonably well. after bracing about two feet of cast below my roofline, and removed a chunk of cast to the floor. i was then able to cut the cast right below the cast tee on the first floor which was a current revent. i then lifted the stack through the wall and into the attic, it wasn't as heavy as i would have thought. sawzalled though all connections first though. my one hang up was cutting the sink vent. the vibration threw something out of whack and i ended up with a snapped drain-thankfully not inside the wall-!. always something eh? then converted each vent to pvc and reconnected them to the main stack in attic. i still have to run the drain line for attic lav. that is what i'm hashing out now. it is stubbed out from the stack already.

    1) the attic sink will be vented via a studor vent, this studor vent, (which must be a min. of 6" from tee), must extend upwards until it is 6" above flood rim of the same sink that it is venting right?

    No! Go to the Studor web site , scroll to the bottom of the page and click on "installations". The Lavatory may be vented directly behind the trap under the cabinet. Cheers, Tom
    tanman's Avatar
    tanman Posts: 11, Reputation: 1
    New Member
     
    #5

    Sep 6, 2005, 01:46 PM
    How about loop vents?
    Hey Speedball,
    The schematics for loop vents used in island sinks break the 6" above highest floodline rule and I'm wondering if a loop vent can be applied to any other fixtures. How about a dishwasher that is not directly adjacent to a sink? Or a shower stall?

    Jason
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Sep 6, 2005, 02:29 PM
    Quote Originally Posted by tanman
    Hey Speedball,
    The schematics for loop vents used in island sinks break the 6" above highest floodline rule and I'm wondering if a loop vent can be applied to any other fixtures. How about a dishwasher that is not directly adjacent to a sink? Or a shower stall?

    jason
    A shower stall is usually found in a bathroom where it's wet vented by the lavatory vent so there would be no reason to install a loop vent and dish washers are usually found in the kitchen where a separate drain and vent aren't necessary. However I suppose that if no drain and vent were available you could enclose the dishwasher and install a drain with a loop vent. While it's true we aren't held to the 6" rule with loop vents you have to understand how they're put together. In a island sink loop vent the bottom of the loop is the drain and we set the "P" trap lower then usual while looplng up as high as we can in the cabinet with the return loop. When the sink drains it drains past the "P" trap and goes down into the lower drain pipe. The higher vent pipe is looped almost to the flood rim so unless there's a blockage the discharge never reaches the vent pipe. The loop prevents this from happening. While a lavatory with the vent installed below the flood rim will feed by gravity back into the vent when you drain a full basin. Hope this explains this to your satisfaction. Regards, Tom
    tanman's Avatar
    tanman Posts: 11, Reputation: 1
    New Member
     
    #7

    Sep 6, 2005, 02:42 PM
    I was just thinking about those fancy installations like a shower/tub in the center of a large bathroom or even a bedroom.

    Thanks for the reply... love this website.
    Jason
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #8

    Sep 6, 2005, 03:29 PM
    Quote Originally Posted by tanman
    I was just thinking about those fancy installations like a shower/tub in the center of a large bathroom or even a bedroom.

    thanks for the reply... love this website.
    jason
    While I've never done it that loop ventwould be the easiest since the drain's so low. Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Fan Blower not working in "ON" or "AUTO" in heat or AC [ 13 Answers ]

Got home from the Brewer game this afternoon and noticed the house was warm(78). Outside was 91. I checked the T-stat and it was set correct. Noticed the air vents weren't blowing anything. Went outside and the condenser and fan was running fine. Then I went downstairs to the furnace unit to see...

Hampton Bay outdoor flood light (motion/optical) [ 1 Answers ]

My HB flood lights stopped working recently, but if I turn the unit to "test", wave my hand in front of the sensor, the lights pop on. Turning it back to 1,5, or 10 minute timer delay does not work, even in the dark. Faulty opical sensor? Would that prevent the unit from operating in timer mode?

Flood Insurance [ 1 Answers ]

I was just informed that my mortgage company required me to have flood insurance. I was wondering if anyone know's what is the general fee more or less to get a elevation certificate. I just got a quote, just for flood was 2,800 not including the home insurance. I find it rather high. So I was told...


View more questions Search