    Grounding an Outlet
    I am moving into an older house that has only 2-prong outlets. Some are 3-prong, but they are not grounded (I have a power strip that tells you if it is gounded or not).

    I found this at Ace Hardware. http://www.acehardware.com/product/i...entPage=family

    How do I install it so that the outlet is properly gounded?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Jul 25, 2005, 07:15 AM
    The clamp is meant to go on a metal water pipe. You then run a wire from the screw on the clamp to a screw on the frame of the outlet. I can't say if such an arrangement meets code. You may find it helpful to look at this thread, https://www.askmehelpdesk.com/showthread.php?t=11184
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #3

    Jul 25, 2005, 08:25 PM
    That link helped. I'll take off my face plate and see if there is the other green screw on the end. If not, I'll try the 3 prong to 2 prong converter with the screw on the face plate acting as the ground. If this works or doesn't, I'll let you know.

    I should let you know that my surge protector has an indicator to which it is grounded.
    Here it is if you want to look at it: RCA surge protector (8 outlets, 2100 joules)
    Picture 1
    Picture 2
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #4

    Jul 26, 2005, 06:26 PM
    OK, the 3 prog to 2 prong grounded to the screw didn't work.

    There is a 3rd screw for grounding. There is a bare copper wire run to it.

    The electricity to the outlets is from a light in the ceiling.

    Could I run a wire from the third screw to the piece of wood it is on? (the box the outlet is in is metal, not plastic)?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Jul 26, 2005, 07:11 PM
    I don't quite understand. You can't ground a wire by screwing it to a piece of wood. As I explained it that other thread, in some older construction, there are 2 prong outlets installed in grounded metal boxes. You can just unscrew them and replace them with 3 prong ones. A metal box can have a ground wire attached to it, but if that wire is not grounded, the box and outlet will not be. You may be able to open the light fixture and connect existing ground wires. If not, you are back to the clamp on the water pipe. The clamp to the water pipe is one of the most reliable grounds, often added to eliminate interference in electronics.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #6

    Jul 26, 2005, 09:06 PM
    What could I run the ground wire to (other than a pipe) to ground it?
    kp2171's Avatar
    kp2171 Posts: 5,318, Reputation: 1612
    Uber Member
     
    #7

    Jul 26, 2005, 09:24 PM
    Labman is right
    Your choices are to connect it to the box (if the box is grounded), run a ground line to another nearby box that is grounded, or get it to a pipe that eventually runs into earth.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Jul 27, 2005, 06:44 AM
    I am sure the breaker box itself is grounded. It should have a buss with extra ground terminals. Once you take the cover off, both the ground and hot wires are exposed, be careful. The alternative is a ground rod driven deep into the ground where is is always damp. Likely there is already one outside where the electrical service entry is. You can also drill a hole in the basement or garage floor. Just be careful where, not over a drain or something.
    Press2Esc's Avatar
    Press2Esc Posts: 251, Reputation: 10
    Full Member
     
    #9

    Jul 27, 2005, 07:19 AM
    Labman,

    How do you know the outlet boxes are grounded? Have you measure them with an ohm meter? If it measures a zero ohms (short) - they are grounded. 2-wire or 3-wire plugs, in older homes are not typically grounded. Of course, depending on your access (e.g. crawl space, attic, wall fish, etc), if you or your electrician has enough access an outlet to be able to ground it, doesn't it make sense to run a new 3 conductor wire back to the main breaker box for code and safety reason??

    Be forewarned, with the heavy of usage of PVC through the years, grounding of water pipes is no guarantee. If you check your electrical service entry point, you will likely see a nearby ground rod. This is your earth ground for your house & main electrical panel...

    P2E

    Quote Originally Posted by labman
    I don't quite understand. You can't ground a wire by screwing it to a piece of wood. As I explained it that other thread, in some older construction, there are 2 prong outlets installed in grounded metal boxes. You can just unscrew them and replace them with 3 prong ones. A metal box can have a ground wire attached to it, but if that wire is not grounded, the box and outlet will not be. You may be able to open the light fixture and connect existing ground wires. If not, you are back to the clamp on the water pipe. The clamp to the water pipe is one of the most reliable grounds, often added to eliminate interference in electronics.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #10

    Jul 27, 2005, 03:23 PM
    I'll check the fuse box (don't have breakers). I do not have an ohm meter to check the outlet. I do not know if the outlet box is grounded. It is attached to wood.

    I won't be posting again until Monday, April 1.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #11

    Jul 27, 2005, 04:16 PM
    If a metal box is grounded one way or another, an outlet screwed to it is grounded. If the surge protector isn't grounded when plugged in, neither is the box.

    You haven't said how old the older house is, or if you are buying or renting. In the other thread, m3rdpower is stuck in a poorly wired rental. My son had that problem too. If you own the house, and it is old enough to have fuses and metal boxes, it may be easier to retro fit proper grounds. A grounded outlet is literally that, having a conductive path from the frame of the outlet to damp ground with unlimited electrons. In modern construction, it is usually actual wires back to the breaker box connected to a rod going deep into the ground. In the past, it was often metal conduit or flex back to the box. Unfortunately for a while houses were wired up with non metallic wire without the third wire for grounding. After enough houses burn down or people are electrocuted, they tighten the code. Where they used plastic boxes and stapled the NM cable inside the wall, updating is a pain.

    You need to figure out what you have and how much work you want to do, Could be as simple as connecting wires that are already there. To do it right, you could have to run new cables. As long as the surge protector indicates whether the outlet is properly grounded, you shouldn't need to do other checking. It is easy enough to do with even a $5 multimeter.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #12

    Jul 27, 2005, 06:32 PM
    The house is 48 years old. I own the house now.

    I know what you are talking about with the newer houses and driving a metal stake deep into the ground, I have seen what this looks like.

    I'll see if the fuse box is grounded.

    I will not be posting again until Monday, April 1.
    Press2Esc's Avatar
    Press2Esc Posts: 251, Reputation: 10
    Full Member
     
    #13

    Jul 31, 2005, 04:26 AM
    Quote Originally Posted by nubuilder
    The house is 48 years old. I own the house now.

    I know what you are talking about with the newer houses and driving a metal stake deep into the ground, I have seen what this looks like.

    I'll see if the fuse box is grounded.

    I will not be posting again until Monday, April 1.
    hmmm, no big hurry nubuilder... get back to it whenever you can & just enjoy your "little" break.. :D
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #14

    Aug 3, 2005, 05:23 PM
    How do I tell if the fuse box is grounded?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #15

    Aug 3, 2005, 07:06 PM
    If you have a meter or a test light, remove a fuse and see if you have 115 volts between the center contact for the fuse and the metal of the box. I would be very surprised if you don't.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #16

    Aug 4, 2005, 04:25 PM
    I do not have any testing equipement. All I have is a AA, AAA, C, D, and 9V tester for my batteries and my power strip with the indicator on it (see the 3rd post on P.1).

    What could I use as a test light, or what is a test light?

    (F.Y.I.-I tried the power strip on a 2 prong outlet in the living room with a 3 prong to 2 prong converter, and it said it was grounded.)
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #17

    Aug 4, 2005, 04:46 PM
    Quote Originally Posted by nubuilder
    I do not have any testing equipement. All I have is a AA, AAA, C, D, and 9V tester for my batteries and my power strip with the indicator on it (see the 3rd post on P.1).

    What could I use as a test light, or what is a test light?

    (F.Y.I.-I tried the power strip on a 2 prong outlet in the living room with a 3 prong to 2 prong converter, and it said it was grounded.)
    I would trust your power strip and declare the problem solved.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #18

    Aug 4, 2005, 06:11 PM
    No this is not solved. The outlets in the LIVING ROOM were grounded, but they were put in many years ago.

    The wiring in the basement room was done long after the house was done, maybe 20 to 25 years ago. The outlets have the third prong (unlike the original wiring).

    I'll try it again in the basement again tomorrow. Let you know tomorrow in the afternoon.
    nubuilder's Avatar
    nubuilder Posts: 20, Reputation: 1
    New Member
     
    #19

    Aug 5, 2005, 12:20 PM
    LIVING ROOM
    I have a 3 to 2 prong converter on it. When I only had 2 prong things plugged in, it said it wasn't grounded. When I plugged a 3 prong item into it, it instantly said it was grounded.

    BASEMENT
    The outlets in the basement are 3 prong. I plugged in the power strip (with no adapter) and it said it wasn't grounded, but as soon as I plugged in something with 3 prongs, it said it was grounded.

    As soon as I plugged it in at my friends house (which is only 20 years old), it said it was grounded and nothing was plugged into it.

    Can anyone explain this to me?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #20

    Aug 5, 2005, 01:03 PM
    At the moment, it doesn't make any sense to me. It really isn't safe living in a house that doesn't have properly grounded outlets. As I have indicated, it can be fairly easy to retrofit grounds depending on the details of the original wiring. If you are going to try to do the work yourself, you will need to pick a few basic tools, a test meter at least. The voltage probes are faster and safer for many trouble shooting uses. I wouldn't trust that outlet strip.

    Your other alternative, perhaps expensive, is to have an electrician do the work.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Grounding Bar vs. Neutral Bar? [ 14 Answers ]

Hello all. I have extended the wires from an unused 240 outlet to the backyard for a spa via a sub-panel. I also hooked up a new grounding electrode near it to avoid having to run a fourth wire all the way back to the main panel. This fourth wire goes to the small grounding bar in the sub-panel...

Generator grounding [ 5 Answers ]

I just bought a 4400/3500 watt generator for a building project. The directions say that I need to ground the generator with a suitable grounding rod and stranded No. 12 AWG wire. I have never heard of contractors grounding their generators. Are they being careless, or are my generator...

Where to install a Grounding Rod [ 14 Answers ]

My house is about 20 years old and I do not have a grounding rod installed. Although all the wiring is grounded to the water pipes, I would still like to install one. My question is how close or far from the main electrical box should the grounding rod be installed? On on the other side of the...

Detached garage grounding rod or not [ 1 Answers ]

Hi, I just ran across another problem. I will be running 40 amps 240 volts out to my garage via underground 8-3 plus ground. Do I need a grounding rod at the garage or is the ground via the service cable to the garage enough? I have seen both and am not sure why. Is the 240 volt service to the...

Help - What to do with the Grounding Wires [ 5 Answers ]

Because of brown waters, I want to re-run the hot/cold water pipes for the entire house. But there is one major problem, the existing galvanized pipes had some grounding wires attached to them and I'll plan to use the PEX pipe. I have no ideas how to run the new grounding wires when I take out...


View more questions Search