    ICM271 Carrier Replacement board Fuse blows
    My Furnace recently stopped working and the Furnace Fan stayed on constantly. I replaced the original Fan Control circuit board (HH84AA011) with a ICM271 drop in replacement board. Still nothing came on, not even the constant fan. I check the 120V-24V transformer and found no 24V output so I replaced the transformer. Now when I turn it on the 3AMP fuse blows instantly and the fan comes on (I understand this is a normal function of the board if the fuse blows). If I temporarily bypass the fuse nothing happens. I was told to suspect the Limit switch. Any other ideas?
    One limit switch wire (red) has a component wired into it. (i.e. wire-component-connector-limit switch terminal) any idea what this is and if it is necessary?

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 6, 2007, 01:34 PM
    All parts are necessary for safety. It sounds like you have a short in the low voltage wiring and if I were you I would check to make sure all of that low voltage wiring is OK and not shorted before I would do anything else.

    You have already spent some$$ trying to fix this and if the wiring does not show the problem I would contact a professional before you cause more $$ to be spent guessing at what the proble is.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Jul 6, 2007, 07:41 PM
    I don't think the problem is the limit switch, you may have ruined the transformer by jumpering it out. Unplug furnace.In order to find your short or ground I suggest you disconnect the low voltage wiring to the thermostat at the board in the furnace (small wires connected with screws)Replace transformer and fuse then plug furnace in at wall receptacle , hold door switch in manualy, while monitoring the amp draw with a amp meter around each thermostat wire, reconnect wire ,one at a time starting with the "C" (common) Then the "R" then the rest. As you reconnect you will find the circuit that is shorted. If it is the yellow wire it is possibly the contactor coil in the condensing unit, if it is the white wire, it is possibly in the heating componets (gas valve, combustion blower controls, etc.)Remember the amp draw should be around 1.0 amps or less.
    You can also trouble shoot without a amp meter by watching for the fuse to blow. (make sure you have plenty of fuses)
    The problem may also be at the thermostat, if you have a common wire to the stat it may be touching one of the other wires.
    Then there is the possibility that the thermostat wires are shorted together between the furnace , stat or condensing unit which can be checked with an ohm meter when the furnace is unplugged.
    I hope this helps, Mike.
    FirmwareDeveloper's Avatar
    FirmwareDeveloper Posts: 2, Reputation: 1
    New Member
     
    #4

    Jul 9, 2007, 08:09 PM
    Thank you for your responses, I appreciate it.

    I have check the continuity of all wires I have access to with an ohm meter and they all seem OK. My transformer is good (120V in 24V out). I did the 1 wire at a time troubleshooting and found that the fuse only blows when BOTH the yellow (from thermostat) and the Dark Green (from the outside condensing unit ) are connected together at the Y terminal on the circuit board. Does this also indicate the contactor coil?
    Yellow alone or Green alone do not cause a problem.

    Thanks again
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #5

    Jul 9, 2007, 08:44 PM
    The coil in the contactor is most likely the problem, it is probably burnt out. Check the wires (low voltage ) out side to make sure they are not bare and shorting out . A lot of times a dog will chew on them and short them out. Mike

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Turning on AC blows control board fuse and 24v transformer [ 15 Answers ]

I read https://www.askmehelpdesk.com/heating-air-conditioning/c-keeps-blowing-fuse-95884.html which was very informative. My issue is with a Carrier Weathermaster 8000 furnace and York AC. The heat works fine, the fan only works fine, I turn on the AC and the LED blinks code 34. I replace the...

Turning on A/C blows 3amp fuse on circuit board [ 1 Answers ]

Hi, Hope someone can help me. As stated in the title, when ever I turn the a/c on it blows the 3 amp fuse on the board. The system works fine with heat on. It's only when I activate the a/c does it burn. I have no idea what is causing the fuse to blow. Does anyone have any ideas of where I can...

Goodman controller board fuse blows [ 8 Answers ]

I have a Goodman GMPN120-5, service guy replaced PCB in Aug due to A/C failure, root cause unkknown or not documented. Last week I turned on heat for first time this season, now nothing runs. Service guy returned, located blown 3A PCB fuse, replaced, still blows. Replaced fuse with 5A for testing...


View more questions Search