I don't think the problem is the limit switch, you may have ruined the transformer by jumpering it out. Unplug furnace.In order to find your short or ground I suggest you disconnect the low voltage wiring to the thermostat at the board in the furnace (small wires connected with screws)Replace transformer and fuse then plug furnace in at wall receptacle , hold door switch in manualy, while monitoring the amp draw with a amp meter around each thermostat wire, reconnect wire ,one at a time starting with the "C" (common) Then the "R" then the rest. As you reconnect you will find the circuit that is shorted. If it is the yellow wire it is possibly the contactor coil in the condensing unit, if it is the white wire, it is possibly in the heating componets (gas valve, combustion blower controls, etc.)Remember the amp draw should be around 1.0 amps or less.
You can also trouble shoot without a amp meter by watching for the fuse to blow. (make sure you have plenty of fuses)
The problem may also be at the thermostat, if you have a common wire to the stat it may be touching one of the other wires.
Then there is the possibility that the thermostat wires are shorted together between the furnace , stat or condensing unit which can be checked with an ohm meter when the furnace is unplugged.
I hope this helps, Mike.
|