New Member
|
|
Jun 20, 2007, 09:32 PM
|
|
Questions about house with aluminum wiring
I have recently purchased a home with what appears to be 80% aluminum wiring. The outlets and switches all worked fine, but were not rated for aluminum use. Prior to purchasing the home I spoke with my insurance agent and she indicated they would need a certificate of inspection from our local electrical inspection office. So I spoke with the inspector and he instructed me to A) replace all outlets and switches with aluminum rated ones or B) pigtail copper to the aluminum using aluminum/copper marettes and use nolox compound. So I choose to do B as it was much less expensive, although we also put in brand new switches and outlets at the same time. Also replaced all the light fixtures. Passed the inspection no problem.
Two problems I am noticing:
1 - almost all of the switches have an "arcing" noise when flipped. If I hold the switch in that middle position between on and off you can hear it on almost all of them. Ive rechecked the connections and they are all very tight at both the switch and marette. Is this likely coming from the pigtail (copper and aluminum) or from the switch itself? Could it be bad switches? Seems very odd that this happens with almost all of them.
2 - I put in some ceiling fans also and one of them has a dimmer on it. I know you aren't supposed to use dimmers with aluminum, but I assume this is OK if I have it pigtailed to copper? When the light is dimmed there is a constant low volume buzzing noise coming from the fan. Is this normal?
Thanks for any advice...
|
|
 |
Senior Member
|
|
Jun 20, 2007, 11:07 PM
|
|
--->Try buying better quality switches. May want to buy one first, hook it up, and record the results.
---> Rid the Fan dimmer control, and try a set speed fan control.
Wait for others to comment!
|
|
 |
New Member
|
|
Jun 21, 2007, 06:12 AM
|
|
 Originally Posted by Washington1
--->Try buying better quality switches. May want to buy one first, hook it up, and record the results.
---> Rid the Fan dimmer control, and try a set speed fan control.
wait for others to comment!
So it could be cheap switches? Is it a safety hazard? The switches are the 10 packs from Home depot.
For the fan - it's the light that dims and causes the noise when dimmed, not the fan. The light and fan is controlled via remote. Im not sure what you mean by a set speed fan control.
Thanks
|
|
 |
Senior Member
|
|
Jun 21, 2007, 06:07 PM
|
|
You know what. I wrote a response--took me twenty minutes, and the damn computer shut down, so I lost all that time, and work. I want be re-writing what I wrote.
Real quick:
The hum is normal because the filament is vibrating when you reduce the voltage. All filaments vibrate at certain frequencies, and at times you will hear it. Try a better quality bulb first. Pick up a 130v bulb from the electrical supply house, and see what happens. The remote may be causing interference as well, but lets try the bulb first, then go from there.
Cheap switches: try buying a Pass and Seymour switch (just buy one), and see if this works. If you want to use Leviton, then use a commercial grade switch instead of your 50-70 cents switch.
Sorry, I wrote more than this last time, but I lost it. Get back to us once you've tried the above.
|
|
 |
New Member
|
|
Jun 22, 2007, 05:43 AM
|
|
 Originally Posted by Washington1
You know what. I wrote a response--took me twenty mins, and the damn computer shut down, so I lost all that time, and work. I want be re-writing what I wrote.
Real quick:
The hum is normal because the filament is vibrating when you reduce the voltage. all filaments vibrate at certain frequencies, and at times you will hear it. Try a better quality bulb first. Pick up a 130v bulb from the electrical supply house, and see what happens. The remote may be causing interference as well, but lets try the bulb first, then go from there.
Cheap switches: try buying a Pass and Seymour switch (just buy one), and see if this works. If you want to use Leviton, then use a commercial grade switch instead of your 50-70 cents switch.
Sorry, i wrote more than this last time, but I lost it. Get back to us once you've tried the above.
Thanks - I will try that. Curious though if the "arcing" noise in the switches is a safety hazard/concern or just an annoyance?
|
|
 |
Senior Member
|
|
Jun 22, 2007, 07:56 AM
|
|
If I hold the switch in that middle position between on and off
I just notice this. If you do this, any switch will arc, because you are creating an air gap. If the switch isn't arcing when in "normal" operation, then you should be fine. It's a safety hazard if you are intentionally causing it to arc (may be putting pit holes in the contacts).
|
|
 |
New Member
|
|
Jun 22, 2007, 08:01 AM
|
|
 Originally Posted by Washington1
I just notice this. If you do this, any switch will arc, because you are creating an air gap. If the switch isn't arcing when in "normal" operation, then you should be fine. It's a safty hazard if you are intentionally causing it to arc (may be putting pit holes in the contacts).
Yeah they only do this while being turned on or off, not while fixed in the on or off position. So this is OK then? Ive never noticed this in my other homes, so I thought it might be cause for concern?
|
|
 |
Senior Member
|
|
Jun 22, 2007, 08:19 AM
|
|
If you are turning the switch on and off--switching normally (meaning, not trying to switch it slow, or balance the toggle in the middle), then you should "not" be getting arcs. If you do, then you need to buy better switches.
Another reason for causing an arc in the switch, would be the load you are placing on the switch. (I'm sure this doesn't count in your situation)
|
|
 |
Uber Member
|
|
Dec 21, 2007, 11:55 PM
|
|
Fans are not supposed to be used with dimmers it is a fire hazard.
|
|
 |
Senior Member
|
|
Dec 22, 2007, 11:59 PM
|
|
Ceilingfan,
OP said this:
it's the light that dims and causes the noise when dimmed, not the fan.
Washington said:
The hum is normal because the filament is vibrating when you reduce the voltage. All filaments vibrate at certain frequencies, and at times you will hear it. Try a better quality bulb first. Pick up a 130v bulb from the electrical supply house, and see what happens. The remote may be causing interference as well, but lets try the bulb first, then go from there.
Cheap switches: try buying a Pass and Seymour switch (just buy one), and see if this works. If you want to use Leviton, then use a commercial grade switch instead of your 50-70 cents switch.
Sorry, I wrote more than this last time, but I lost it. Get back to us once you've tried the above
and this:
Rid the Fan dimmer control, and try a set speed fan control.
|
|
 |
Uber Member
|
|
Dec 23, 2007, 12:01 AM
|
|
Sorry, I didn't see those replies. My apologies.
|
|
 |
Senior Member
|
|
Dec 24, 2007, 11:00 PM
|
|
No problem!
Have a Merry Christmas!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Receptacles and Aluminum Wiring
[ 7 Answers ]
I wish to add GFCI outlets to make my kitchen outlets safer for me and my family. I have aluminum wiring in my house, but I couldn't find CU/AL rated GFCI outlets at the store.
I'd like to know which is a safer option: reguler outlets in the kitchen that are CU/AL rated or GFCI outlets that are...
Thermostat wiring questions
[ 2 Answers ]
- White-Rogers type 1E50W-341 manual mercury thermostat with Fan auto/on switch.
- 4 wiring terminals on thermostat (G - R - W - Y)
- 3 wires coming from wall (red - green - black).
- want to install new Noma programmable thermostat
- disconnected old thermostat and (like an idiot) did not...
Spa wiring questions
[ 4 Answers ]
I recently purchased a hot tub (spa). It calls for 6-3 with ground 240 volt 50 amp gfci breaker installed. I have almost completed the job and have some questions. I installed a 50 amp breaker in a subpanel in my laundry room and ran the 6-3 wire with ground down in the crawl space out to the...
Addition wiring questions
[ 6 Answers ]
Greetings all,
I am finishing up an addition to my house. With winter fast approaching, I want to get the electrical done and inspected before the snow flies. (This is pretty long,but, I want to make sure that I do it right before the inspector comes out.
For some background info:
I...
View more questions
Search
|