    Upflush toilet venting
    I am in the process of finishing my basement and decided to use a Saniflo Saniplus macerating pump unit for lifting wastewater from a sink, toilet, and shower into the existing 4 " drain line (the 4" drain exits the basement approximately 4' from the basement floor). The force main is the easy part, since the drain line runs directly above the new pump unit, but there is no convenient vent stack available to tie a vent line into. Are there venting alternatives (Saniflo says that cheater vents won't work since the unit needs two-way air flow)?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Nov 2, 2005, 01:06 PM
    Sanaflo's correct. Unlike your house vent system a holding tank vents both ways. Out when a fixture discharges into it and in when the pump lifts it up to the main. You must vent the tank but you do have options. You can run a vent out the roof or up and revent into a existing dry vent at least 6" over the flood rim of the highest fixture. Another option would be to exit out the basement and run up the side of the building a ways. However there are limitations.
    You must not terminate them under a window, door or any ventilation system, or within 10 feet of such openings unless it's at least 2' above such opening. The vent terminal shall be screened and slope back to the tank at 1/8th to 1/4" to the foot. (Chapter 14, Section 1404.4 of the Standard Plumbing Code) good luck, Tom
    lstaley34's Avatar
    lstaley34 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 2, 2005, 01:34 PM
    Thanks for the very fast reply.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why is toilet venting shown in UPC unacceptable? [ 1 Answers ]

I was looking at "various methods for venting toilets" in excerpts from the UPC ( http://www.masterplumber.com/Laws/UPCExcerpts.html#ventexceptions).The last configuration shown is labeled as not allowed. It has both the vertical vent pipe and the vertical toilet discharge pipe connnecting to a...

Need some help with venting, moving toilet adding bath [ 9 Answers ]

I am moving my toilet to the other side of the bathroom, and adding a tub. My bathroom is very small 5' X 7' and I only have one existing vent. The vent is 2" in the wall and is 3" coming out of the roof. Anyway, I was wondering if this piping plan would work, or if someone has a better way to do...

Standalone toilet venting (hypothetical)? [ 1 Answers ]

If only a toilet were drained from a dwelling to a sewer/septic would it need to be vented according to code or otherwise for safety?

Question about toilet venting [ 9 Answers ]

Hello all! I stumbled upon this forum... what a godsend! Anyway, here's a question for the plumbing experts. I have two bathrooms, each with one toilet and one sink. All four of these items are vented through a single 2" pipe up to the roof. I've been having a bit of trouble with the...

Toilet/Shower - Venting [ 1 Answers ]

I am remodeling 2 bathrooms into one. I am moving a few things around, but my question is. I had a 3" vent that went up a wall in between the 2 bathrooms, well I had to do away with it. It was at the end of the line of the rough in and 2 toilets were connected right near it. My question, there...


View more questions Search