    Solid lit Red LED on terminal strip of honeywell R8184G4009
    We have a forced hot water heating system with Beckett Oil Burner, and
    Honeywell R8184G4009 intermittent ignition oil primary. The honeywell ignition
    Is about 3 years old and the heating system is 20 years old. Today, we noticed that
    The furnace is not turning on. When I went down to the basement to look at the
    Heating system, I noticed that the Red LED on terminal strip of honeywell R8148G
    Is on (solid). I pressed the red button on R8148G to reset the system. The heating
    System worked for about 10-20 minutes, then it stopped. When I went down
    To the basement, I found the Red LED turned on again (solid). I decided not
    To press the reset button the 2nd time, and ask the question here. What can be wrong?
    When the system turned on for the 20 minutes after I did the 1st reset, the
    Heat coming out of the radiators seemed to have been fine. Although, I noticed
    The temp gauge on the heating system read 200 degF, which I thought was a
    Bit higher than usual. Our system was always around 180-190 degF. And I also
    Noticed that there was some water stain under the copper pipes that is connected
    To the safety valve. We also thought that we could smell very light oil ordor
    In the basement.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 28, 2009, 01:55 AM
    What can be wrong?

    The burner safety control is telling you that the burner is not operating correctly. This is why the control is tripping and the reason you might smell a slight oil odor. Call for On Site Service of your boiler to have this problem corrected and in the mean time STOP hitting the reset control.
    abcsalem's Avatar
    abcsalem Posts: 70, Reputation: 2
    Junior Member
     
    #3

    Nov 6, 2009, 09:35 AM
    Thank you for your reply. I knew hitting the reset button more than once wouldn't be good. So I only hit it once, and when the furnace shutdown after 10 minutes, I called the furnace service technician. It turned out that, our oil filter needed to be changed. He charged $152 to do the service.

    The service technician also mentioned that, the pressure regulator valve and the safety valve, are the originals (20 years old) and both needs to be replaced. He said the pressure is at 15 pounds, it should be 18 pounds, and the safety valve is weeping. He gave us an estimate of $300 to replace both valves. I thought I could do this work myself.

    Any suggestion on what the steps are to replace both valves? Our furnace is oil system with forced hot water. I assume, I need to shutoff the furnace first, then shutoff water to the house, and start draining the furnace. Also after installing the pressure regulator, how one would set the pressure to the correct value? Are the pressure regulator valves set to a certain settings at the factory or the technician that is installing it needs to set that on site after the installation is complete?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 6, 2009, 06:15 PM
    The safety valve is preset so just get one that matches the old one exactly. The water inlet pressure regulator that automatically fills the boiler can be adjusted so look at the directions that come with the valve.

    Yep 8.00 oil filter cartridge and the rest in service call and labor. That is about right.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Male strip clubs v.s women's strip clubs [ 42 Answers ]

EXCUSE THE TYPO: "MALE"strip clubs NOT "MAKE" strip clubs Here's just a general question for the women... Are women really turned on by muscular, sweaty greasy men in thongs with hard ons or a banana in their pants?? Or is this just entertainment to pas the time? I went to a bachelorete party this...

Chronotherm IV Plus stuck terminal [ 5 Answers ]

I'm trying to install a Honeywell Chronotherm IV Plus (T8624D2004) on a conventional residential system: gas warm air furnace & A/C (both single stage). The wiring is pretty standard: red - R/RC; white - W1; yellow - Y1; green - G and a common wire from the other side of the transformer - C; unused...

Three terminal lamp socket [ 1 Answers ]

I need a wiring diagram for a three terminal lamp socket. It will light a night light in the lamp base or light the main lamp or light both the top and the bottom.

Sister is Terminal and I Don't want to See her [ 15 Answers ]

My sister has a brain tumor. This was diagnosed 7 years ago. She went in for a biopsy, finally, yesterday. It didn't go well and she is in critical condition. However, she will probably live. No one knows how long. She seems stable, per the hospital this AM. I am getting major pressure...

No RC terminal on new thermostat? [ 8 Answers ]

Hello: I saw your name on an internet search for thermostat wiring problems, so I thought I would try you for this one. I could not get help elsewhere. I have an oil burner, and a separate a/c unit. I installed a programmable thermostat 2 years ago that works well, although the location is...


View more questions Search