    Conduit Sizing and Wire Type
    Hi folks,

    The application here is to get power to a landscape area (4'x4') for decorative lighting purposes. The overall landscape design calls for up to five of these areas to be lit - at some point. The furthest one from the house will be 300 ft. I'm looking for least expensive recommendations on:

    1. what size, type, and depth of conduit
    2. what size and type of line
    3. configuration of the drops - i.e. is it possible to ultimately support 5 in a daisy-chain fashion off one line from the house

    Thanks,
    MMD
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #2

    Apr 18, 2008, 07:25 PM
    You may use type UF cable for direct burial... you don't need to use conduit... 300 feet? Use #12 Type UF.
    buzzman's Avatar
    buzzman Posts: 54, Reputation: 9
    Junior Member
     
    #3

    Apr 18, 2008, 08:13 PM
    See also notes from "Handyman2007". The depth is usually a foot and a half (18") if installed around foot traffic only. Go three feet (36") if installed across a vehicular traffic area. You can install up to 12 outlets (lights in this case) off one 15Amp branch circuit legally. Five is more than legal.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #4

    Apr 19, 2008, 03:25 PM
    You can install up to 12 outlets (lights in this case) off one 15Amp branch circuit legally. Five is more than legal.
    Buzzman,
    If I'm reading you correctly. You are saying we aren't allowed to have more than 12 lighting outlets on a 15A circuit. Can you explain this, with code references and maybe even a sample calculation?
    buzzman's Avatar
    buzzman Posts: 54, Reputation: 9
    Junior Member
     
    #5

    Apr 19, 2008, 04:18 PM
    Quote Originally Posted by Washington1
    Buzzman,
    If I'm reading you correctly. You are saying we aren't allowed to have more than 12 lighting outlets on a 15A circuit. Can you explain this, with code references and maybe even a sample calculation?
    This is based on CEC (Canadian Electrical Code). I can only help you based on this. The US can be very different, and it can change from state to state due to the dynamics of its geographics (Cold/Dry to Hot/Humid). There are specific hazards that can exist due to these climatic conditions. You will have to check with your local codes, but at least you know what to ask and how to ask it. To explain myself, 12 total outlets mean a combination of either lights receptacles or both in ONE 15A branch circuit. Switches to don't count as an outlet, because it is not a load (Only in Canada).
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #6

    Apr 21, 2008, 04:04 PM
    The OP is from Canada?

    How can you tell?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Apr 21, 2008, 05:46 PM
    Buzz, a better way of putting it would be "In MY AREA you can install up to 12 outlets (lights in this case) off of one 15Amp branch circuit legally.", as opposed to just stating this as fact without explanation. This is a very local code and is NOT very common.


    Also, WHY would you say conduit is a waste of time and money?? Have you EVER seen rocky soil conditions??
    There are places I wouldn't hesitate to use direct burial cable, and other's I wouldn't even think about it.
    buzzman's Avatar
    buzzman Posts: 54, Reputation: 9
    Junior Member
     
    #8

    Apr 21, 2008, 06:19 PM
    Quote Originally Posted by stanfortyman
    Buzz, a better way of putting it would be "In MY AREA you can install up to 12 outlets (lights in this case) off of one 15Amp branch circuit legally.", as opposed to just stating this as fact without explanation. This is a very local code and is NOT very common.


    Also, WHY would you say conduit is a waste of time and money???? Have you EVER seen rocky soil conditions???
    There are places I wouldn't hesitate to use direct burial cable, and other's I wouldn't even think about it.
    In that case I would use teck cable... Armored cable...
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #9

    Apr 21, 2008, 06:51 PM
    Quote Originally Posted by buzzman
    In that case I would use teck cable......Armored cable...
    Seeing that most have no idea what TECK cable is (at least I believe most from the US--I being from the US, and had to give this same information to another person from Canada), here is a brief presentation--compliments of Thomas and Betts:

    Teck Cable Specifications
    The Teck cable name is derived from one of
    the first users, the Teck-Hughes Gold Mines
    in Kirkland Lake, Ontario. Teck 90 is the CSA
    Type designation. The trade designation is
    Armored Cable.
    Teck cables with a working potential up to 5,000
    volts are manufactured in accordance with CSA
    Standard C22.2 No. 131. The cables are provided
    with a bare ground conductor and an optional
    outer jacket. Depending on the phase conductor
    insulation, the cables are designated as Teck
    90 (X-LINK) when the insulation is cross-linked
    polyethylene, and Teck 90 (EP) when it is ethylene
    propylene. Both cable types are rated for 90°C
    service (dry location) and 75° C (wet locations).
    When Teck cable is suitable for installation at a
    temperature down to minus 40° C, it is marked
    “Teck 90 (X-LINK) Minus 40” or “Teck 90 (EP)
    Minus 40”.
    Teck cable with a working potential over 5,000
    volts is manufactured in accordance with IPCEA
    standards and is certified by CSA. Cables are
    provided with or without ground wire, as required.
    Teck cable with an outer jacket may be used
    for exposed or concealed wiring in wet or dry
    locations, indoors and outdoors, and in
    corrosive environments. It is suitable for use in
    ventilated, non-ventilated and ladder type cable
    troughs, and in ventilated flexible cableways in
    both dry and wet locations. It is also suitable for
    direct earth burial and for Class II, Division 2; and
    Class III, Divisions 1 and 2 hazardous locations,
    as per the Canadian Electrical Code.
    Flexibility and ease of installation are key
    features of Teck cable. The absence of dead air
    space within the cable increases heat transfer
    and minimizes condensation. The overall
    protective covering provides good environmental
    protection.
    Bend radii for permanent training during installation
    usually varies between 7 to 12 times the cable
    diameter, depending on the construction of the
    cable and the manufacturer's recommendations.
    Larger radii bends are required for other conditions.
    Electrical Code Requirements
    Section 12-3024 of the Canadian Electrical Code
    requires that the terminating fittings used must
    provide adequate strain relief to terminal connections
    and ensure electrical continuity without
    injury to the nonmetallic sheath. Continuity is
    mandatory whether the armour is used as
    a grounding conductor. Except for dry locations
    that are free from corrosive atmosphere, the
    nonmetallic jacket cannot be stripped back to
    the point where the armour is exposed after
    installation.
    Where single conductor cables carrying 200 amps
    or more enter metal boxes through separate
    openings, certain precautions are required
    to prevent overheating of the metal by induction.
    Use of nonferrous or nonmetallic box fittings,
    locknuts and bushings and installation of nonmagnetic
    panel inserts is suggested in the code.
    Please refer to the following for further details
    and complete information:
    1. CEC Section 12, Wiring Methods; CEC
    Section 4, Conductors
    2. CSA C22.2 No. 131 and 131S (Supplement
    #1), Safety Standard for Type Teck Cable
    3. CSA C22.2 No. 18, Safety Standards for
    Outlet Boxes, Conduit Boxes and Fittings
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #10

    Apr 21, 2008, 08:21 PM
    :eek:
    buzzman's Avatar
    buzzman Posts: 54, Reputation: 9
    Junior Member
     
    #11

    Apr 21, 2008, 08:36 PM
    Quote Originally Posted by Washington1
    Seeing that most have no idea what TECK cable is (at least I believe most from the US--I being from the US, and had to give this same information to another person from Canada), here is a brief presentation--compliments of Thomas and Betts:

    Teck Cable Specifications
    The Teck cable name is derived from one of
    the first users, the Teck-Hughes Gold Mines
    in Kirkland Lake, Ontario. Teck 90 is the CSA
    Type designation. The trade designation is
    Armored Cable.
    Teck cables with a working potential up to 5,000
    volts are manufactured in accordance with CSA
    Standard C22.2 No. 131. The cables are provided
    with a bare ground conductor and an optional
    outer jacket. Depending on the phase conductor
    insulation, the cables are designated as Teck
    90 (X-LINK) when the insulation is cross-linked
    polyethylene, and Teck 90 (EP) when it is ethylene
    propylene. Both cable types are rated for 90°C
    service (dry location) and 75° C (wet locations).
    When Teck cable is suitable for installation at a
    temperature down to minus 40° C, it is marked
    “Teck 90 (X-LINK) Minus 40” or “Teck 90 (EP)
    Minus 40”.
    Teck cable with a working potential over 5,000
    volts is manufactured in accordance with IPCEA
    standards and is certified by CSA. Cables are
    provided with or without ground wire, as required.
    Teck cable with an outer jacket may be used
    for exposed or concealed wiring in wet or dry
    locations, indoors and outdoors, and in
    corrosive environments. It is suitable for use in
    ventilated, non-ventilated and ladder type cable
    troughs, and in ventilated flexible cableways in
    both dry and wet locations. It is also suitable for
    direct earth burial and for Class II, Division 2; and
    Class III, Divisions 1 and 2 hazardous locations,
    as per the Canadian Electrical Code.
    Flexibility and ease of installation are key
    features of Teck cable. The absence of dead air
    space within the cable increases heat transfer
    and minimizes condensation. The overall
    protective covering provides good environmental
    protection.
    Bend radii for permanent training during installation
    usually varies between 7 to 12 times the cable
    diameter, depending on the construction of the
    cable and the manufacturer's recommendations.
    Larger radii bends are required for other conditions.
    Electrical Code Requirements
    Section 12-3024 of the Canadian Electrical Code
    requires that the terminating fittings used must
    provide adequate strain relief to terminal connections
    and ensure electrical continuity without
    injury to the nonmetallic sheath. Continuity is
    mandatory whether or not the armour is used as
    a grounding conductor. Except for dry locations
    that are free from corrosive atmosphere, the
    nonmetallic jacket cannot be stripped back to
    the point where the armour is exposed after
    installation.
    Where single conductor cables carrying 200 amps
    or more enter metal boxes through separate
    openings, certain precautions are required
    to prevent overheating of the metal by induction.
    Use of nonferrous or nonmetallic box fittings,
    locknuts and bushings and installation of nonmagnetic
    panel inserts is suggested in the code.
    Please refer to the following for further details
    and complete information:
    1. CEC Section 12, Wiring Methods; CEC
    Section 4, Conductors
    2. CSA C22.2 No. 131 and 131S (Supplement
    #1), Safety Standard for Type Teck Cable
    3. CSA C22.2 No. 18, Safety Standards for
    Outlet Boxes, Conduit Boxes and Fittings
    I was just going to say "google it", get some loving and go to bed... but you win... or did you? LOL..

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Can you use Metal Conduit as ground to convert 2 wire to 3 wire? [ 3 Answers ]

I need to convert an old cinder block house from 2 wire outlets to 3 wire by adding a ground to all outlets. Since the entire house is cinder block, all the circuits from the basement breaker box are in flexible metal conduit and metal outlet boxes... Is it possible to use the metal conduit...

Conduit sizing [ 1 Answers ]

I have 4 conductor tray cable , 3 number two and one # 6 bare ground in a jacketed tray cable, would 1 1/2 rigid conduit be suficient for this application, it runs about 200 ft

Conduit type and ground? [ 1 Answers ]

I am installing a spa and will be running a 220v/50A circuit for its use. Before pouring a slab I would like to bury the conduit and stub it up at the appropriate location. What type of conduit should I use? Is it best to use solid pipe which I would need a tube bender, or can I use PVC or...

Conduit sizing? [ 4 Answers ]

Hi all! I am relocating my breaker box approx 30 feet from its original location. Installing splice box in the old location for connections. My question is : I have 14 12-2 and 3 12-3 to pull from new box to splice box what size conduit do I need so not to worry about heat build up or de-rating...


View more questions Search