No problem... at this point, I also feel it's a faulty aquastat... I will recheck the wiring and update the post once the technician checks it out... thanks for all your time
-
Hello and thanks for the information!
To clarify my issue, the upstairs zone ( connected to the RA89A ) is working fine, i.e. thermostat calls for heat, the circulator kicks in and the boiler turns...
-
There are no zone valves - the downstairs thermostat is connected to the Honeywell L8124aquastat and the upstairs thermostat is connected to a Honeywell RA89A relay. I did rewire the downstairs...
-
Well, here's a start ( sorry about the lack of camera picture quality )... picture attached is the aquastat that has the downstairs thermostat connected...
-
Found this on honeywell's website - the configuration I have is shown at the bottom of page 4...
http://customer.honeywell.com/techlit/pdf/PackedLit/95-6571.pdf
-
I kind of just noticed it recently... I checked the wiring to the aquastat - 2 wires go to the thermostat, 2 go to the 120v feed, 2 go to the boiler and 2 go to the circulator - not much to mess up -...
-
The cut-in is set at 160 and the cut-out is set at 180. The furnace cuts in and out at these temps... as long as the downstairs zone isn't activated... thanks
-
Hello,
First, a description of my system - it is a weil mclain oil / hot water furnace with 2 taco 007-BF4 circulator pumps, controlled by LUX programmable thermostats ( 2 wires connected ). The...
|