But I am still holding the new 8610 U cost 96.00!
The heating guy could not figure out how to apply that unit!!
The 8600 is replaced with that 8610 U module Honeywell !
COULD SOMEONE...
-
I myself often get blocked by the view of a large SUV.
I refuse to drive till I get a full "panaromic "view,regardless of the driver behind me honking!!
Got it !
Rather be late then the...
-
-
Correctioin I had delyed ignition before!!
Al
-
After spending $96.00(not returnable ) Had the heating repairman come out and found it was the Orifice clogging on the pilot light !
For lousy 79.00 he got it going .
However, the guy could...
-
Was told by the stupid gas company guy it could be the module !
Go figure !
-
Fight it ,you got nothing to loose
-
We were told the original Module S8600M is now replaced with a universal one 8610 U by Honeywell!
I am unablke to get the furnace going with that new module !
The old one works Ok! GO...
-
That car has 100thousand miles and the check engine light never comes on.
All the dashboard light go on before starting and go out when running !Ford Crown 2001 and Marquis 2001 ignition were...
-
Forgot to say :SEARS carries Carrier parts !
-
Have a heating repair friend contact one of the supply stores after you give them your motor number!
Today's time those parts houses are hungry for business,
I did it !
-
My 18 year old 75 BTU Tempstar furnace the Gas valve has three wires .
One ,to open the pilotgasvalve and two to open the main gasvalve!
I am not getting a pilotlight gas! Or lit one !
...
-
I cleaned the SENSOR.and noticed there is no igniton lignt or spark present ,when starting the furnace !
Only the gas exhaust blower running ! Alas I noticed there is a pilotlight tube...
-
-
How to you test the Honeywell S8610U3009 furnace module and circuit board with the meter !
Gas company claims the control module or circuit board could be at fault due late ignition !(5 minutes )...
-
Burner does not ignite for 5 minutes ,after setting thermostat for heat !
I have gas compony check for full supply tomorrow and then what!?
-
Thanks for that info!
Alas ,I noticed burner takes to ignite for aprox. 5 minutes too,after thermostat is set for heat !
I have the gas company check for full supply of gas tomorrow, and then...
-
I still having a blower delay on my Tempstar furnace after burners are on for 5 minutes!
We have no Fan limit onli limitswitch !
-
Sears #867-769426 High effience unit
Blower comes on after 5 to 6 minutes!after flames go on !
What can I do I changed the Limitcontrol and set it at 250 degrees and is still doing the...
|