Most likely no power or bad capacitor
-
Is this a ac unit or heatpump??
-
Make and model of furnace and ac unit please
-
You need to get a hard start booster from a hvac company
-
-
Yes w2 goes to aux jumped to e. make sure to do the correct installer setup
-
Do you have another thermometer in the house?? What temp does it say? Either the t-stat is bad and showing the wrong temp or the hole in the wall behind the stat is to big, or there is something...
-
Is it blinking red or green? Does fan run on on position? If not jump red to y orred to g at control board lower door and see if anything works.
-
Seems high side is to high should be around 375 for 135 suction. What is temp outside? Sounds over charged or bad txv in coil
-
On the outdoor ac or the indoor airhandler?
-
If the blower motor runs then shuts down it is probably over heating and going out on overload. May need replaced
-
What is the model number?
-
Does compressor and fan both shut off?
-
The fan is not connected to the compressor, just make sure you get the right rpm when changing it.
-
Sounds like either air in pipes, or bad expansion tank, what is the pressure on the boiler?
-
-
Are we sure the grinding is in the fan motor not the compressor?
-
Is the compressor running or just the fan? Could be bad fan motor or bad start capacitor. As for why it runs when t-stat is off must be a stuck contactor. Turn power off and check for burnt wires...
-
So when it is not working, neither the indoor blower or the ac unit is running? Sounds like a bad control board, or a bad t-stat.
-
Bent fan blade, bad motor, or bad mounting.
-
Either not getting 24 volt power, battries are bad, or t-stat is just bad.
-
Is the source of this sound coming for the outdoor unit or the indoor?
-
Don't think much of any damage was done. Txv should be fine. Does it seem to be operating correctly?
-
Most of the time these days the a-coil does not get the dirt in gets stuck in the secondary heat exchanger coil depending on what type of system. I agree most likely a airflow problem, and why was...
-
Make sure power is off then wire them back together
-
Red to rh jumped to rc
Blue to c
Green to g
White to w
Yellow to y
Does this t-stat have a installer setup??
On a side note never buy hunter t-stats!!
-
Blower motor or condenser fan motor? No wires should go from compressor to the fan.
-
Famous supply company in pa
-
Is the cap going to the fan the same mfd as the old one? If it is sounds like a new fan motor is needed.
-
-
Yellow and red t-stat wires are touching somewhere. This is the only way both units would run
-
Are any wires touching each other at the t-stat. it your system a gas furnace and ac or a heatpump?
-
If neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. In that case could be a...
-
Did you get a new a-coil also? I agree in less the indoor unit was installed wrong or the outdoor unit froze up causing the water it is really of no fault of the hvac company
-
x2 and w can't both go to aux, what is brown hooked to in the basement furnace? Blue need to be hooked to c or you wll be changing battries a lot, make sure it is hooked to c on furnace. I would...
-
Replace start capacitor, do you have to start it on the fan on position and ac on both?
-
Could be unit is not big enough for area, or could be out of freon, or compressor could not be running.
-
Low freon pressure, or low air pressure at vents?
-
The compressor is outside the blower is inside, so inless you have problem in both units. If compressor is bad you will get same amount of airflow just not cold. If fan is bad ac outsdide works just...
-
What is the coil voltage? Just get a universal contactor you don't want to pay for anything carrier
-
Change air filter, check to see if there is ice on copper lines inside or outside on units. May ne freon and frezing up
-
Could be, or if dampers not working, or no bypass damper was installed unit may be freezing up
-
Is there a question here? If it starts then quits running replace the fan motor
-
All control boards are in the blower wheel part of the furnace.
-
Sounds like the control board is acting up again
-
Well there is no nitrogen in the system inless you put it there so that can't be a issue. Not pulling a vac is not good but should not cause the problem you are having. Did you see this black freon?
-
Sounds like size is a problem, or lack of airflow. Maybe not enough returns
-
Is this a mini split wall unit?
-
Furnaces have 2 doors the control panel should be in the one opposite from where the vent comes out, may have a metal cover over it after taking door off
|