        How to use the same drain.vent for utility sink in laundry room?
       
                  
        I want to install a utility sink in my laundry room utilizing the same drain/vent as what the washing machine uses now.
 Current setup: Washing machine enters into a drain, goes through a p-trap, then that connects to the drain/vent pipe from the left side.
 
 What I want to do: I want to install a sink on the left side also and run the drain along side the drywall and turn it 180 degrees and enter the same drain/vent used for the washing machine from the right side. I figured turning a pipe 180 degrees isn't a problem, so long as I have enough slope in the drain pipe.
 
 Problem: In a perfect world, I would be able to use a double Y connection on the drain/vent (one for the washer and one for the dryer), however, the current connection for the washer is to high on the vent, so I would need to bring the utility sinks connection below the connection of the washer on that same drain/vent. Does this cause a "venting issue"? Any other ideas? Thanks!
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 01:17 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Attached are a couple pictures... although the second one is sideways (sorry)
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 01:24 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks for the quick reply!So, what you're saying is just tap the sink drain into the washer drain (prior to the washer p-trap - meaning the pipe on the left in the)... and then can you describe the venting of the sink part again?
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 01:24 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Hold on... pics. Helped, but now, what is the drain pipe coming off to the right?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 01:27 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        You're talking ab out the horizontal one near the floor? I'm not sure where that one goes (unfortunately not the original owner of the house). Could possibly be a bathroom drain from upstairs? I don't know what that one does... 
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 01:28 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Without knowing what that pipe is it is hard to advise here... ;)  Find out what the pipe is and then let me know what it is.  I'll be back in a couple hours.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 01:46 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I wish I had a camera that could see through drywall. This is my best guess... since the laundry room is on the side of the house with the family room (thus no other water sources near there on this level)... I can only assume its from the room directly above there... which is the master bathroom. So, it has to be either the sink or bathtub drain coming down.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 01:57 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        massplumber2008 - I reviewed some photos of neighbors who hae a similar model and it looks to be the drain for the shower above in the master bathroom. Does that help any?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 04:12 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK... couple ideas.  My first idea is to have you remove the washing machine Ptrap and install the new sink off that pipe.  Then you would just have the washing machine hose connect into the sink and be done with this with very little work... ;)
 Otherwise, yes, you can connect underneath the washer drain fitting (but above "shower" fitting) and vent the new sink drain into the existing vent at about 42" off the floor (invert sanitary tee fitting)... see images.
 
 Install a full size cleanout to the new drain (see images) and be sure that the new vent for sink pitches from the washing machine vent to the sink drain, OK?
 
 Mark
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 04:46 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Ok, thanks, so would your first idea look something like this?? Except I forgot to draw a p-trap for the sink
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 04:50 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        No, my first drawing doesn't show the sink drain connecting into the washer standpipe... shows a separate tee fitting being cut in below the washing machine drain fiting (look at image again), but above the proposed shower drain fitting... (see another image below at my next post)... 
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 04:58 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        See image below
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 05:06 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by massplumber2008   see image below First, thanks for taking the time with the explanations and the drawings!
 
Couple issues I'm running into with this design is that there is only 6.5" of "vent" pipe" between where the washer connects to the vent and the shower drain connects to the vent. So, putting a connection between those 2 for the laundry tub could be tough. Another problem is all of the water pipping in front where this new drain would connect to the pipe. I'll try to attach a closer up image of that area in a couple minutes.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 05:13 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Here are the closeups with a measuring tape
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 05:13 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        If you are willing to cut out some of the washing machine drain piping you could install a double sanitary tee fitting and pick the sink and washer drain up that way... :)
 Here, if you use a 2" PVC SHIELDED CLAMP (see image) you could cut the pipe between the shower tee and the washer tee, install a new fitting for the sink/washer and then install a coupling in the vent and join all back using the clamp as the final fitting.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 05:18 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        [QUOTE=massplumber2008;3389739]If you are willing to cut out some of the washing machine drain piping you could install a double sanitary tee fitting and pick the sink and washer drain up that way... :)
 Wouldn't that be like my original drawing to you? Just connect the new sink drain to the washing machine drain with a tee (higher than that of the p-trap), and just have both drains running through the current washer p-trap?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 05:20 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Also, stupid question, when you refer to "Add a cleanout", what does that exactly mean?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 05:28 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Wouldn't be like your original drawing at all.. can't connect the sink into a washing machine standpipe, but if you installed a DOUBLE SANITARY TEE fitting into the stack you could pick up the washer ptrap and run a new Ptrap over to the sink... see image.
 The cleanout is called a test tee or some call it a dandy cleanout (see image of an ABS plastic one).  Install this on the pipe going to the new sink drain... just in case you need it in the future.
 
 Mark
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 6, 2013, 05:35 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I gotcha now! I just need to make sure there is enough "height" for the sink drain to slope down and still catch where the double sanitary tee is.
 I've also read that using a "Y" double sanitary tee (as opposed to 90 deg angles) is better in case one of the drains ever gets clogged... it would be easier to snake out...
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Feb 6, 2013, 05:37 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Double wye cancels out the contribution of the vent... not applicable here, but I know what you are saying in terms of snaking the drain.  To resolve this issue, plumbers use a special drop head tip on the end of their snakes.
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Adding sink drain to laundry room
 [ 8 Answers ]
I want to add a sink drain from and adjacent room to an existing laundry room. The original drain design does not physically allow space for another connection to the stack below the existing washer drain (see original below). I am thinking of modifying the washer P-trap and using the existing...
 
Are vent pipes needed on laundry sink and floor drain in basement
 [ 5 Answers ]
I have a room that is on the back of my house at the same level as my walkout basement. I currently have only a French drain in the center of the room. I would like to put in a laundry sink and a proper floor drain in that room. The room has a concrete floor and the main 4" drain line from the...
 
Installing a utility sink in the laundry room
 [ 4 Answers ]
Hi, 
 
I want to hook up a utility sink next to my washing machine on the first floor.  The washer discharges into a standpipe.  The standpipe has a trap, and then connects through a tee to a vertical waste pipe (drain stack?) that goes upstairs through the roof as a vent.  Below this tee, there is...
 
Kitchen Sink/Laundry Sink Drain Vent Non-exist
 [ 3 Answers ]
The set-up from kitchen sink leading down to drain to basement: 
1. Kitchen sink - (R side) - connected to a P drain I think you call it -PVC-, connected to a "metal" T, which has a Studer vent gizmo attached to the top of it, then draining into a metal pipe straight down to the drain in the...
 View more  questions
Search
 
 |