               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 30, 2013, 12:59 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
      
      
        
        Moving drains below slab for major remod
       
      
    
    
    
                  
        Bath remodel next questions: 
Below are two schematics with two new floor plans 
I hope they will help me make my questions more clearly understood 
(Tub is on outside wall of slab on grand construction  likely a grade beam of concrete along the back wall). 
 
1)	In upper left where the shower was  I will move a vanity  I have been advised not to use the shower drain as it has a trap and you cannot use a double trap.  Ok then. So now the idea is to put the drain into the wall and bring it to the existing 2vent- tap into the vent with sanitary tee.  Cap off the old shower drain and fill that hole with concrete. 
2)	Toilet move (thanks for answers to previous post) in good shape  concrete busted out and existing line exposed  new connection will be a flange to 4 to 90 4X3 to 22 degree coupling to existing line.   That should get me hooked up  uses same vent  no issues there. ( I hope) 
 
 
3)	New shower location ONE: wife threw me a curveball  hence two floor plans 
a.	Adjacent to tub (her new idea) in the first schematic.  I will have to bust out concrete to get a drain in the floor : 
b.	Can I tie the new shower drain into the existing tub drain 
c.	Do I tie in above the tub trap ( if possible  enough room) 
I.	If I tie in above trap do I not put a trap in shower drain? As the tub trap would be a trap for both? Center of new shower location to tub trap is about 3'  4 ' 
d.	Should shower drain be 2? 
e.	Is existing vent ( for removed  sink and tub adequate for tub and shower) 
f.	Is a center drain preferable  or is it OK to offset it such that it is close to the existing tub drain ( less concrete to break out) 
g.	If a and b are not correct I must find one of the other lines to tie into?  
 
4)	New shower location TWO:  
a.	Across from the tub in second schematic.  I will have to bust out concrete to get a drain in the floor  - tie into toilet (3) drain with 3X3 hub with 2 long sweep connector 
b.	Now I must put a trap on shower drain 
c.	Should shower drain be 2? 
d.	Is existing  2 vent OK for both toilet and shower 
e.	Is a center drain preferable  or is it OK to offset it such that it is close to the exposed toilet drain (trench) as  there is less concrete to break out 
I hope this I not too much to ask and thank you in advance for your answers 
     
     
    
      
      
    
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 1, 2013, 07:44 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Perhap this is too many questions for one post? 
If so my appoligue
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Eternal Plumber 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 1, 2013, 10:14 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        You're just fine.  I have poor eyesight and have a hard time reading prints,  We have sharp experts here and I'll shake one out to answer you.   Tom
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 1, 2013, 03:04 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        It is a lot of questions, but I can help tomorrow sometime if you confirm that you will be back to review my answer, OK? 
 
Mark
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 1, 2013, 03:52 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        OK you bet that I will and thank you very much 
	
		
			
			
				
					  Originally Posted by  massplumber2008
					 
				 
				It is a lot of questions, but I can help tomorrow sometime if you confirm that you will be back to review my answer, OK? 
 
Mark 
			
		 
	 
 
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 2, 2013, 04:18 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Hi MLBDIY 
 
1) all sounds correct here. 
 
2) also sounds good 
 
3a) Yes, you'll need to break open the floor. 
 
3b) Tub drains are 1.5" and shower drains need to be 2", but if you are lucky that tub drain will be 2" AFTER the PTRAP.  If you find 2" then you can definitely connect into that drain for the new shower.  If you find only 1.5" after the tub ptrap then you could connect into it, increase it to 2" and pipe up the shower drain... just won't be to code. 
 
3c) No you do NOT cut into into/above the tub ptrap... eliminate this. 
 
3d) Shower drain needs to be 2" and must have its own 2" ptrap located directly under the new shower strainer. 
 
3e)  If sink drain is capped off then you can use the sink vent as the shower vent. 
 
3f)  If this is a custom shower floor then you decide where it goes... just will be pitching the floor as needed.  When you build this custom shower be sure to pop back to consult on proper way to do the job... MANY people screw these up! 
 
3g) see 3b 
 
4a) yes, install a 3"x2" combination wye and pick up the new shower PTRAP.  The toilet vent can act as a wet vent for the shower. 
 
4b) yes 
 
4c) yes 
 
4d) yes 
 
4e) same as 3f above... ;) 
 
Back to you...  
 
Mark
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 2, 2013, 05:40 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I realized I have asked for lots of information and I definitely appreciate the generosity of your time thank you very much.  I will post pics as I progress. 
 
	
		
			
			
				
					  Originally Posted by  massplumber2008
					 
				 
				Hi MLBDIY 
 
1) all sounds correct here. 
 
2) also sounds good 
 
3a) Yes, you'll need to break open the floor. 
 
3b) Tub drains are 1.5" and shower drains need to be 2", but if you are lucky that tub drain will be 2" AFTER the PTRAP.  If you find 2" then you can definitely connect into that drain for the new shower.  If you find only 1.5" after the tub ptrap then you could connect into it, increase it to 2" and pipe up the shower drain...just won't be to code. 
 
3c) No you do NOT cut into into/above the tub ptrap...eliminate this. 
 
3d) Shower drain needs to be 2" and must have its own 2" ptrap located directly under the new shower strainer. 
 
3e)  If sink drain is capped off then you can use the sink vent as the shower vent. 
 
3f)  If this is a custom shower floor then you decide where it goes...just will be pitching the floor as needed.  When you build this custom shower be sure to pop back to consult on proper way to do the job...MANY people screw these up! 
 
3g) see 3b 
 
4a) yes, install a 3"x2" combination wye and pick up the new shower PTRAP.  The toilet vent can act as a wet vent for the shower. 
 
4b) yes 
 
4c) yes 
 
4d) yes 
 
4e) same as 3f above...;) 
 
Back to you... 
 
Mark 
			
		 
	 
 
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 3, 2013, 05:03 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Don't forget to consult with us if you are building a custom shower with custom shower pan... ;)
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 3, 2013, 06:38 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I definitely will do exactly that.   
Thanks again for your help. I am going to try to get a final location for the new shower from the wife in a day or two and begin phase two of slab cutting. 
  
As I will now put a ptrap under the strainer is there any certain amount of head I need (or perhaps I should ask how deep should I put the ptrap?  - I ask because the pips are shallow as this is the back of the house and clean out is in the front.    
 
I know I need Ό drop per 1 run  I am hoping I have enough room! 
 
You guys are generous with your time/expertise thank you
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
Sub slab drains
 [ 4 Answers ]
I have attached a picture to better ask my question. 
 
Can I use this assembly for new toilet location 
1)Flange  
2) 90 Closet bend (from verticle to horizontal)  
3) 90 from Closet bend back into original horizontal drain line 
 
All 4" PVC 
 
I am a bit worried about two 90 that close to each...
 
 
One toilet won't flush and drains slow following a major rain storm
 [ 1 Answers ]
Three out of four toilets in house work fine, but basement toilet will not flush and drains very slow after blow fills up almost to the rim.  Toilet appears to be  functioning OK.  It is as if the line (beyond the toilet is clogged or filled with water) and will not allow additional water in the...
 
 
Major clog in tub in slab foundation
 [ 4 Answers ]
I'm a homeowner with three dogs.  I wash the dogs in the tub using panty hose material to try to catch as much hair as possible.  Obviously, this hasn't worked well.  I have a major clog in the tub drain.  I called a plumber who spent most of his time on the cell phone trying to get a diagnosis...
 
 
Moving p-trap in a slab
 [ 3 Answers ]
I have a question on moving a p-trap and plumbing for a tub on a slab.  I am going from a drop in tub to a free standing tub and so I need to dig up the slab, replumb the p-trap to the proper location - ~2ft over and then refill the slab.  I noticed that there was a hole just off center under my...
 
 
Moving plumbing in the slab
 [ 31 Answers ]
We are remodeling our master bath and want to eliminate the shower and replace it with a tub; however, after demo we can see that not only does the vent have to move, but the drain will need to be moved as well. 
 
What I'd like to know is whether there are any options (without a violation or...
 
 
 
View more  questions
Search
 
 |