        I am installing a wetbar in a basement.  I had a 2" pvc drain line roughed-in before the slab was poured.  This 2" pvc line is vertical and stubbed off at about 12".  I am putting a base cabinet over top of this drain line and will use a "S" trap to connect to the sink above.  Since there is no vent line available, I will install an air vent under the counter.
 Beside this 24" base cabinet, I'm installing an ice maker.  The drain is 3" off the bottom.  The horizontal run from the ice maker to the 2" drain is about 18".  Since the ice maker drain is so low to the floor, I will have to use a condensate pump.  The 2" drain in the cabinet is 6.75" off the floor.
 
 I've read about an air vent requirement for the ice maker but since I'm using a condensate pump I don't know how to physically hook everything up.  Do I bring the ice maker drain to a point above the sink "P" trap?  What venting is required for the icemaker if any or does the sink AAV take care of the requirement?
 
 Thanks
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 25, 2008, 01:13 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        If you loop your condensate pump hose you will have created a trap but tieing into the sink drain above its trap is all that is necessary. The codensate pump tank is not 100% air tight and self vents.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 25, 2008, 01:29 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I called an inspector and he said it needed to be connected like a dishwasher.  He said the ice machine needed to be protected from a plugged drain line and backing up into the ice machine.  He told me to copy my dishwasher hookup.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 25, 2008, 01:41 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Did he say the dishwasher hook up could use a big loop in the drain or does he require a counter top air gap. Worth asking him.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 25, 2008, 01:55 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        He didn't mention a loop,  I've looked under my sink and there is what appears to be an air vent for draining purposes.  I'm not sure what an air gap looks like, but there is nothing mounted at counter top height and connected to any piping.  When I get home I'm taking a good look under my sink again.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Jun 25, 2008, 02:07 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thought I would post a picture of the loop and the air gap setup Ballenger is talking about... 
 Doesn't sound like you have the air gap Parkflyer.. so a high loop is probably going to work best... but as Ballenger said... can't hurt to ask the inspector to be sure...
 
 MARK
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 25, 2008, 03:07 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I am always impressed with the pics you and Tom can attach. Teach me how.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Senior Plumbing Expert |  | 
 
                  
                      Jun 25, 2008, 04:06 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Anytime Bob! 
 I'll send you information on how I do it... look for it!
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 26, 2008, 03:40 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Nicely done!  I definitely do not have an air gap!  I have the disposal hook-up.  The only thing I have that you don't show is a studervent in the drain to the wall.  My dishwasher line is a high loop over the cabinet side.  Hope they didn't slip somethig past the inspector. 
 Thanks,
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Eternal Plumber |  | 
 
                  
                      Jun 26, 2008, 05:22 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				Hope they didn't slip somethig past the inspector.
			
		 If the imspector passed the job with the AAV installed you have nothing to worry about.  Good luck,  Tom
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 26, 2008, 07:34 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks for all your help guys.  I'm an electrical guy so I like working with my hands, just don't know much about plumbing and this drain stuff is complicated.
 I spoke with the inspector again.  He told me the icemaker with a condensate pump can be installed like the dishwasher with a high loop.  He said air gaps were required if I had a gravity drain.  It doesn't matter but I'm a curious guy so I'll ask.
 
 He said in a gravity drain the air gap is to prevent the gray water from entering the icemaker if there was a drain plug.  They want the nasty stuff to run on the floor before entering the icemaker.  He said an air gap is not required when using a pump.
 
 What I don't understand is how gray water is kept out of the condensate pump with the high loop.  Only if the loop was higher than the counter top would it prevent gray water from entering the icemaker.  That way if there was a plug in the drain it would back up and out the sink.  But the loop will be under the cabinet so a backup would travel through the loop before it backs up high enough to exit the sink via the countertop.
 
 The only thing I can think is the condensate pump is not sealed and the backup will exit the pump somehow and not enter the icemaker.  It's all very confusing.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Ultra Member |  | 
 
                  
                      Jun 26, 2008, 08:16 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Hey Mark,
 Please  add me to your list of how to make the pics, would be greatly appriciated, Thanks in advance.
 
 Best Regards,
 John
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 26, 2008, 08:53 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        In post #2 you said I was very helpful but then gave me a reddie for inaccurate, what's up with that?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Improvement & Construction Expert |  | 
 
                  
                      Jun 26, 2008, 09:11 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        afaroo
 Open picture with paint.  Crop if possible.  Reduce size if necessary. To do so, click on Image, choose stretch/skew.  Reduce width and heigth by same percentage.  Save as JPG.  Repeat if necessary to get file down to acceptable size.  The JPG file format is most important part.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 26, 2008, 09:45 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Ballenger,
 Because I'm an idiot!  I hit the wrong button by mistake.  I tried to edit it but the system wouldn't let me.  I tried to post a rebuttal and the system said I had to rate others first.  Sorry about that.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 26, 2008, 12:38 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Yes, once you rate someone you have to give 5 others a rating before you can come back to the first guy, me. Maybe some other day.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 26, 2008, 12:51 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Am I right in my assumption?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 26, 2008, 01:03 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I am a bit foggy, can you tell me your assumption again?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jun 27, 2008, 05:33 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Trying to understand drain requirements.  Question is below. 
	
		
			
			
				
					  Originally Posted by parkflyer Thanks for all your help guys.  I'm an electrical guy so I like working with my hands, just don't know much about plumbing and this drain stuff is complicated.
 I spoke with the inspector again.  He told me the icemaker with a condensate pump can be installed like the dishwasher with a high loop.  He said air gaps were required if I had a gravity drain.  It doesn't matter but I'm a curious guy so I'll ask.
 
 He said in a gravity drain the air gap is to prevent the gray water from entering the icemaker if there was a drain plug.  They want the nasty stuff to run on the floor before entering the icemaker.  He said an air gap is not required when using a pump.
 
 What I don't understand is how gray water is kept out of the icemaker with the high loop.  Only if the loop was higher than the counter top would it prevent gray water from entering the icemaker.  That way if there was a plug in the drain it would back up and out the sink.  But the loop will be under the cabinet so a backup would travel through the loop before it backs up high enough to exit the sink via the countertop.
 
 The only thing I can think is the condensate pump is not sealed and the backup will exit the pump somehow and not enter the icemaker.  It's all very confusing.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Repair & Remodeling Expert |  | 
 
                  
                      Jun 27, 2008, 12:03 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I guess you mean you thoughts on the condensate pump not being sealed. I would agree the likelihood of a back up reaching the ice maker is almost non-existent. However, building inspectors come in many flavors so you try to work with them, do it his way since he will do the inspection. No wee wee matches with skunks, you always loose.
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Ice Maker
 [ 2 Answers ]
Yes I have a Jenn-Air refrigator and need to replace the Ice Maker do I need to shut off water? Only because I have a crawl space and if I don't need to go in crawl I won't. 
 
Thanks for any and all information Terry
 
Designer needs maker
 [ 1 Answers ]
I have some design ideas for luggage,handbags, etc.  Who do I go to to have these designs made?
 