    Dsc 1832 entry delay not disarming?
    Hi, could you please help me with my dsc 1832 system, the problem is disarming the system when entry delay is active, when I enter my code the keypad continues to beep and system goes into alarm after entry delay finishes, once the system is in alarm, I enter my code and the system disarms. Could this be a programming problem?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 13, 2012, 09:43 PM
    That's odd, worked on them many years, never seen.
    Verify Entry delay is programmed for Entry 1 or Entry 2.
    Verify Entry times, default should be fine.
    Motion is not programmed as a Fire or other 24 hour burg zone?
    Worse case, Default Panel and start over.
    If you are NOT using an Alpha Keypad, programming errors and false alarms can easily occure, due to entrepreting Led's or numbers on the other keypads.
    I like an Alpha KP in every system, it also has custom names and an Event Buffer so you can see the last 254 Events.
    joy888's Avatar
    joy888 Posts: 1, Reputation: 1
    New Member
     
    #3

    Oct 3, 2013, 10:08 AM
    Did you fix your problem? I am having same problem with my dsc 1832
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Oct 4, 2013, 06:30 AM
    Maybe try a 902 for minute, then 903 and see if the Panel sees the Keypad.
    I always do it, so I don't know if this is the result of not Enabling Supervision.
    It will also show any devices attached(Wireless Receivers, Expanders, Output modules, Etc)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

DSC 1832 with RFK5500 keypad, entry delay not working. Please help [ 4 Answers ]

So originally I worked through the manual, then wired it all together Zone 1 PIR Zone 2 PIR Zone 3 PIR Zone 4 wireless door Zone 5 wireless door Zone 6 not used Zone 7 not used Zone 8 smoke

DSC PC 1832 programming troubles [ 9 Answers ]

Hi…I am currently replacing an old DSC PC 2525 home security system with a newer PC 1832. The trouble is… I am having difficulty even getting to first base programming this unit Is there someone on board who can walk me through this? This is what I have: 2 new keypads.. a pk 5501 at the...

Entry delay not working on my new DSC 1832 [ 1 Answers ]

I installed and programmed a new 1832 panel. I set delay 1 at 30 sec, delay 2 at 45 sec and exit delay at 60 sec. The zone is set at delay 1. The exit delay works fine, but I get no entry delay at all. Alarm goes off as soon as the door is opened. Any ideas?

Trouble with DSC 1832 programming [ 3 Answers ]

Recently I have installed dsc 1832 security system . So far I have done good. But I can not solve my smoke detector problem . Smoke detector is FSA-410BT 4-wire . I have run cat5 wire for this connection . The reason is simply - I had left over cat5 . I have used Bro for 12v+ and BLU for GND....

Dsc 1832 resistor value [ 1 Answers ]

I have a DCS 1832 and I am getting intermitting open. The wires at the control panel are tightly secured. It could be a resistor problem and I am unsure of to what the resitor value should be for the zones. Can you help?


View more questions Search