New Member
|
|
Jun 26, 2006, 09:36 PM
|
|
Wiring manual fan switch
I'd like to wire my blower motor to my Honeywell CT2800 programmable thermostat so that I can use the manual blower switch. However, I am a bit confused as to how to do this. The furnace is a Clare Brothers MBG120. The 120VAC comes into the furnace and the white wire goes to the 120VAC to 24VAC transformer as well as to the furnace blower. The black wire goes to some type of switch that has a dial on it and a knob that you can pull out and run the fan manually. Limit switch I am guessing. Out of that switch comes a red wire that goes directly to the fan and a white wire that goes to the other side of the transformer. From the transformer, there are two wires and they go to a valve assembly on the gas inlet. On that valve assembly are the terminals TH, COIL, and TR. One of the wires goes to coil and the other one goes to TR. On the same terminals, the thermostat is wired and a yellow wire goes to the TH and a red wire goes to the coil. Up at the thermostat, the yellow wire goes to the terminal marked R and the red wire goes to the terminal marked W. There is a G in the thermostat, but there isn't anywhere on the furnace. I think that I might have to install a relay, but I am confused since the fan motor doesn’t have one already and runs strictly off 120VAC. Can anyone shed some light on this? Thanks very much.
|
|
 |
New Member
|
|
Jul 18, 2006, 04:36 PM
|
|
That box with the dial and the white knob to turn on the blower is called a fan/limit switch, and unfortunately the only way to turn the fan on is by pulling the white knob. With these older furnaces there isn't many options you can do to improve the functionality of the furnace, since they are very basic. Connecting a programmable thermostat up to an old Clare furnace is a waste of time.
Brian Belanger
Gas Technician
The Stove Store, Spencerville Ont. Canada
|
|
 |
New Member
|
|
Jul 19, 2006, 12:54 PM
|
|
Thanks for the reply. I actually have the thermostat wired up and working for heat. I was looking for a way that I could hook up the fan to the thermostat so that I could turn on the fan by itself for summer cooling. I opened up a hole in the air intake for the furnace so that it would take the cool air out of the basement and put it upstairs. Right now, I just pull the white knob and it comes on. It works fine, but it's a pain in the arse to go up and down the stairs. Was hoping I could wire it to the thermostat. But if that's not possible, would it be possible to put in a on/off switch (near the thermostat) for the fan and bypass the limit switch? If so, how would I do this? Thanks again.
|
|
 |
Uber Member
|
|
Jul 19, 2006, 03:32 PM
|
|
Yes you will need a relay with a 24 volt AC coil and at least one set of contacts rated at 120 volt AC 15 or 20 amps. The contact rating must meet or exceed the amp draw of the fan motor.
Then you will need another wire brought up to the stat to connect to G. You can run a #18-2 thermostat cable up to the stat.
Cap one wire at both ends as a spare, use one ,connected to G, and the other end connect to one side of the coil of the new relay. The other side of the coil should go to TR. I believe this is the common for the 24 volt .
Before connecting to the relay, You should check with a meter to measure 24 volts between the wire from G, with the stat in "fan manual" position, and TR.
On the 120 volt contacts , you need to cut these two wires into the 120 volt feed to the fan limit switch, thus switching the feed to the fan.
Any questions get back with them, and be to to have 24 volts across G wire and TR, if not you will not have 24 volts at the relay coil.
|
|
 |
New Member
|
|
Jul 20, 2006, 06:57 PM
|
|
Just make sure you don't touch the limit switch... it is a safety device!
|
|
 |
Ultra Member
|
|
Jul 20, 2006, 09:44 PM
|
|
How many wires do you have now going from the furnace to the thermostat, also how many terminals do you have on the low voltage terminal board at the furnace. Most furnaces manafactured in the last ten to fifteen years were made so that centeral air could be added at little cost. So tell me about the wires and the terminals
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Ceiling Fan Wiring To Switch
[ 1 Answers ]
I just installed a new ceiling fan in a room where the switch previously controlled only an outlet and there was no power directly at the switch, only at the outlet.
At the switch box I wired the two white wires together and then wired the black wires, one each, to the screws on the switch.
The...
Dimer switch wiring?
[ 1 Answers ]
I am replacing a single pole switch with a new dimer switch. On the dimer there are four wires, rerd-black-blue and the ground. Where are all these wires connecting to. Jeff
Wiring a light switch
[ 2 Answers ]
The light currently just has a pull cord and I want a simple wall switch instead. The power runs to the light from the other side of the room. Do I just need to run a wire from the switch to the light and tie it in or have the power come to the switch first and then to the light? How does it tie...
Furnace fan switch wiring
[ 4 Answers ]
I have an oil furnace, controlled by a thermostat that only has 2 wires going to it, but I want to be able to turn on the fan only from the fan switch on the t-stat. There do not appear to be any further connections at the furnace to hook up to, and the fan switch at the furnace (which can be set...
View more questions
Search
|