The question is about the life of a filter in an air handler. I have been watching some of the 5 inch filters in our group homes, and while they can look gray in a matter of 2 or 3 months, the static pressure drop across the filter hasn't changed much. I can start in the range of 0.25" to 0.35" WC and I have been replacing them yearly at the spring PM. When I replace them I might get a measurement of 0.75" or so, but have never seen over 1" WC. In the name of science I ran one until I got to that 0.75" reading and it lasted almost a year and a half. It made me wonder, what is a good way to tell when a filter is shot? What would be a good number to use to determine filter drop? I know, air speed changes those numbers, but then a new filter has a higher initial number, so it might have to be a percentage. (0.25" to 0.75" = 300%) Any ideas, or better, any hard science? I can't find anything in the instruction manuals.
|
|
|
 |
Ultra Member
|
|
Jan 23, 2009, 06:21 PM
|
|
|
Manometer reading are generally the best way to determine how restricted a filter is. Everything else is variable.
|
|
|
 |
Plumbing Expert
|
|
Jan 23, 2009, 06:29 PM
|
|
|
I would think the time spent doing intensive testing for filter clarity would cost more than just replacing the filters on a regular schedule. Just a thought. Filters are cheap(comparitably) to purchase and change. Why overthink a simple process. However, you do raise an interesting question, and I look forward to hearing all advice.
|
|
|
 |
Uber Member
|
|
Jan 23, 2009, 07:57 PM
|
|
|
SP between 0.5 to 0.75 at the highest fan speed measured on the discharge side. Definitely no more than 1.
You can turn the reading across the filter into a % filter used, but not directly. 0.5 to 0.75 may just be 100%.
As the SP increases, your CFM decreases. AC requires a higher CFM than heating.
You may then be able to get a higher filter lifetime over the heating season.
|
|
|
 |
Ultra Member
|
|
Jan 24, 2009, 07:49 AM
|
|
|
The length of time a filter is in service is not always the best indication of need for replacement. System usage, pets, remodeling, housekeeping, etc. etc. all factor into how long a filter will last. I provide the high-MERV air filters for many of my service customers, and filter usage varies a great deal from the most to least frequent replacement. Some are nearly clogged in just 6 months, while others show very little usage after 1 year. There is no one-size-fits-all answer for the question of filter replacement.
|
|
|
 |
Senior Member
|
|
Jan 25, 2009, 02:05 PM
|
|
|
MissouriBound,
I am using a UEI 2 port electronic manometer. My measurement method is one port in the return air duct 2 ft or so ahead of the filter, and the other between the filter and fan, at least a foot or more away from the filter if possible. My measurements therefore are DIFFERENTIAL pressure. The pressure drop ACROSS the filter.
I would think the time spent doing intensive testing for filter clarity would cost more than just replacing the filters on a regular schedule. <snip>
MyGirlsDad,
Yes, I agree, but this is research, not just blind mechanics. I work for a non-profit, and at $20 or more a throw, if I can save them some filters, that's as good as a donation. If I feel bad about the time researching things, I can donate that. I am just curious by nature and want to do the best job possible. Note: all this AMHD stuff is on MY time! :p
SP between 0.5 to 0.75 at the highest fan speed measured on the discharge side. Definitely no more than 1.
KISS,
Clarify discharge side. Of the fan? Of the filter? Of the complete air handler?
<snip> As the SP increases, your CFM decreases. AC requires a higher CFM than heating.
You may then be able to get a higher filter lifetime over the heating season. <snip>
Yes, I know this. However, I do not have a pitot/static tube to probe the ducts and actually measure CFM so I can't actually correlate pressure drop numbers to CFM numbers. (Yet... :D Tools are better than candy.) And yes, I usually like to change filters in the spring if possible. My biggest concern is to catch them in time BEFORE they cause problems without just using LAR service techniques. What would be a realistic percentage of CFM drop that would indicate time to change the filter? 95%? 90%? 80%? And of course that begs the question of correct CFM numbers for the equipment at hand. We have systems that have good duct systems and some LOUSY ones that probably don't even come up to air flow spec WITHOUT a filter. And almost NONE of them give actual CFM number requirements in the manuals that are laying with the systems. Establishing baselines might be fun!
KC13,
Agreed wholeheartedly. Hence my question.
I really like the MERV 11 filters that we are using wherever possible. I actually think I can tell a difference in the cleanliness of the houses since we got rid of the hogs hair filters and changed to these, but I want to be certain that there aren't some hidden gotchas that I might miss.
Thanks any and all for the input. Any more information or links to something that can help me apply science to my job?
EPM
Note: LAR = Looks About Right. Unfortunately a very common method of engineering.
|
|
|
 |
Uber Member
|
|
Jan 25, 2009, 04:29 PM
|
|
|
Use your manometer and look at the SP after the blower.
I could find out the hard way, but it would take a while and I'd have to start now.
My tstat at home has a filter monitor built in and can measure RPM, static pressure and CFM.
Right now I'm at:
30% filter used
1450 CFM
1004 RPM
0.59 Static pressure
Remind me in a month and I'll do the readings again. It might be more useful, to do the calc with a new filter.
I could put in a new filter and measure the parameters and assume that the new one was identical as the old one when it was new.
The tstat does a dirty filter test once a day by running the fan at max speed for about 5 minutes.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Life in heaven or life on earth?
[ 21 Answers ]
Given a choice of living forever in perfect health on a paradise earth or living forever in heaven as a spirit, which would you choose?
I lost the love of my life, my life doesn't make sense anymore
[ 4 Answers ]
I lost mybestfriend and love of my life 2 weeks ago and I don't understand my lifes purpose anymore, we had a connection so strong this doesn't make sense, everything I did in my over the past 22 years was for me however the constant knowing we would be together, we had 3 years to go before...
How do you calculate NPV and PI
[ 3 Answers ]
My question is find the NPV and PI of an annuity that pays $500 per year for 8 years and costs $2,500. Assume a discount rate of 6%. I'm lost! How do I even calculate this?
Pump won't lite after cleaning filter and inner filter
[ 1 Answers ]
Filter was complet mush and guk, also in the pump I took out and cleaned the screen , all good now, I primed filter and pump but still would not ignite. Blnk blk blk, after 3 second hold button furnace attempts then must hold for 30 secs to reset from lockout. SO after many attemps, "does it every...
How do you calculate the NPV?
[ 6 Answers ]
What is the NPV for a project if the cost capital is 12% and the initial after-tax cost is $5,000,000 and is expected to provide after-tax operating cash flows of $1,800,000 in year 1, $1,900,000 is year 2, $1,700,000 in year 3, and ($1,300,000) in year 4?
View more questions
Search
|