Ask Experts Questions for FREE Help !
Ask
    jsemelgar's Avatar
    jsemelgar Posts: 5, Reputation: 1
    New Member
     
    #1

    Aug 10, 2008, 11:22 AM
    Transformer keeps burning out
    I'm a jack-of-all-trades. My contactor got stuck in the on position (it was pitted and kind of burned). I replaced it with a new one, but stupidly connected the Low Voltage wire to the same side on the contactor. Some wires smoked at the contactor and I shut off the power.

    The neighbor (studied for A/C but not working in the field) showed me my error and correctly hooked the LV wire. Afterwards, the 240/24 volt transformer had no power coming out the 24v side. We replaced the transformer and it burned out again. 240 Volts come to it, but 24v don't come out.

    I can't visually find a shorted wire from the 240 side back to the blower motor nor at the blower's capacitor. The blower seems to run fine according to the neighbor. There is no circuit board. Another A/C friend told me, over the phone, that it could be the blower motor having a short.

    This forum's previous postings suggests a short along the 24V wiring (through thermostat and/or contactor).

    Before I call repair man, should I replace the 24V wiring and contactor? Should I replace the blower motor? Thanks to all suggestions, in advance.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 10, 2008, 02:44 PM
    Quote Originally Posted by jsemelgar
    I'm a jack-of-all-trades. My contactor got stuck in the on position (it was pitted and kind of burned). I replaced it with a new one, but stupidly connected the Low Voltage wire to the same side on the contactor. Some wires smoked at the contactor and I shut off the power.

    The neighbor (studied for A/C but not working in the field) showed me my error and correctly hooked the LV wire. Afterwards, the the 240/24 volt transformer had no power coming out the 24v side. We replaced the transformer and it burned out again. 240 Volts come to it, but 24v don't come out.

    I can't visually find a shorted wire from the 240 side back to the blower motor nor at the blower's capacitor. The blower seems to run fine according to the neighbor. There is no circuit board. Another A/C friend told me, over the phone, that it could be the blower motor having a short.

    This forum's previous postings suggests a short along the 24V wiring (through thermostat and/or contactor).

    Before I call repair man, should I replace the 24V wiring and contactor? Should I replace the blower motor? Thanks to all suggestions, in advance.

    You will need to disconnect all low voltage wires from each circuit and test each cable or bundle for shorts and continunity.

    To stop the transformer from burning out after you test all the wires and decide to replace the transformer again I sugges you install a fuse in the low voltage circuit. Attached is a drawing that shower the circuit to fuse. In the drawing it showes a miniature circuit breaker but you will probably never find on and that is why you need to install a fuse holder and fuse where the circuit breaker is. NOTE Ignore all other wiring on drawing except the transformer to the R low voltage circuit.

    NOTE make sure you are using a transformer designed for the power supplied to it. In your case 240 volts primary as stated in your post.
    Attached Images
  1. File Type: pdf LennoxCBX32MV[1].pdf (175.4 KB, 372 views)
  2. jsemelgar's Avatar
    jsemelgar Posts: 5, Reputation: 1
    New Member
     
    #3

    Aug 26, 2008, 10:04 AM
    My Solution:
    The contactor was burned out (perhaps shorted) at the wound coil. This was causing the transformer to burnout. I bought a new transformer with a reset switch and a new contactor.

    I want to VERY MUCH thank HVAC1000 for his assistance.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Aug 26, 2008, 11:46 AM
    Glad you got it going.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

24 V Transformer Bad, No AC [ 2 Answers ]

One hot Summer day, My Central Air went out, but the fan continued to run even when the thermostat was turned off. The smell of burnt electrical wiring throughout the house. I removed the front cover of the air handler, unplugged the 120 VAC power cord and When I checked the circuit it was...

24v transformer [ 2 Answers ]

Need wiring diagram to wire in 24v transformer I have gas furnace and a regular condensing unit not a heat pump. Fan relay side is 120 v . Had old style fan relay which is no longer available was sold new trans with plug in fan relay. Wall thermo cycles condensing unit but blower fan in furnace...

Transformer [ 1 Answers ]

I have a Goodman Heat Pump. The transformer in the air handler burnt out and I replaced it with one protected with a reset button. Now, when I use unit, I can only use in emergency heat. When I use in heat or cool mode it will trip the transformer in 30 seconds. Is this a low voltage problem? Air...

Transformer Hum [ 2 Answers ]

I have a new lennox 2 stage furnace. The furnace works fine except that the 24 volt transformer hums so loud that you can hear it through the ductwork when the furnace is off. I have tried to isolate the transformer but have not been successful. Any advice?

Transformer [ 1 Answers ]

Hi guys I'm having trouble finding a replacement transformer for my heating unit. The model number is AT140B1123. It's a Honeywell product but I can't find it on their website. Thanks Lou