    RHEEM A/C Unit blower motor won't start
    I have a problem with my RHEEM air package unit Air and heating, the blower motor won't start and it keeps blowing my 24v transformer, transformer literally blows up by doing an explotion noise. Now I am thinking that it might be the blower motor it self the one returnig High Voltage power to my transformer via the low voltage wires located in the motor. I already removed the low voltage wires from the motor but then I am afraid this would not work. Do you thing it might be OK to buy a new Motor?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    May 3, 2008, 05:45 PM
    The stongest possibility is a short in the 24 V wires heading to the relay. Disconnect bothe ends and do a continuity check between them and ground. There should not be any.

    There are other possibilities, but put a 3A fuse on the secondary of the 24 V transformer or buy an energy limited transfomer.

    Bet you can get the AC to start my manually moving the relay contacts. Do this forcibly and with something totally insulated. No 24 VAC required.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    May 3, 2008, 05:53 PM
    Your blower motor should not have low voltage wires going to it unless it's a DC drive variable speed motor. If it is a variable speed motor you will have two pin connectors going to it(they hook up on the bottom of the motor.) one with three large wires and one with 7 or 8 smaller wires. I agree though it sounds like you may have high voltage coming in on the low voltage side.
    martinco's Avatar
    martinco Posts: 6, Reputation: 1
    New Member
     
    #4

    May 4, 2008, 11:15 AM
    Quote Originally Posted by KeepItSimpleStupid
    The stongest possibility is a short in the 24 V wires heading to the relay. Disconnect bothe ends and do a continuity check between them and ground. There should not be any.

    There are other possibilities, but put a 3A fuse on the secondary of the 24 V transformer or buy an energy limited transfomer.

    Bet you can get the AC to start my manually moving the relay contacts. Do this forcibly and with something totally insulated. No 24 VAC required.
    From: martinco; Thanks a lot man! You are a genius.
    martinco's Avatar
    martinco Posts: 6, Reputation: 1
    New Member
     
    #5

    May 4, 2008, 11:34 AM
    Air conditioning Blower motor
    I diconnected the low voltage wiring leaving the transformer to the relay and there is no continuity with ground nor any continuity with the relay, now I talking about the relay that controls the speeds for the blower motor, do you think I might be a good idea to replace the main contactor relay? I checked the $$ and is only $24.00 to avoid the possibility that the relay coils are bad and passing high voltage into the low voltage.
    Please advice, thank you.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    May 4, 2008, 02:32 PM
    You missed what I said:

    Disconnect the wires to the relay.
    Disconnect the transformer.

    Now measure across the wires that went to the relay.
    Measure from each disconnected wire to ground.


    What happened when you puched on the relay contacts? You can only do this if they are exposed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Rheem RACB-030JAS residential A/C unit condenser fan motor replaced [ 26 Answers ]

I just replaced the condenser fan motor and it initially spun up then stopped, after 10 minutes it ran again then stopped. Now I can hear it buzz then stop but not spin. The original motor was a GE 5KCP39BG K075CS 1/6 HP 1075 RPM 208/230 V its replacement a Dayton 4M205G 1/4 hp 1075 RPM ...

Rheem furnace blower motor won't turn on [ 2 Answers ]

My furnace blower motor will not turn on. The troubleshooting guide says to replace blower motor but the diagnostics says the Limit Switch is Open any ideas

Rheem AC/Heating unit blower motor [ 2 Answers ]

How hard is it to change a blower motor on a Rheem Criterion heating/airconditioning?

Heating unit blower motor [ 2 Answers ]

The blower motor when out on my rheem furance the heating company told me it would be about 800.00 to replace does this sound about right please let me know joe 773-230-1148

Rheem Classic 90 Plus Blower start issue [ 11 Answers ]

The blower started acting up for few weeks. There was a several consistent short rumblings of the blower, something like half second on and half second off after ignition. Once the rumbling is over, the blower fan just works fine. I can also hear the relay inside the control box clicks when it...


View more questions Search