    240V space heater to 208V supply
    I purchased a used construction 240V space heater (4.8KW) 12/2 cabtire wiring (rated 20A).

    Can I connect this to a 208V supply or must I re-size any items in the space heater
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 1, 2007, 07:52 AM
    A 4800 watt unit will draw 20 amps at 240 volts, and 23 amps at 208 volts. Either way, this unit must be fed by a 30 amp circuit with all #10 wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Thermostat for 240V, 5000 Watt electric space heater [ 6 Answers ]

I have a garage electric heater (without thermostat) which I want to wire to a thermostat. The heater is rated 240 volt, 5000 Watt. First, can you suggest any particular thermostat that will handle this line load (I've only been able to find ones that handle up to approx. 3800 Watts) and, lastly,...

Replace 240v Water Heater Circuit with 120v Receptacle? [ 4 Answers ]

I have a 240v electric water heater that I am getting rid of (going NG tankless). Can I use the now unused 240v wire that comes from the breaker panel as a 120 volt receptacle so I can have a plug on the wall where the old electric water heater was? The new tankless water heater is going...

Can 208v be a substitution for 240v? [ 3 Answers ]

I've got a true 3ph 100A service and a 240v Cold Saw (for cutting steel). Can I rewire this saw for use in my 208v service? Obviously if I just grab 2 hots and the N I'll only get 208 across the poles and 120 at each leg, so I would assume that I would lose efficiency at the very least. But can...

Connecting 240v heater to 2 - 1 pole breakers [ 2 Answers ]

I have 2 - 15amp tandem breakers - both are 1 pole. I know that normally you would use a 2 pole breaker to create a 240v feed to the heater. However, if I connect my 12-2 wire to the 2 different breakers, I get 240v and my heater works correctly. Is there any problem to doing this rather than...

120V heater tape off a 240V source. [ 3 Answers ]

Hi, My question is very similar to HandyJohn's and much my question was answered in is post. Mostly verifying my suspicion of needing a step down transformer here. Just wondering if you know of any simpler options I may be overlooking outside of running a dedicated line. Here's my...


View more questions Search