    Why does furnace vacuum tube need to be clamped off?
    Lennox gas furnace flame goes out reignites goes out etc. New circuit board installed. Exhaust vent clean. Exhaust blower clean working. Will only continue to burn if vacuum line is disconnected from sensor and clamped off. What is probable cause?
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #2

    Jan 12, 2008, 07:22 AM
    Blockage in condensate trap? Restricted air intake?

    The sensor you are referring to-could it possibly be a pressure switch? (round disc shaped thingamabob with 2 wires and 1 or 2 rubber hoses connected).
    Den53nis's Avatar
    Den53nis Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 12, 2008, 07:47 PM
    Yes, It is the pressure switch. A New one was tested same problem so that's not it. The vent blower was taken off and checked for blockage all Ok. Air does not appear the problem. What is the Condensate trap??
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #4

    Jan 13, 2008, 07:36 AM
    Quote Originally Posted by Den53nis
    Yes, It is the pressure switch. A New one was tested same problem so thats not it. The vent blower was taken off and checked for blockage all Ok. Air does not appear the problem. What is the Condensate trap????
    A condensated trap is used in high efficiency furnaces to allow the water in the secondary heat exchanger and collector box to drain properly. It's usually plastic, sits in the blower compartment, or right outside the furnace. It typically drains out of 1/2" CPVC pipe or some such into a condensate pump.

    They are not found on 80% efficiency furnaces-just the higher efficiency models. Higher efficiency furnaces extract so much heat out of the vent gasses that the gasses actually reach a temp below dew point in many cases, and condensate is extremely heavy.

    Did the pressure switch have 2 rubber hoses on it or just 1?

    Check for a split in the hose and make sure the unit is sealed tight (for example if the cover is off the burner enclosure, put it back on with its proper seal. If the seal is destroyed, seal it back up with Hi Temp RTV-a red silicone based caulk. It is extremely important to have ALL seals intact on a sealed combustion unit, otherwise pressure switch failure can occur as the negative pressure it needs to engage is not developed when the inducer comes on... it just sucks air through the leak (air, like water, will seek the path of least resistance)
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #5

    Jan 13, 2008, 08:14 AM
    Quote Originally Posted by Den53nis
    The vent blower was taken off and checked for blockage all Ok.
    When the inducer blower was taken apart to inspect, was it sealed properly when being reassembled? If not, you maybe adding to your problems. You have to be sure the seal between the inducer and its mounting is totally sealed as well. Not getting a good seal can cause the pressure differential issue you now have and can allow condensate to leak out of the inducer halves or mounting.

    How old is this furnace? Has the exchanges been inspected?

    Eric D
    Den53nis's Avatar
    Den53nis Posts: 4, Reputation: 1
    New Member
     
    #6

    Jan 13, 2008, 06:34 PM
    The blower is sealed. The hose is not leaking. The furnace is 13 years old. Not high efficiency. Only one hose to the pressure switch. Everything mentioned has been checked, and the same problem exists. The flame is full for 10 seconds with vacuum hose attached and then full shutdown of flame. With hose disconnected and plugged works fine.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #7

    Jan 13, 2008, 07:07 PM
    Sounds like you have the wrong pressure switch for the job. If you had the right pressure switch for the system and the pressure switch tube was not hooked up the furnace would not work.
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #8

    Jan 14, 2008, 09:45 AM
    Quote Originally Posted by T-Top
    Sounds like you have the wrong pressure switch for the job. If you had the right pressure switch for the system and the pressure switch tube was not hooked up the furnace would not work.
    I agree-sort of. It sounds like the pressure switch is NormallyClosed and proving, but should be NO, and proving on the draft? But all models I've worked on wouldn't fire at all if pressure switch failed on call OR reset (returning to open state). The old carriers with the little inducer board up top... those can be finnicky-but this is a Lennox.

    It's not high efficiency, but has a pressure switch? Hmmm... that's a bit odd in itself. Must be a "chimney friendly" type furnace.

    Honestly, this is starting to get a bit drawn on... and I'm a bit concerned. It may be nothing, but I would certainly have this checked out by a technician. I like to err on the side of safety when it comes to gas and electric. Bad things tend to happen if you don't...
    Den53nis's Avatar
    Den53nis Posts: 4, Reputation: 1
    New Member
     
    #9

    Jan 14, 2008, 03:21 PM
    I have had two separate technicians both of which are stumped. The factory rep has been called. Thanks for all of the posts
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #10

    Jan 14, 2008, 03:48 PM
    Quote Originally Posted by Den53nis
    I have had two separate technicians both of which are stumped. The factory rep has been called. Thanks for all of the posts
    Dennis,

    When you do get it figured out how about a follow-up reply to let us know what you found?

    Thanks,

    Eric D

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

? Safe to bypass vacuum switch to test furnace ignition? [ 3 Answers ]

I have two Amana 80 SSE IIO units. One just stopped igniting. The trouble indicator light was blinking 2x to indicate the vacuum switch was stuck closed. I made sure the tube was clear, and applied suction to the tube to and could hear the switch activate. The trouble light shows clear now....

Vacuum breaker [ 2 Answers ]

I know there is a way to plumb a dishwasher in without having a vacuum breaker on your sink but I have forgotten how. Can someone help me?

Vacuum breaker [ 2 Answers ]

I would like to install my dishwasher without a vacuum breaker on my sink faucet. I have a garbage disposal. I understand that I can install the dishwasher through the garbage disposal without a vacuum breaker but I do not know how. Can you help ?

Best vacuum cleaner? [ 2 Answers ]

I am thinking about buying a new vacuum cleaner and would like a recommendation on one that you have found to be good at really suctioning up the dirt. Price is not a factor.


View more questions Search