New Member
|
|
Jul 11, 2007, 01:51 PM
|
|
|
No power out to my thermostat
Hi
Can anyone help I replaced a thermostat (ruud) because the power was always on
The fan kept blowing even when the unit have been turn to the off position and the fan was on the auto position
Now nothing comes on I checked the trasformer where it has 120 coming in but no power coming out where it should show 24v
I have a black wire connected from the t-tat to the 120 then checked to see if any power would be present but no luck yet
Can some one tell me what is happening here pleaseeeeeeee
Greatly appreciated
|
|
|
 |
Uber Member
|
|
Jul 11, 2007, 02:24 PM
|
|
|
You should not have "black wire connected from the t-stat to the 120". Dangerous.
Most common and basic of Central Air is 240 volts to Air Handler, and 240 Volts to Outside Compressor Unit.
In the Air Handler is Transformer, usually 240 volts to 24 volts.
24 volts goes to Thermostat Red, then if you connect to Green, fan will run. Or turn to cool.
Yellow or blue for cool( puts 24 volts out to compressor contactor), White is sometimes
Heat.
There is in depth info at start of heating and AC(Sticky). Very Possible added info there
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Jul 11, 2007, 02:25 PM
|
|
|
It sounds as simple as a bad 24 v transformer. Before replacing check to insure the screws are tight. The tansformer is a common item at home centers, $30.
|
|
|
 |
Uber Member
|
|
Jul 11, 2007, 03:30 PM
|
|
|
Did you check the power at the transformer or furnace terminals? Newer furnaces have a fuse on the control board, much cheaper and easier to replace than the transformer. If you don't have a fuse, I would pick up an inline one and wire it in to make sure the new transformer doesn't follow the old.
Note, most furnace-A/C systems the blower and control transformer run off the 120 volt.
|
|
|
 |
Ultra Member
|
|
Jul 11, 2007, 09:45 PM
|
|
|
If you are testing the transformer, and you have 120 volts going in and nothing on the secondary side, then you have a bad transformer. Do some testing to make sure there are no shorts, also take the above advice, install an inline fuse, it can save you a transformer.
|
|
|
 |
New Member
|
|
Jul 26, 2007, 07:38 PM
|
|
|
My transformer has 3 wires blue which I don't have it connected to anything
Red not connected as well
Black to the 123v which reads 122v when checked with a meter
On the other side of the t-stat I have 2 yellow wires both of then read 1.9v
I have one going to t-stat and the other to the terminal #1 on the sequencer ithink that is the name is a black thing with numbers from 1-6
One yellow wire from transformer to the 1 terminal which reads 1.9
Terminal 2 reads 1.8v
Terminal 3 reads 122
Terminal 4 reads 122
Terminal 5 and 6 0v
Still no power to my t-stat
Can you please help with my big problem 122v primary 1.9v on secondary
|
|
|
 |
Uber Member
|
|
Jul 27, 2007, 06:30 AM
|
|
|
Looks like bad transformer, blue and red unused wires probably different taps for primary.
Black is 120 primary, blue and red, may be 240 volt, or 277 volts.
With no load, measure voltage in and out. Do cap off red and blue.
Is the breaker for your ac 240 volts? Wondering if half of breaker tripped.
|
|
|
 |
New Member
|
|
Jul 27, 2007, 01:44 PM
|
|
|
Well coming out of the breaker have a black wire and a white both of them read 122v
I'll change the transformer and see if that fixes my problem
Thank you for your help greatly appreciated
|
|
|
 |
Uber Member
|
|
Jul 27, 2007, 01:53 PM
|
|
|
The black and white are both on breaker? If you put leads on black AND white, Do you get about 244 volts? If so, you may need a 240 volt to 24 volt transformer.
|
|
|
 |
New Member
|
|
Aug 1, 2007, 12:49 PM
|
|
|
Do I need to connect the black and white out the breaker to the black on the transformer or just to the black out the breaker
Because I a 120 volts to 24 volts and connected black from transformer to the 120volts out the breaker and I cannot get any reading on the 24 volts side (secondary)
Help please
|
|
|
 |
Uber Member
|
|
Aug 1, 2007, 03:21 PM
|
|
|
Very Important! Don't know if I'm missing it. I know you get 120 from black and white.
If you put meter on black, and one lead on white, You may get 240 volts?
You got a 120 volt primary transformer? If so may have harmed transformer.
Use appropriate tap if wrong(240) Not black wire.
You can measure resistance on transformer. If primary or secondary are opened, will
Not work.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
No power to thermostat
[ 19 Answers ]
Hi,
I was trying to replace my old stat with a new programmble one. I had turned off the furnace before installing new one. But the new one didn't work and so, I put the old one back on. But the old one does not power now and display on the old stat does not come up. Can any one help me here...
No power on thermostat
[ 1 Answers ]
Help!! This morning we woke up to a freezing second floor. It is on a second unit, and when I went upstairs, the thermostat has no reading at all... no power. I checked the breaker and all was fine there. Is there an exterior switch on the unit that could need to be powered up?
No power to thermostat, no fuses
[ 15 Answers ]
I have a International Comfort Products heating and AC unit. The problem I am having is that the blower runs constantly and there is no power to the thermostat. I can find no fuses on the unit. None indicated in the schematic either. The transformer checks out OK, the wirng checks out OK also. Any...
No power to thermostat
[ 2 Answers ]
I recently had a pool heater installed. The electrician installed it to the incorrect voltage. We found this out when we tried to power up the pool heater. Right after he came back and installed it to the correct voltage, the thermostat and heat pump to my house quit working. It is getting no...
No Power to Thermostat
[ 2 Answers ]
We have two electric central A/C units - one upstairs, one down. We discovered that the upstairs A/C unit was running 24/7 making the upstairs very cold (and a $680.00 electricity bill). The original Honeywell programmable thermostat was not shutting it off regardless of the room temp -vs-...