Hi, We had a contractor come over to look at our Air Conditioning Unit. We had an American Standard R-22 Allegiance 12. He said that the Condenser was "Grounded Out" and we needed to replace the condenser or alternatively we should replace it with a new system altogether. Are there other alternative reasons this could happen? The fan did not immediately go on, but he said that it probably would have gone on. The Condenser did not go on at all. Not exactly sure what "Grounded Out" means. He said that American Standard R-22s are not in existence anymore and he recommended Payne. His charge is 3K+ which includes a new Payne and labor and other gasses etc... Not sure if that is reasonable or not. Of course, I think it sounds high. Cheers and much thanks in advance.
|
|
|
 |
Ultra Member
|
|
May 15, 2010, 12:03 PM
|
|
|
Grounded out means the compressor wiring is bad. This is not always the case, could be a burnt wire at the compressor or the contactor. If it is grounded out the breaker would trip every time you turn on the ac. Also the fan will run if the compressor was unhooked witch needs to be done in order to see if it is grounded out.
|
|
|
 |
New Member
|
|
May 15, 2010, 05:45 PM
|
|
|
Thanks very much Joshdta. If it is Grounded Out, does this mean it definitely needs to be replaced? And, if it is burnt wire instead, is it fixable and can a non-handy man like me replace it?
He did say that the breaker tripped multiple times, but I was not there to witness it. He definitely did not unhook the compressor and so I do not know if the fan was running.
Again, your help is very much appreciated!
|
|
|
 |
Ultra Member
|
|
May 15, 2010, 05:55 PM
|
|
|
Hang on a minute. Original post said "condenser", not compressor. Two completely different things. If the compressor is bad it is a big deal, and it's always cost effective to change the system. A bad condenser motor isn't such a big deal. However, R22 systems are obsolete and a new system is in order.
|
|
|
 |
New Member
|
|
May 15, 2010, 06:25 PM
|
|
|
Missouri Bound - Went back through my notes. You are right. He said the Compressor was grounded... not the condenser. Thanks!
|
|
|
 |
Ultra Member
|
|
May 15, 2010, 06:33 PM
|
|
|
Well you can test it yourself if you have a ohm meter
|
|
|
 |
Ultra Member
|
|
May 15, 2010, 06:35 PM
|
|
|
I suggest you call a couple of other contractors to give you an estimate. That will give you a price range to consider, and an option to check references. Take the time to check out your options.
|
|
|
 |
Ultra Member
|
|
May 15, 2010, 07:25 PM
|
|
|
How old is your ac unit? The American Standard Allegiance 12 should have a 10 yr compressor warranty!
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Air conditioning unit-heat pump-air smells moist
[ 3 Answers ]
The air coming from my vents smell as if something may be wet. I know that sounds crazy, but could the air be passing through some moisture source? We have the heat on at the current time. Last week we had the air on, I smelled this same smell. The air filter had this particular smell on it, like...
Air Conditioning unit
[ 5 Answers ]
Since 6-29-09 the company has been trouble shooting why my unit is not working. It started the breaker trip and they put in a new motor, that wasn't the answer. They told me to call an electrician to install a new breaker I did that. Keep in mind my compressor was working per the technican, the new...
Air conditioning unit
[ 0 Answers ]
My central unit is rattling. It burnt up my motor and I just bought another one but it is rattling also. What could the problem be.
No Air Flow in the HVAC unit
[ 1 Answers ]
Hi,
I have a Trane Xe 1200. It was working fine till couple of weeks back, but last week I noticed that the rooms were not getting cold after a long time. On checking the vents found that even though the thermostat says it is ruuning, there was very low to none air flow coming through the ducts,...
Air conditioning unit blowing warm air
[ 2 Answers ]
I live in an apartment with a heating and cooling system that uses water pipes. I'm not familiar with this. My air conditioner blows warm air and when the man from the A/C company comes to check it. He says it's working fine but then a few days later it happens again. What is going on?
View more questions
Search
|