Hi I have auto. Irrigation sistem but die computers have to start a pump the output voltage of the computer is 24vac so I have got a 24vac contactor and only coneccted the live wire from my computer and the other point of my contactor that's marked C I have hooked up to the neutral of my 220vac (home power) but it doesn't work why?
|
|
|
 |
Uber Member
|
|
Mar 4, 2012, 07:37 AM
|
|
|
You can't get 220/240 volts off the neutral.
Are you saying your computer outputs 24 volts ac?
Or your computer power supply?
You should be able to apply 240 volts to the transformer primary, and have the secondary 24 volts go to the contactor. The transformer needs to be large enough for the contactor coil, and the contacts need to be rated for your load(pump).
|
|
|
 |
Uber Member
|
|
Mar 4, 2012, 07:44 AM
|
|
|
Where are you located?
|
|
|
 |
Uber Member
|
|
Mar 4, 2012, 08:46 AM
|
|
|
When I saw the 220, I thought they may not be from around here?
|
|
|
 |
New Member
|
|
Mar 4, 2012, 11:18 AM
|
|
|
The computer output is 24v ac, you see I have 24vac from my computer that supplys a commen port(neutral) and my station 1(between commen and my station 1 I get 24vac).But the contactor and the motor are a long distance from my computer so I wire only one wire and at the motor I picked up a neutral. The I should be able to get 24vac?
|
|
|
 |
Uber Member
|
|
Mar 5, 2012, 06:58 AM
|
|
|
You don't say the amount of current the 24 Volts out of the computer has.
See if the contactor energizes when connected to the computer and watch the voltage as you connect. If the voltage drops significantly, and doesn't energize, you need a more sensitive relay(less coil current).
Your pump and computer wiring will have NO connections between them.
Computer only connects to the contactor coil. And your pump only connects to the contactor contacts and your source of power(220).
|
|
|
 |
New Member
|
|
Mar 5, 2012, 11:24 AM
|
|
|
Thanks for all your answers the main problem was that I tried to take the live wire from my computer that supply's 24v between conmen and station 1, I only took the station 1 wire and picked up a commen at another cb-bord(from the neutral bar). The problem is when you take 220 and convert it to 24v it becomes positive and negative and it's like taking 2 car batteries and take a positive from the one and a negative from the other one... it would just not work!!
|
|
|
 |
Uber Member
|
|
Mar 5, 2012, 12:28 PM
|
|
|
A Transformer increases, decreases, or the mantains the same voltage(isolation), It doesn't convert to DC. Rectifiers will convert to DC. You have more than a transformer.
When you say computer, I take it you mean the Sprinkler Timer/Controller?
Is the Pump to run as each zone is active, Can you tell more what you are wanting to do?
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
24v Transformer
[ 4 Answers ]
I am trying to find a good source for a 24v transformer. I am working on a project that will use a digital home thermostat to control a couple of 24v relays. I've found all of the parts but a suitable, cheap, 24v thransformer. I thought this would be the easiest part to find but it is turning...
24v transformer
[ 4 Answers ]
How do I wire up a 24v transformer in a furnace for thermostat? What does 24v & 24vA connect to? I have a problem of fusses blowing when I turn on the furnace.:confused:
How does heating transformer work?
24v transformer
[ 2 Answers ]
Need wiring diagram to wire in 24v transformer I have gas furnace and a regular condensing unit not a heat pump. Fan relay side is 120 v . Had old style fan relay which is no longer available was sold new trans with plug in fan relay. Wall thermo cycles condensing unit but blower fan in furnace...
24v Transformer Keeps Blowing
[ 2 Answers ]
I have a GE Smart Home low voltage switching system in my 1955 home. My transformer (120vac/24vac 40va) keeps blowing and I have since read that I should add an inline fuse to the 24v side to avoid blowing the transformer. My question is, how do I find the short? There are many low voltage wires...
How does a 24v transformer work
[ 4 Answers ]
My A/C unit stopped working during the night and I could not turn on the heat or air. I recently had to replace my 24V transformer so I thought to replace it first. When it came in I installed it and everything worked for about 30 seconds before the transformer got hot and everything stopped again....