Heil 5000 HVAC
I have a Heil 5000 central air unit. The compressor or the unit it outside keeps tripping the breaker. If I let it set for a few hours, then I can reset the breaker and it will run just fine and cool the house. But after a while, a few hours I'm guessing, it will trip the breaker. Although I have not had the time to sit around and babysit it to see actually when the breaker is tripping, I have a hunch when it is. Now I am not very familiar with AC units, I am rather mechanically and electrically inclined. If I am correct these compressor work with the same principle as a regular air compressor, when they start a pressure relief valve is activated so that the motor can start and come up to full running speed before the compression actually starts. I did a little research and discovered that this compressor requires a minimum circuit ampacity of 25.5 amps. The wiring and circuit breaker was 10 awg on a 30 amp breaker. Now if you take into consideration the rules of electrical theory, you are required to be about the circuit ampacity by 20%. Whichc would mean that 10 AWG and a 30 amp breaker is not sufficient. Now let me state that the compressor is requires 90 feet of conductor to get from the breaker panel to the compressor disconnect. I believe that I may have an issues with what I believe should be the pressure relief valve for start. Like I said, if I let it set for a while, I can reset the breaker and it will run fine. I believe that letting it set for a while allows the pressure to bleed of the high pressure side allowing it to start much easier and run properly.
Ok so that was a quick version of my issue. I welcome all and any input.
Thanks
|
|
|
 |
Uber Member
|
|
Aug 10, 2012, 04:25 PM
|
|
|
You can't relieve pressure without releasing Freon.
Many AC Techs or systems will have a delay so the compressor doesn't try to start with high head pressure, the delay helps.
I would use an Amprobe to see the current, could be a bad breaker or loose connections on the breaker or breaker buss.
|
|
|
 |
New Member
|
|
Aug 10, 2012, 04:47 PM
|
|
|
Ok so I forgot to mention that since I believe according to electrical theory that the conductor and bresker are too small I did replace the conductor and breaker. There is now new 6awg aluminum range cable for the conductor and a new 40 amp breaker and it still trips. I did use an amprobe bef
|
|
|
 |
New Member
|
|
Aug 10, 2012, 04:50 PM
|
|
|
Anmprobe and before I replaced the conductor and breaker it was pulling 110amps for the first 5 seconds and then would drop to it's normal running which was 15 to 16 amps. But that was only after I let it set for a while
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Aug 10, 2012, 05:41 PM
|
|
|
 Originally Posted by Buckslayer9000
Anmprobe and before I replaced the conductor and breaker it was pulling 110amps for the first 5 seconds and then would drop to it's normal running which was 15 to 16 amps. But that was only after I let it set for a while
Put a hard start kit on it and while you are at it check the run capacitor for the proper value. Many times a run capacitor will become weak from use or age and the run capacitor can be a cause of your type of problems.
|
|
|
 |
Uber Member
|
|
Aug 10, 2012, 05:43 PM
|
|
|
Likely a Compressor problem, you may get lucky and have bad connections or a bad capacitor.
|
|
|
 |
New Member
|
|
Aug 10, 2012, 07:33 PM
|
|
|
Ok awesome input. I have been pondering capacitor issues but I'm not sure what the value of these capacitors should be. I'm well aware of how to test them. But like I said, I just don't know what the value should be. Could you point me in that direction?
|
|
|
 |
New Member
|
|
Aug 10, 2012, 07:34 PM
|
|
|
Oh yeah definitely not a connection issues... I have checked that like 10 times because I keep questioning myself
|
|
|
 |
Uber Member
|
|
Aug 10, 2012, 08:18 PM
|
|
|
 Originally Posted by Buckslayer9000
Oh yeah definitely not a connection issues...... I have checked that like 10 times because I keep questioning myself
On the Compressor itself?
|
|
|
 |
New Member
|
|
Aug 10, 2012, 08:25 PM
|
|
|
On every connection even related to the compressor
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Heil 5000 High Efficiency air-conditioner will not cool.
[ 2 Answers ]
Hello,
Florida summers at 95-degrees are terrible, especially when your air-conditioner stops working in the middle of it. :mad: Here are the symptoms:
- It's connected to a gas line. The heat works well, but when the cooling is turned on it blows out room-temperature air.
- The fan on...
View more questions
Search
|