Ask Experts Questions for FREE Help !
Ask
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #1

    Sep 29, 2009, 04:33 PM
    Goodman igniter not working
    I have a Goodman GMP125-5 Rev B. The flue fan starts up and then I hear a click like the igniter should be glowing, but it doesn't. I replaced the igniter last year. I also pulled it and there are no cracks. This is the first time I have attempted to use the heater since last spring. Thanks, Al
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 29, 2009, 05:13 PM
    Check the board where the ignitor plugs in for power/voltage. You will have to figure a way for your meter to stay attached while you start the furnace. Also check the board for the number of blinks. The blink code will be on the wiring diagram on the back sode of the blower access door.
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #3

    Sep 29, 2009, 05:19 PM

    I get continuous blinking, and I don't have a voltmeter handy. When I fired up the A/C earlier this year the condensation was stuck and got the circuit board wet. I wonder if that got fried?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Sep 29, 2009, 05:26 PM
    OUCH it is a good possibility the board is toast but it is always best to test. You could hook a light bulb with some wires attached to the terminals for the ignitor power test but you should have a meter and know how to use it for proper testing.
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #5

    Sep 29, 2009, 06:00 PM

    I found a small test light. Tested OK on an outlet. Plugged in to the 2 wires going to the ignitor. Flue fan turned on, about 10 seconds later I got one dim split second flash on the test light, then a couple of seconds later I hear the click and no power on the test light after that.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Sep 29, 2009, 09:21 PM
    The power to the ignitor should have stayed on longer than that. Any blinks on the circuit board? How many?
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #7

    Sep 30, 2009, 05:45 AM

    Continuous blinking on the circuit board light.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Sep 30, 2009, 06:50 AM
    Look below and you might also look on the back of the blower door for a diagram.
    Attached Images
  1. File Type: pdf Doc1.pdf (40.4 KB, 264 views)
  2. agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #9

    Sep 30, 2009, 07:41 AM

    What is the action required for error code "flamed sensed no call for heat"?
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #10

    Sep 30, 2009, 07:43 AM
    Do I need to clean the Flame Sensor with emory cloth?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Sep 30, 2009, 08:09 AM
    You can try to clean the flame sensor but the board might be shot as was mentioned before.. BTW you are never to touch the ignitor (black/gray) area with your bare hands.
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #12

    Sep 30, 2009, 08:15 PM

    I tested the wire for the ignitor all the way back to the board and no power. Found out it was a stuck relay on the board. I gave the relay a couple of taps and the ignitor kicked on. The heat is on. Thanks for all your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Sep 30, 2009, 09:03 PM
    Usually the relays cannot be replaced and if it was stuck the board is not safe to be trusted since all the safety devices use the board. I suggest you obtain a replacement ASAP especially since cold weather is around the corner and you would not want to experience a board failure when it is real cold outside.
    agreiser's Avatar
    agreiser Posts: 8, Reputation: 1
    New Member
     
    #14

    Oct 1, 2009, 07:53 AM

    Thanks for all your help and advice. I will replace that board ASAP. Best Regards, Al
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #15

    Oct 1, 2009, 08:15 AM
    No problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace not working after turning off and back on [ 6 Answers ]

Hello, we purchased a Goodman furnace June 2006. When we turn off the furnace, and turn it back on, the furnace does not work. I've left numerous voice mail and text messages for Air Kings in Columbus, Oh and they do not return my call. This is the company that installed the furnace. It is 30...

Goodman heat pump not working properly [ 5 Answers ]

I built a new house 6 months ago and had a co-worker/friend (20ys hvac experience) install my hvac. A goodman GPH15 packaged heat pump 3.5 ton with a honeywell th8320 thermostat. The air worked great in the summer but the heat is not working properly. He has been out many times trying to solve...

Goodman furnace igniter stays on 20 sec with pilot light [ 1 Answers ]

Have a Goodman forced air unit in my garage, was used only now and then, a while ago it started this... turn furnace on and igniter comes on and lights pilot then stops for a second then comes back on for about 20-30 seconds... all this time pilot is light and strong... then igniter stops and...

Goodman Gas Furnace Not Working [ 2 Answers ]

I have a Goodman Model # EG030075-1AB REVC Gas Heater it has been converted to run on LP Gas. Furnace has worked fine for years. Turned the heat on and nothing happens. The LED on the control board is not lit. I checked the voltage at the control board and all the voltages appear to be normal. ...


View more questions Search