The heater wouldn't run, the blower would come on but no heat because the burners wouldn't come on. A technician got it to run again until it came up to temperature, then it stopped. Then we replaced the pressure switch, the ignitor and the transformer and we got the burners to come on and it ran for about 12 hours. It wouldn't come on again and we were getting three blinking lights from the ignition control panel still, which the manual says that the blower vent is blocked. Once we checked the old transformer after we had the new one installed, we were getting 24 volts. Then we replaced the ignition control panel and put the old transformer back on because it had spades in it that we could use. The heater isn't running and we're still getting three blinking lights from it. We checked the voltage of the transformer and we were getting the correct 24 volts to the pressure switch. We didn't replace the limit switch that plugs into the pressure switch. Is it possible that the limit switch that's connected to the pressure switch is open and not closed?
|
|
|
 |
Ultra Member
|
|
Dec 20, 2011, 07:53 PM
|
|
|
Have you checked to make sure the flue vent is clear, the obstruction could be in vent pipes or even inside the inducer motor housing, many times if all else fails you have to remove inducer motor and housing and give it a good shaking, might be surprised what might fall out
|
|
|
 |
New Member
|
|
Dec 20, 2011, 08:24 PM
|
|
|
OK,thank you and we'll try removing the inducer motor and housing and as you suggest. I appreciate the quick reply and suggestion.
|
|
|
 |
New Member
|
|
Feb 17, 2013, 01:05 PM
|
|
|
 Originally Posted by wmproop
have you checked to make sure the flue vent is clear,,the obstruction could be in vent pipes or even inside the inducer motor housing,,many times if all else fails you have to remove inducer motor and housing and give it a good shaking,,might be surprised what might fall out
How do you clear a flue vent? Where is the inducer motor & housing?
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Goodman furnace blower fan issue
[ 7 Answers ]
Just started up furnace for the year. Ran OK for a day. Now furnace ignites then blower fan starts will run, stop for a bit, start again, stops, and eventually it starts again and runs until temp is maintained to thermostat setting.
Goodman furnace issue
[ 0 Answers ]
I own a gpd1004 sn-0104625001. I have had 2 hvac companies checking my gas furnace.
Neither could find out the problem..
My furnace was bought new in 2001 9yrs. Old.
The problem is, it will try to turn on, igniter will come on , inducer will come on, but no gas will come out. Then it shuts...
Goodman Furnace electrical issue
[ 48 Answers ]
Have a new Goodman furnace that has a peculiar issue. The furnace will heat just fine and burners will shut off normally when set point is reached. After the burners have shut down, the blower will run for a minute or so then it seems as though it is given a signal to stop then immediately...
Goodman furnace issue
[ 5 Answers ]
Had a Goodman furnace model # GM 80903 BN installed a year ago, right from the start, the problem started with the burner not igniting when the blower moter is running continuously. I have to have the motor running continuously for the particular model of air-cleaner I have to work properly. So...
Goodman Furnace Issue - Heater won't work, no fire
[ 1 Answers ]
My Goodman heater won't fire up. When I turn the heat on, the sequence of events:
1) Small fan at top section turns on.
2) Heating element turns on, bright red. The system sounds like it is trying to turn on.
3) Then the bright red goes off. The fire does not light. The fan does not start
4)...