New Member
|
|
Oct 12, 2010, 12:43 PM
|
|
|
Goodman control board not sending power to ignitor?
I have brand new goodman furnace, AC part works fine, but when I turn it on heat the draft inducer motor never starts. I checked there is no power coming to it from the control board.
|
|
|
 |
Plumbing Expert
|
|
Oct 12, 2010, 04:06 PM
|
|
|
Jump r and w on the control board and let me know what happens. Make sure the blower compartment safety switch is pushed in while running this test, otherwise you will not have power to the control board.
|
|
|
 |
New Member
|
|
Oct 12, 2010, 05:17 PM
|
|
|
Comment on mygirlsdad77's post
After I jump r and w the red light flashes 3 times, indicating pressure switch failure. But the draft inducer fan never starts so I am thinking its not pressure switch problem.
|
|
|
 |
Plumbing Expert
|
|
Oct 12, 2010, 05:23 PM
|
|
|
If a pressure switch is stuck closed, it will not allow the draft induce to start. Try disconnecting both wires from both pressure switches and let me know what happens.. If this is a brand new furnace, I really think you need to have the installer back to trouble shoot the furance. Doing work on the furnace yourself will void warranty. If you installed the furnace yourself, then warranty is already void, in which case I will try to help as best I can.
|
|
|
 |
New Member
|
|
Oct 12, 2010, 05:32 PM
|
|
|
Comment on mygirlsdad77's post
I thought there was only one pressure switch, This is a GMS8 Single stage furnace, I Tried disconnecting wires from one pressure switch no change, blower did not start.
|
|
|
 |
Plumbing Expert
|
|
Oct 12, 2010, 05:49 PM
|
|
|
Sorry, your correct. Only one ps on your unit. Now, bear with me here. There are anywhere from one to three flame rollout switches on you unit Located directly above the burner assembly. They are small switches with a small button in between two wire connections. Press on the small button and if you feel or hear a small click, then the limit was tripped and the click reset it. One step at a time here, as its hard for me to diagnose without having my hands on the unit.
|
|
|
 |
New Member
|
|
Oct 12, 2010, 05:59 PM
|
|
|
Comment on mygirlsdad77's post
I will try the rollout switches first thing tomorrow. This furnace is in the rental unit so I can work on it only during day hours. Do you have any suggestions on what else to try if its not the rollout switch.
|
|
|
 |
New Member
|
|
Oct 17, 2010, 09:18 PM
|
|
|
I finally got this furnace to work. What happened was that some water got to the control board and made it malfunction. Had to replace whole board ($60 at local goodman distributor), and a pressure switch which was also bad ($14)
|
|
|
 |
Plumbing Expert
|
|
Oct 18, 2010, 04:09 PM
|
|
|
Glad you got it fixed, and thanks for the update.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Goodman gmnt080-4 ignitor
[ 7 Answers ]
I have a Goodman GMNT080-4 Furnace. It would not ignite, I changed the ignitor and it worked for 2 weeks. This morning it failed to ignite. Could the ignitor have gone bad again?
Goodman and igniter or ignitor
[ 3 Answers ]
Goodman model GDT070-3B
Light blinks 3 times -- the codes indicate the info below.
Pressure switch failure to close -- Venter pressure switch vent blockage.
The small motor starts and then I can hear gas flow (can smell a small amount later) and then it shuts down. There is never a flame.
...
Goodman gpd075-3 ignitor
[ 0 Answers ]
I have a goodman gpd-075-3. The ignitor ignites for about 4-5 seconds then kicks off. It will do this every 1-2 mintues. Why won't it stay on?
Location of goodman ignitor
[ 2 Answers ]
I had a technician come out to check my furnace and told me that I need a new ignitor for a goodman furnace. He removed the ignitor and I ordered one online but I am not sure where the ignitor is located at within the furnace.
Power to furnace control board but stops there
[ 3 Answers ]
Hi
I was given a Nordyne KG6RA gas furnace. After installing, I turned on and there was a low hum when the power got to it. I held the door switch closed so I could see. After a few seconds there was a spark and then blue smoke and everything went dead. I could not see where the smoke came...
View more questions
Search
|