New Member
|
|
Mar 12, 2014, 06:01 AM
|
|
|
Gibson furnace not running
Hi, I have a Gibson kg6rk that has locked out. I got 1 light flashing ,inducer motor running and doing nothing else , no power going to pressure switch. I tried jumping ps to see if switch was problem didn't work, no juice found at switch wires. I replaced circuit board to no avail ,still doing same thing! Any help would be greatly appreciated live in suburb of Chicago and it cold. Thanks Greg
|
|
|
 |
Ultra Member
|
|
Mar 12, 2014, 07:46 PM
|
|
|
Can you please tell us the meaning of the blink code? There should be either a sticker (maybe inside the blower compartment door) or the key to the blink code could be printed on the circuit board. If you have the owner's or installation manual the blink code key should be in there as well.
|
|
|
 |
New Member
|
|
Mar 13, 2014, 03:22 AM
|
|
|
 Originally Posted by Grady White
Can you please tell us the meaning of the blink code? There should be either a sticker (maybe inside the blower compartment door) or the key to the blink code could be printed on the circuit board. If you have the owner's or installation manual the blink code key should be in there as well.
Hi,It is limit open circuit ,external load on "w".I checked power at board 69 volts at m1,123volts heat,123volts eac,123 volts transformer.thermostat is calling for heat 26 volts.I went on roof with inducer fan running good flow coming out. Nothing can get in flu.I bypassed pressure switch with furnace off then turned on still nothing right at start. Thanks for the help!
|
|
|
 |
Ultra Member
|
|
Mar 13, 2014, 05:34 PM
|
|
|
You obviously have a volt meter. Now it is a matter of tracing the limit circuit. Usually these limits are in the 24 volt control circuitry. The wiring diagram will help you determine which wires are in that circuit. It's a shame manufacturers won't make the various circuits in all furnaces a standard color.
One can also use an ohmmeter or continuity tester to look for open limits. To use a voltmeter, the power has to be on. With an ohmmeter or contiuity tester, you'd want the power off. Limits are all in series.
|
|
|
 |
New Member
|
|
Mar 14, 2014, 03:37 AM
|
|
|
 Originally Posted by Grady White
You obviously have a volt meter. Now it is a matter of tracing the limit circuit. Usually these limits are in the 24 volt control circuitry. The wiring diagram will help you determine which wires are in that circuit. It's a shame manufacturers won't make the various circuits in all furnaces a standard color.
One can also use an ohmmeter or continuity tester to look for open limits. To use a voltmeter, the power has to be on. With an ohmmeter or contiuity tester, you'd want the power off. Limits are all in series.
Hi there's no power on the limits circuit, no power at roll out switch, no power at any switches.
|
|
|
 |
Ultra Member
|
|
Mar 14, 2014, 07:02 PM
|
|
|
How are you checking for power at the switches, including limits & roll outs?
|
|
|
 |
New Member
|
|
Mar 14, 2014, 07:06 PM
|
|
|
 Originally Posted by Grady White
How are you checking for power at the switches, including limits & roll outs?
Volt meter
|
|
|
 |
Ultra Member
|
|
Mar 15, 2014, 06:36 AM
|
|
|
Sorry, poorly asked question. Where are you putting the probes? One should be on the common side of the transformer or low voltage common terminal of the board & the other should be moved from test point to test point. Another way is to put the probes on each side of the component in question. If you get no voltage across the component, that component is open & the source of the trouble. BTW: I saw you had 69 volts at terminal M1. What is M1 connected to? "M" usually designates a motor terminal. That voltage was measured to ground or neutral?
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Gibson furnace
[ 0 Answers ]
Furnace green light blinks continuously and motor kicks in like it is going to start but then shuts off
Gibson furnace?
[ 0 Answers ]
The fan on our gibson furnace will not shut off. We replaced the thermostat which didn't help. Any suggestions?
Gibson Inducer Constantly Running
[ 0 Answers ]
Hi All,
I have a Gibson gas furnace, and am having issues with the inducer. As soon as there is power to the furnace, the inducer starts running and doesn't stop until I cut power. The furnace will go through 1 heating cycle. But won't kick back in for a second cycle when called for. The...
Gibson Furnace
[ 9 Answers ]
Gibson Furnace will blow cold air sometimes instead of warm air. I believe it to be a problem with a wire because we had it worked on before. There are also two lights - one stays on continuously and the other one will blink. Is this something I can repair myself? If so, how? The furnace is...