Gas furnace problem Goodman model# GMP075-3 revb
When it starts up everything appears normal, the induced draft fan starts for about 30 seconds, the glow plug gets red hot, the gas ignites, about 30 seconds later the main blower wheel spins. The hot air comes out of the registers and everything works great but only for about 5 minutes, then for some reason the flame stops and about 2 minutes later the main blower wheel stops? The only thing running is the small draft for about 5 minutes or so then it finally kicks off. All is now quite for about 15-20 minutes and the whole cycle starts up again. I cleaned the flame sensor and it did no good. Now this portion is very difficult to explain, but when everything stops there is a very slight "hint" of odor coming from the registers (almost unnoticeable unless you put your nose right next to it)... smell like maybe something electrical burning out or failing? My guess is maybe the main blower wheel giving out? IF that is it then why would the flame stop THEN the main blower stops, I would think it would be the opposite if it is the blower?
This all started a few days ago but it has gotten much worse (now I can not warm the house up at all).
I would greatly appreciate some good advice here, I'm unemployed.
Thank You Everyone
|
|
|
 |
New Member
|
|
Jan 31, 2010, 07:10 PM
|
|
|
I forgot to mention that this is a natural gas furnace and that the red light on the circuit board remains solid red (no blinking)
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 31, 2010, 07:13 PM
|
|
|
Is the filter clean?
Are all the registers open?
|
|
|
 |
New Member
|
|
Jan 31, 2010, 07:31 PM
|
|
|
NO, We have a 5 bedroom/3 full bath home and a few bedrooms and a bathroom we leave the reg. closed because they are never used (we have done this for years now)?
|
|
|
 |
New Member
|
|
Jan 31, 2010, 07:32 PM
|
|
|
And the filters is clean
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 31, 2010, 07:42 PM
|
|
|
The reason for the registers being closed is the fact that closing them can trip the high limit control which might give the same symptoms you are having now. Something in the control system is cutting the furnace off before the thermostat is satisfied. You need to check the circuits(usually with a meter) to tell which one is causing the problem.
|
|
|
 |
New Member
|
|
Jan 31, 2010, 07:53 PM
|
|
|
I was wrong earlier, about HALF the reg. were closed (idea was to save on heating bill, not a good idea I now realize). Will opening the reg. fix the problem... I just opened them all
|
|
|
 |
New Member
|
|
Jan 31, 2010, 07:54 PM
|
|
|
Also would you mind telling me eactly how to check the circuit board (circuits)
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 31, 2010, 07:58 PM
|
|
|
Well checking the circuit board is always left for last. I will provide you with a DL for your manual and you can take it from there. This is a Goodman factory manual and the best source for info around BUT pay attention since this manual covers many different models so make sure the instructions etc pertain to your exact unit model number.
http://www.hvacpartsshop.com/Gmph075-4%20Series.Pdf
|
|
|
 |
New Member
|
|
Jan 31, 2010, 08:01 PM
|
|
|
I can see opening all the vents is a bit too late now, same symptoms occurred (regardless I will leave them all open)
|
|
|
 |
New Member
|
|
Jan 31, 2010, 08:04 PM
|
|
|
hvac1000 thank you for your assistance.
May I ask are the circuits you are referring to on the circuit board?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 31, 2010, 08:48 PM
|
|
|
No they are limits/other control safetys like rollout switches/fan controls etc. That book I sent you has all the info but you have to be able to read it and understand what it says. To do heating repair you need experience working with electric and electric devices and for most home owners it is over there head. Sorry not being a smart a$$ but I think you know what I mean. You have the skill or not? Only you know your level of talent I just provide the book to make it easy..
|
|
|
 |
New Member
|
|
Feb 1, 2010, 02:18 AM
|
|
|
I agree, and I will give it a whirl. Thank you again & I will keep you posted, you do not by chance live in the Cincy area in case I could use some hired help down the road do you?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 1, 2010, 04:00 AM
|
|
|
Sorry but I am not for hire. Any extra time I have is donated to one of the local universitys to help further the education of both young and older men and women interested in advanced discussions/education of the HVAC trade plus I also learn something new almost every day since NO ONE I ever met can no it all about HVAC. The trade is probably the most complex issue going and has been that way for many years.
|
|
|
 |
New Member
|
|
Feb 1, 2010, 06:05 AM
|
|
|
OK I now think it is the blower motor, Iexamined the cycle again and the blower motor stops spinning THEN about 1 minute afterwards the flame discontinues and I get 4 red blinks off the circuit board. I just took the motor off, it says GE V064AS as a part number. Any ideas where I could purchase one?
|
|
|
 |
New Member
|
|
Feb 1, 2010, 06:08 AM
|
|
|
Also there is another number on the blower motor 5KCP39FG
|
|
|
 |
New Member
|
|
Feb 1, 2010, 06:19 AM
|
|
|
Where can I purchase a gas furnace replacement blower motor
I have a blower motor failure on my natural gas furnace Janitrol GMP 075-3. On the motor it says a GE 5KCP39FG then in very bold there is V064AS? Where can I get a replacement, I am having a terrible time finding one.
Thanks!
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 1, 2010, 07:01 AM
|
|
|
It could be the motor run capacitor causing the problem. Did you test for voltage at the motor wires after the motor stopped? Just because the motor stopped does not mean it is defective unless tested first.
Look in your yellow pages under electric motors. Usually there is a local company that sells and also rebuilds old ones. You can usually take the capacitor ALONG with the motor to them and they will test it for you. Call them and find out before you drive there.
|
|
|
 |
New Member
|
|
Feb 1, 2010, 09:38 AM
|
|
|
Thank you hvac1000, i will keep you posted on the progress!!
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 1, 2010, 10:36 AM
|
|
|
OK do that.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Gas furnace won't ignite model GMT090-4 Goodman
[ 10 Answers ]
As stated my gas furnace will not ignite. Looked on main board no blinking lights. Everything is connected pretty firm. I can hear it blowing from the induce blower but no igniting. I hear gas coming just won't ignite. I checked the ignitor, it has some white spark residues. Seems still good....
Goodman furnace problem
[ 4 Answers ]
I have two goodman furnaces. They both heat up, but, they both have erratic or uneven sounding flames. They run for a while and then click the flame sensor snap switches off. What would cause this, especially same problem on 2 different units?
Goodman gas furnace gmp075 3
[ 2 Answers ]
Hi , my goodman furnace gmp075 3 furnace ,inducer turns on ignitor glows ,burners fire for about 5-7 sec,then turn off blower doesn't come on,but if I let it cycle about 5 times then the blower does come on and it works fine,can anyone tell me what's wrong, thank you
Goodman Furnace GMP075-3
[ 1 Answers ]
Had a Heating Co. check my furnace. They found heat exchange cracked at heat exhange-burner entry venturi point and main center roll out missing. They said we should replace. Does that sound correct? Is the furnace safe to run?