    Gas furnace/burners not working (Fraser Johnson V1000
    Hi,

    I recently moved in to a condo with a Fraser Johnson Model V1000 HVAC system. It's probably over 20 years old. The cold air works great but the heat doesn't.

    The pilot is lit, the fan works, vents are clean, but the burner is not kicking on so only cold air is coming out.

    Also when I set the thermostat to turn on auto it never kicks on the fan I have to manually set the fan to on.

    I went through the instructions to turn the burner on but though the pilot is on when I move the dial to furnace control dial from "PILOT" to "ON" it doesn't kick on the burners.

    Any ideas/suggestions? Thanks.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 13, 2007, 01:21 PM
    Fan operation is a separate entity.

    When there is a call for heat, the fan and burner usually come on. The limit switch usually provides some delay for the fan to initially turn on with a call for heat and it also provides some delay so that the fan runs for a while after the burners shut down. This can also be done with timers.

    Your burner control usually has three positions: OFF (the pilot goes out), Piltot (Only the pilot stays lit and the position is used to re-light the pilot). ON - The gas valve is controlled by the thermostat.

    You do have the furnace in the "HEAT" mode with the setpoint higher than the temperature at the stat?
    eschuen's Avatar
    eschuen Posts: 62, Reputation: 6
    Junior Member
     
    #3

    Nov 13, 2007, 04:30 PM
    Since your a/s is working we can rule out the transformer since it is working the fan relay. This is an old unit and my first step would be check the wiring and connections especially at the limit switch. If you have a VOM (volt ohm meter) see if you have voltage present through the limit. The limit will stop the gas valve from activating. That's the box with a wheel inside of it with temps stamped on it. If there is no voltage there disconect the white wire coming from the thermostat and see if you have 24 volts there. If no voltage there you have a wire problem or a bad t-stat. Remove the thermostat from the sub base and jump a wire between the white and red wire. If the unit fires you have a bad t-stat. Hope this helps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman Gas Furnace Not Working [ 2 Answers ]

I have a Goodman Model # EG030075-1AB REVC Gas Heater it has been converted to run on LP Gas. Furnace has worked fine for years. Turned the heat on and nothing happens. The LED on the control board is not lit. I checked the voltage at the control board and all the voltages appear to be normal. ...

Central AC with gas furnace blower not working [ 3 Answers ]

The house was getting hot so I checked the thermostat and discovered there was no air coming out of the vents. The outside unit comes on but no noise from up in the attic. I had no problems earlier in the day. The fan doesn't come on in the auto or on position.:confused:

Gas Stove burners [ 1 Answers ]

My GE gas stove's burners are very blackened out and it is a chore to light them and have even burns. How do I clean them.

Gas stove burners [ 2 Answers ]

I have a magic chef gas stove. It is about 8 years old. About a year ago the two high speed burners quit lighting. And now only one of the burners will light. You can light them with a match. And after they are hot the other three igniters will light them short term

Burners won't ignite--no gas? [ 1 Answers ]

Lennox model GMP075-3. Installed in '95. I've tried resetting according to instructions on access cover panel (turn heat to 'off', turn off power to furnace, turn gas valve to 'off' for 5 minutes, etc.) When I call for heat, small (induction?) fan runs for a few seconds, the igniter unit glows...


View more questions Search