I have a HEIL gas furnace located outside my house,I found that with the front panel removed it operates perfectly,however with the panel in place as normal the burner will light but will go out. Once I remove the panel I hear the gas valve click and its running perfect. I replaced the pressure switch but nothing changed. The draft inducer fan is running
|
|
|
 |
Ultra Member
|
|
Jan 5, 2010, 08:15 AM
|
|
|
Model number ?
If filter clean?
Is indoor returns clear and open?
|
|
|
 |
New Member
|
|
Jan 5, 2010, 08:25 AM
|
|
|
Model PGAA47F1K4
Filters are new
Returns are clear
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 5, 2010, 10:26 AM
|
|
|
If the unit has a flame sensor clean it carefully. Very fine sand paper OR steel wool will work. Check for loose wiring especially at the Honeywell smart valve if so equipped. Be especially careful of cleaning the flame sensor since the igniter hangs over the sensor and is delicate.
Usually something like this has to do with airflow into the unit for combustion or loose wiring. Also check the safety switch on the blower access door since it can be moved around a bit when replacing the front door of the unit.
Post back with results
|
|
|
 |
New Member
|
|
Jan 5, 2010, 01:09 PM
|
|
|
I cleaned the flame sensor as best as I could and I don't see any loose wires
What could be causing a lack of air for combustion?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 5, 2010, 02:47 PM
|
|
|
You said the furnace is located outside your house.
Is it in a room built for it?
Does this room have combustion are provisions?
Why is the furnace outside your home? Is it a trailer/mobile home?
HOW long has this unit been installed in this room?
|
|
|
 |
Ultra Member
|
|
Jan 5, 2010, 04:36 PM
|
|
|
Uhh, I was assuming it was a package unit, my bad!
|
|
|
 |
New Member
|
|
Jan 5, 2010, 04:38 PM
|
|
|
The entire a/c furnace is one unit located next to the house with the ductwork going into the crawlspace and up into each room. The unit is not covered in any way and this is how all the units are setup in my subdivision I believe that this unit is called a packaged unit thanks
|
|
|
 |
New Member
|
|
Jan 6, 2010, 07:08 AM
|
|
|
Yes it is the front panel which covers the entire half of the packaged unit which is the furnace side it gives access to the burners,gas valve,circuit board, pressure switch and draft inducer fan
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 6, 2010, 08:52 AM
|
|
|
After looking at all the service literature that I posted I can see nothing that could cause your problem. I am not saying the unit does not have a problem it is just a simple unit and this is a very strange situation with it turning off just because the door is put on the front of the unit unless somehow by attaching the front door it is causing the flames to come out of the burner area and tripping the flame roll out disc( NOTE: I believe your rollout switch has a manual reset so unless you are reseting the roll out switch on every shut down event disregard the roll out switch mention in this post). It is also a possibility the exhaust blower or other wiring is intermittent or loose causing the furnace to shut down. The exhaust blower has to be tested with a manometer as per the service manual.
You might try and have the unit running when you put the panel back on and see if you can look through the slats in the panel to see if anything unusual happens that might point to the problem. Sorry but from long distance I cannot see or test anything.
If I have not mentioned this before keep a copy of a 3 documents I posted on your computer since they will come in handy some day.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Pilot light stays lit, but the gas valve will not open
[ 1 Answers ]
I have an old Thatcher furnace model 53170. The pilot light stays lit, but the gas valve will not open to ignite the burners. I have a constant 24v across the transformer terminals. When I check the terminals at the gas valve I experience an intermitant 24v signal about every 5 minutes. I can't...
Burner indicator light stays on
[ 1 Answers ]
I have a whirlpool RF315PXKQ0 range/oven I was cooking on the back right burner and there was a LOUD POP as obviously the element shorted out and the circuit for the range tripped. Disconnected and reconnected everything and threw the circuit breaker to ON and it stayed on OK. All burners, oven,...
On Trane XE 60, how to remove front cover and start pilot light?
[ 1 Answers ]
This is a Trane XE 60 unit, model TUP080B936A with a standing pilot.
Our heat did no go on this morning. I turned the circuit breaker off.
1. How do I remove the front panel?