Ask Experts Questions for FREE Help !
Ask
    jsh82's Avatar
    jsh82 Posts: 4, Reputation: 1
    New Member
     
    #1

    Oct 5, 2009, 10:59 AM
    Ducane furnace won't lite.
    Model: MPGA100A4
    Serial: 5004879510
    Unlabeled number under the serial number: 20093403A
    Natural Gas

    Hope this is all the info about the unit you need. It's a Ducane furnace, and last season, it would ignite, run for a few seconds, then go out, and just do that over and over again indefinitely. There is an in-line fan in the exhaust tube that is always on, I guess to help pull the exhaust outside. There is also a flap valve this in that same exhaust tube that could be adjusted to let normal air in too. It is between the furnace and the in-line fan. I adjusted this to full closed position and duct-taped it so no air could be pulled in, and hamper the fans ability to pull the exhaust out. (hope this makes sense) This let the furnace run for the rest of the season without issue until the duct tape fell off, or a spot opened in the tape to let air in. Its been of the entire summer and now that its getting cold here in Michigan, I turned it on, and now it will not ignite or even try to, no sound comes from it except the blower inside the furnace, and the in-line fan. The gas is on, I did the sandpaper on the sensor trick, and nothing. I cannot smell any gas or anything. If the thermostat is all the way down, the only thing running is the in-line fan. When I turn up the thermostat, the blower inside the furnace will come on, so I know its getting information from the thermostat, but nothing else happens, no ignition, no igniter getting red hot.. nothing but the blower. It has a honeywell thermostat/valve. Model number for that is: SV9501M2056

    Here is a link to the exact one that's on it:
    SV9501M2528 SmartValve Honeywell FREE NEXT DAY AIR SHIPPING

    I'd greatly appreciate any help that can be given, I would like to avoid a service call as my financial situation is precarious at the moment, and will be jobless for a year or more come November (Yay for General Motors... )
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 5, 2009, 12:47 PM
    The Honeywell Smart (DUMB) valves have some problems especially where the wires are on the valve. Try moving the wires around while the unit is calling for heat and see if the furnace will start working as a first step. Post back with the results.

    BTW the inline fan is not supposed to run all the time just when there is a call for heat.
    jsh82's Avatar
    jsh82 Posts: 4, Reputation: 1
    New Member
     
    #3

    Oct 5, 2009, 12:59 PM

    I just went and tried it, and no luck. Blower and fan come on, but no ignition or click or anything. :(
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 5, 2009, 01:16 PM
    OK now you will have to start tracking down the 24 volt circuits etc.

    Here is some info for you to use.
    Attached Images
      
    Attached Images
  1. File Type: pdf 69-1004.pdf (348.3 KB, 1547 views)
  2. File Type: pdf 69-1270.pdf (402.2 KB, 477 views)
  3. File Type: pdf 2003htgcat_p207-208.pdf (730.7 KB, 722 views)
  4. jsh82's Avatar
    jsh82 Posts: 4, Reputation: 1
    New Member
     
    #5

    Oct 6, 2009, 01:02 AM
    Thank you for the info, I will run through it and grab a voltmeter when I get up tomorrow, hopefully I can resolve this with your help! Thanks again
    jsh82's Avatar
    jsh82 Posts: 4, Reputation: 1
    New Member
     
    #6

    Oct 6, 2009, 08:46 AM
    Also, the problem I had last year, that I had to block off that air bypass in the exhaust tube for the furnace to quit cycling on and off. Is that sort of thing normal, or could that have caused some of my present difficulties?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Oct 6, 2009, 09:50 AM
    Is that sort of thing normal

    No it is not normal. I suggest you contact a local dealer for a on site inspection of your furnace. While I have no model number information on Ducane which I believe is a Lennox company the bypass you blocked off does not bode well for the proper operation of the equipment.
    mnrdnld's Avatar
    mnrdnld Posts: 2, Reputation: 1
    New Member
     
    #8

    Nov 25, 2013, 06:53 PM
    Ducan furnace model# fpbb075a3b it want light
    mnrdnld's Avatar
    mnrdnld Posts: 2, Reputation: 1
    New Member
     
    #9

    Nov 25, 2013, 06:56 PM
    Ducane furnace # fpbbo75a3b want light

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman gmnt100-4b furnace won't lite [ 8 Answers ]

I have a 4 year old furnace. Igniter glows but will not ignite.then it shuts down. Then starts to recyle again. I have checked voltage at the gas valve and all limit switches. All read 25 volts except one. I was told by a hvac repairman to jump it to see if it is the problem. Jumping made no...

Ducane Gas Furnace [ 2 Answers ]

Where exactly is the filter on a Ducane Gas Furnace

Ducane furnace not always ignigting [ 2 Answers ]

I have a ducane furnace model cmpe100u4b that is not always igniting. Led will read normal then trip to a code call for heat (fast heartbeat) while the furnace clicks into and throughout its heat cycle. Any ideas (I already had to change the fan limit switch and inducer motor).

Ducane Gas Furnace intermittent fire goes out, fan still on [ 8 Answers ]

Manufacturer: Ducane model # FPBB100A5, manufacter # 9874569843 Age: year is 1995 printed on it 80% efficiency: There is metal flue pipe and a fan I think is draft inducer blower so System: Gas Fired Forced Air Furnace Fuel: Natural Gas Sometimes before it reaches the desired temp the furnace...

Furnace won't lite [ 1 Answers ]

I have a amana furnace can't get the hot surface igniter to work... igniter is new, no power to it.. control board flashes once , meaning a lockout(?)furnace will light if I use lighter... I checked all 3 overloads and pressure switch, all show good... induction fan runs as soon as power is on,...


View more questions Search