Carrier hvac fan won't stop running
Hi,my unit just act up about 10 days ago,while run on heat it keep running the only way to stop it is to shut down the main switch . Thermostat is useless at this time no matter what position setting fan still running ac won't come on the same to heat.Just change the circuit board still won't help , there're no voltage on the board thermostat terminal . I saw a fire burn mark on the wire with fuselink to the limit switch but my friend check and he said that it has power through.Should I call a contractor ? Thank's
|
|
|
 |
Ultra Member
|
|
Dec 27, 2009, 07:07 PM
|
|
|
Check the primary limit switch. If open, it may reset with a few taps from the butt of a screwdriver between the terminals. If the fuse link looks burned, double-check it.
|
|
|
 |
New Member
|
|
Dec 27, 2009, 07:22 PM
|
|
|
My friend checked the limit switch and he said that it's OK.
|
|
|
 |
Ultra Member
|
|
Dec 27, 2009, 07:31 PM
|
|
|
With power applied, check for 24v between "SEC-1" & "SEC-2" on board. If not present, transformer has failed.
|
|
|
 |
New Member
|
|
Dec 27, 2009, 07:41 PM
|
|
|
I forgot to give the unit model , it's a 48NLT roof top unit . The old board have the S1 to 5 on the right and N1 to 5 on the left , no fuse on it .
|
|
|
 |
New Member
|
|
Dec 27, 2009, 07:46 PM
|
|
|
Also the board number is HH84AA017
|
|
|
 |
New Member
|
|
Dec 27, 2009, 07:58 PM
|
|
|
I'll try tomorrow after work.
|
|
|
 |
New Member
|
|
Dec 28, 2009, 01:51 PM
|
|
|
Double check the fusible link and that's the problem . Thank's KC13.
|
|
|
 |
Ultra Member
|
|
Dec 29, 2009, 04:47 AM
|
|
|
The fusible link was the SYMPTOM. Why it failed is the actual problem. Flame roll-out is the most common cause.
|
|
|
 |
New Member
|
|
Dec 29, 2009, 01:36 PM
|
|
|
Still wait for part , when install the F L , I will check and clean the flame sensor replace if need.
|
|
|
 |
Ultra Member
|
|
Dec 29, 2009, 04:31 PM
|
|
|
How old is the unit? If the fusible link failed due to a faulty heat exchanger, operating the unit with it bypassed is dangerous. A replacement link will fail in short order as well.
|
|
|
 |
New Member
|
|
Dec 30, 2009, 11:31 AM
|
|
|
20 years old and no the unit is not operate at this time , I just bypassed the F l to make sure it's not the board problem . Will inspect the heat exchanger . Thank's for the advise.
|
|
|
 |
New Member
|
|
Dec 31, 2009, 02:31 PM
|
|
|
Heat exchanger look good , flame sonsor look a bit dirty , just clean it , still wait for the F-L .
|
|
|
 |
New Member
|
|
Jan 7, 2010, 08:29 PM
|
|
|
Install new fusible link , work fine now
|
|
|
 |
New Member
|
|
Jan 18, 2010, 07:53 PM
|
|
|
Carrier hvac won't come on
Just finish repair my unit from won't stop running by replace the fuseible link and it work fine for a week or so until now come another problem . Last night just come back in town , turn on the heater all I hear is the humming sound from the draft inducer motor and nothing come on ,today I turn on the unit , draft inducer come on , the ignitor clicking for about 30 seconds then stop , no gas hissing sound at all , no fire . Give me some idea . Thank's
|
|
|
 |
New Member
|
|
Jan 18, 2010, 07:56 PM
|
|
|
Carrier hvac won't come on
I forgot my unit is HVAC Carrier model 48NLT036300 rooftop unit.
|
|
|
 |
Ultra Member
|
|
Jan 18, 2010, 09:02 PM
|
|
|
Is it doing anything? How about when you set tstat to fan on, does the blower then blow cold air,, if not have you checked the breaker
|
|
|
 |
New Member
|
|
Jan 23, 2010, 12:30 PM
|
|
|
The fan come on when turn on the tstat , ac also on when turn to cool , breaker OK , I think the flame sensor or pilot ignitor maybe the problem . Found new part online reasonable price , will replace the pilot burner assembly since it's too old anyway .
|
|
|
 |
Ultra Member
|
|
Jan 23, 2010, 01:12 PM
|
|
|
In many/most cases you can clean flame senser and not have to replace also pilot assembly
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Carrier Heat Pump won't stop running!
[ 3 Answers ]
We have a carrier tech2000 electric heat pump and it won’t stop running. We attempted to turn the unit off at the thermostat, but the only way to stop it is to turn it off at the breaker. The unit outside seems to be off? The outside fan doesn't spin despite the hot hair & constant blowing...
Ceiling Fan w/power off won't stop running!
[ 7 Answers ]
After installing my Hampton Bay Fan, everything was normal. Several weeks later, the fan began to intermittently run backwards at 6 RPM (very slow) when both the fan motor switch and the light switch, (both are wall switches) ARE TURNED OFF!! It then stopped this behavior. Now, several months...
Carrier package unit blower fan turning off while compressing keeps running
[ 2 Answers ]
I have a Carrier 50ZPA package unit 1.5 years old. In the winter, the blower would come on by itself without the compressor engaging. Now in the June-July Summer, The compressor comes on but the blower fan just shuts off and does not come back on. The compressor keeps running with the blower fan...
I installed a new thermostat and the fan will not stop running
[ 3 Answers ]
The wires are connected correctly and the fan will not stop running. I put the old thermostat back on the wall and the fan would not stop running and I bought a third thermostat and the fan will not stop running. Cool air is also coming for the vents. What is wrong?
Car hvac blower motor will not stop running
[ 3 Answers ]
I have a 2005 impala with a 3.4 V-6. The hvac blower motor will not stop running, even with the car turned off. The only way I can stop it is to pull the 30amp fuse from under the hood. Any suggestions?