Ask Experts Questions for FREE Help !
Ask
    Pamkrueger's Avatar
    Pamkrueger Posts: 3, Reputation: 1
    New Member
     
    #1

    Nov 3, 2008, 10:09 AM
    Can a new puron condenser be hooked up to an existing 1/4 inch line
    We are in a condo development built in 1970's, and are now facing the changeover from "freon" to puron a/c units. We have run into problems because our current units run through 1/4 inch lines into the condos. The new puron units "require" 3/8 inch lines (or so we have been told.) Our existing chases into the units will not accommodate the 3/8 inch lines so some of the new puron units are being connected to the existing 1/4 inch lines. They seem to be working, but we have heard that this may 1) invalidate the warranty, 2) reduce the efficiency below 13 seer, 3) cannot be done (even though it has been done), etc. What is the real story? What happens if this is done, vs. the problems it may cause down the road? Thanks for your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 3, 2008, 01:31 PM
    Quote Originally Posted by Pamkrueger View Post
    We are in a condo development built in 1970's, and are now facing the changeover from "freon" to puron a/c units. We have run into problems because our current units run through 1/4 inch lines into the condos. The new puron units "require" 3/8 inch lines (or so we have been told.) Our existing chases into the units will not accommodate the 3/8 inch lines so some of the new puron units are being connected to the existing 1/4 inch lines. They seem to be working, but we have heard that this may 1) invalidate the warrenty, 2) reduce the efficiency below 13 seer, 3) cannot be done (even though it has been done), etc. What is the real story? What happens if this is done, vs. the problems it may cause down the road? Thanks for your help.
    The real story is that

    The unit has to be installed to the manufacturers specifications contained in the install manual.

    If Puron R-410A is replacing a R-22 the lines have to be flushed by a special flushing agent. The new refrigerant uses a different oil for compressor lubrication and the old oil must be removed since it is not compatible with the new oil.

    All joints have to be brazed to with stand the higher operating pressures of R-410.

    The inside coil (Evaporator coil) must be replaced to match the new outside unit since the R-410A refrigerant operates at a higher pressure, the newer coils are larger and the old smaller original coils will NOT allow operation at 13SEER due to not being designed for the new refrigerant.

    There are more items but I thought I would just post a few since I believe you will have a problem in the future with your new unit unless it is installed correctly as per the written manufactures instructions.

    The system may work but not as designed or intended and yes this setup can void the warranty since the install instructions are not being followed.

    Please see attached.
    Attached Images
  1. File Type: pdf MismatchedSystems.pdf (131.5 KB, 194 views)
  2. Pamkrueger's Avatar
    Pamkrueger Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 3, 2008, 02:02 PM

    Hi, Thanks for your quick response. Given the above info, does it make a difference if the air conditioner is a "straight cool". Are there some companies ie: York, that can be effectively hooked up through a 1/4 inch line without causing the problems you mentioned?
    Thanks again.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 3, 2008, 03:07 PM
    Given the above info, does it make a difference if the air conditioner is a "straight cool".

    Given the info it has a determental effect on strait A/C or heat pump units.

    Are there some companies ie: York, that can be effectively hooked up through a 1/4 inch line without causing the problems you mentioned?

    The unit being hooked up has to be installed according to the manufactures install instructions. If in doupt call the factory but I already know the answer and I have given it to you..

    Puron is a trade name for Carriers refrigerant so I believe we were talking about Carrier. York has basically the same set of rules but you can check with York factory for your answer.

    One other item you did not mention but special care needs to be take with is line length. There are also rules in the install instructions which require larger tubing over extended lengths or heights. It is all in the factory install manual or if you wish call the factory.

    We have run into problems because our current units run through 1/4 inch lines into the condos.

    I have never found a structure that the correct line size could not be run. I have found some HVAC dealers that have said that so they did not have to do the extra labor to run the new lines. I have also found homeowner associations that did not want new lines because of esthetics since they would have to be boxed in.

    I just tell it like it is.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #5

    Nov 3, 2008, 08:29 PM

    I would be concerned about head pressure if you ignore the factory specs and hook the system into too small of a line. The high head pressure can, and most likely, lead to premature compressor failure.

    As previously posted you will have to replace the evap coil or at the very least install a TXV.
    Pamkrueger's Avatar
    Pamkrueger Posts: 3, Reputation: 1
    New Member
     
    #6

    Nov 4, 2008, 06:36 AM

    Thanks for your help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Utility Sink connected to 5 inch cast iron waste line [ 2 Answers ]

I just purchased an home that was built well before plumbing. Apparently the waste line was installed before 4" became the standard, so my home has 5" cast iron which all of the professionals around here swear they've never seen before. The utility sink is connected after the y, by a "saddle...

Venting of a toilet 3 inch horizontal drain line [ 1 Answers ]

How far away from a vent can a toilet be installed 3 inch horizontal pipe >Moved from Forum Help<

How to run pipes to existing sewer line [ 1 Answers ]

I am building a bathroom with two tolets from scracth and two sinks have no ideal where to start.:) :)

Using existing tub drain line in concrete slab [ 4 Answers ]

I am installing a new whirlpool tub in place of an existing conventional tub. The old sink drain terminates into a concrete slab. The new sink drain will be at least 2 feet from the old. What are my options? Is there anyway of tieing in the new drain into the old drain without taking up all the...


View more questions Search