My central a/c (Rheem) quit working. Opened the unit and the contactor was fried-completely burned. Replaced the contactor. Can physically push in on the center connections of the contactor and the A/C unit comes on and runs fine (as long as I'm holding it in). Will not turn on by itself. Digital thermostat will kick on the furnace fan, but cannot get the A/c to kick on. Yes it is over 80 in the house and the thermostat is set on 68. It is turned to cool. I've tried clicking to off and back to cool several times. All digital displays look fine.
What next? Which wires from the back of the thermostat would I connecct to get the A/C to turn on to verify that the thermostat was bad? Choices are: green, yellow, white and red.
|
|
|
 |
Ultra Member
|
|
Jul 29, 2008, 10:16 AM
|
|
|
The red and yellow,, if wired according to rule of thumb should start your a/c but sounds like you might have some shorted wires,, start at the a/c unit looking for chewed or uninsulated wires that could be grounded or touching,,
|
|
|
 |
New Member
|
|
Jul 29, 2008, 10:34 AM
|
|
|
Tried the yellow and red at the thermostat nothing. Trying to trouble shoot my way through.
Furnace and fan work from thermostat just not the A/c
Replaced the batteries in the thermostat just to be on the safe side-no difference.
Opened furnace circuit board panel. Didn't see any fuses at all.
Breakers are not blown in main circuit box are not blown.
Fuses on outside box by a/c are not blown.
No power in the thermostat lines at the a/c unit.
There was when I first reattached the wire to the new part. Got a spark when I pushed it on. I'm not seeing anything that looks out of place.
|
|
|
 |
Ultra Member
|
|
Jul 29, 2008, 10:44 AM
|
|
|
With your volt meter,, check see if there is 24 volts at the furnace end of stat wires that are going to your a/c unit,, if you do,, then check for 24 volts at end of stat wires in a/c the two smaller wires that tie on or plug into your contacter,, if you have power in furnace but not at a/c,, would be easier to replace the wire from furnace to a/c
|
|
|
 |
New Member
|
|
Jan 6, 2011, 12:36 AM
|
|
|
It seems to me that is not the thermostat even though it could possibly be it. Sense the thermostat is calling for heat lets assume that is good. Your problems is that the contactor is not pushing in to allow the 240v to go to the unit and it only works when you do it by hand. Well, what it is, is that your contactor coil is not receiving 24volts to energize it. What you need to do is to check from the inside unit at the board your red and yellow wires that are going outside. If this wires are alive(24v) then they might go to another board outside if you have a heat pump, and if from that board to the contactor there is no power in the wires hooked to the contactor coil then is the board(it could be a relay in the condensing unit board). You need to check for loose or ground wires. It could be that. If you have no power in the yellow wire going outside in the board that is located in your inside unit (evaparator unit) then is your thermostat for sure.
|
|
|
 |
New Member
|
|
Aug 9, 2012, 07:17 AM
|
|
|
I have the same scenario at my house. The red wire is energized at the furnace, but the yellow isn't. (obviously no power at the contacter either). I thought it had to be thermostat, so I put a new one in. Same results: Blower fan in furnace comes on, and I can physically press in contacter to engage capaciter, and, condenser. What did you figure out for yours? I am about to run a whole new thermostat wire.
Thanks
|
|
|
 |
New Member
|
|
Aug 11, 2012, 12:34 PM
|
|
|
On the side of my furnace/blower is a pump to get rid of condensation. It was clogged with filth and the float rose so high that it activated a kill switch to the whole unit. Cleaned out the pump, and got my thermostat signal back to the outside condenser. $0. Hope this helps.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Wiring codes from old Carrier thermostat to new Hunter thermostat
[ 1 Answers ]
WIRING CODE HELP FOR THERMOSTAT
I am in an office and have an old Carrier programmable thermostat which no longer works. I purchased a Hunter 44660 thermostat to replace. My problem is that the wiring codes on the previous thermostat do not match up the codes on the new thermostat.
Codes and...
Thermostat Wiring, have NO A/C working
[ 3 Answers ]
I tried to change from our Bryant non programmable termostat (w/ mercury) to a Lux non programmable thermostat (non mercury).
The LUX thermostat did not need as many wires that the Bryant thermostat needed. There was an A screw, but don't know what wire goes on A. There was a jumper between...
Check if working
[ 3 Answers ]
friends would you all please check if mindcaller.com works,
check the following things=1)does the record timer begin when you press the record button(even after it may ask mic + cam use in adobe settings)
2) does it send the voice message successfully
and please answer each of the 2 questions in...
Heat pump thermostat says check
[ 1 Answers ]
Our heat pump has had a leak over the last few years and the past week it hasn't been able to "keep up" with even mild temps. Now the thermostat says "check". What should I do? I turned the unit off.
How to check Operating Thermostat on a Kenmore Dryer
[ 1 Answers ]
Kenmore dryer not heating.
My dryer has an operating thermostat that has 4 terminals on it. 2 connected to red wires on both ends and 2 on the top with purple wires.
I checked the terminals with red wires for continuity and it looks good with zero reading.
Do I test the top terminals as well...
View more questions
Search
|