Hi everyone,
I have a 9 year old Bryant Plus 90, model #CD5AXW024017AAAA that keeps giving a code 33. After doing some investigating, I found that an old filter was still against the blower motor along with the current filter. The old filter was completely clogged- I think it worked its way out of view of the filter slot and I installed another one without realizing I hadn't removed the old one. I assumed this had solved the problem but it still seems as if the igniter area is producing too much heat and triggering the limit or rollout switch. The unit will cycle through the normal startup process and start producing heat, but after a few minutes the metal casing above the pilot is almost too hot to touch, the 33 code starts flashing, and the pilot goes out while the blower continues to run.
Is the shutoff being caused by the unit getting too hot and what are some potential causes?
Thanks for the help and have a great holiday!
John
|
|
|
 |
New Member
|
|
Nov 27, 2008, 08:14 AM
|
|
|
I forgot to mention that the furnace runs on propane
|
|
|
 |
New Member
|
|
Nov 27, 2008, 10:29 AM
|
|
|
A few more details: looking at the flame, it is pretty jagged and has portions of yellow in it. The box also make a bit of a rattling noise too- don't know if that is normal or not.
Thanks
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 27, 2008, 01:39 PM
|
|
|
Your problem will not be a simple one. If the blower for the home is running the unit should not overheat unless the A/c coil is blocked with dirt since you removed the clogged filter. Do you have central A/C?
|
|
|
 |
New Member
|
|
Nov 27, 2008, 04:03 PM
|
|
|
Yes I do have central AC. Could you give me an idea on how to access the coil? Would compressed air work well for that?
Thanks for the help
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 27, 2008, 04:25 PM
|
|
|
The coil is mounted on the top of the unit.
You probably have more problems than just that issue. The flames should not look as you described and the box should not rattle.
|
|
|
 |
Plumbing Expert
|
|
Nov 27, 2008, 04:29 PM
|
|
|
What does the book say code 33 means?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 27, 2008, 04:34 PM
|
|
|
33 LIMIT CIRCUIT FAULT - Indicates a limit, draft safeguard, flame rollout, or blocked vent
switch (if used) is open. Blower will run for 4 minutes or until open switch remakes
whichever is longer. If open longer than 3 minutes, code changes to lockout #13.
If open less than 3 minutes status code #33 continues to flash until blower shuts off.
Flame rollout switch and BVSS require manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel. - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections. - Inadequate combustion air supply (Flame Roll-out Switch open
In his first post there air filter was super dirty and that also means that the furnace has been neglected for 9 years or so. The unit is overheating and it probably needs a complete professional service.
|
|
|
 |
Plumbing Expert
|
|
Nov 27, 2008, 04:45 PM
|
|
|
Okay, sounds like you need to have evap coil cleaned, and also(on 90+ units) may have to have furnace coil(located directly above squirell cage) cleaned. Agree with hvac, time to call for a pro.
|
|
|
 |
New Member
|
|
Nov 27, 2008, 07:02 PM
|
|
|
Is it possible these symptoms are related to a cracked heat exchanger? That's my biggest fear right now.
Yeah, I had the feeling that it wasn't going to be a single issue or simple fix. I'll see if I can get someone to look at it soon- not sure how the holiday weekend will affect that. Thankfully I've got the fireplace to keep things tolerable.
Thanks
|
|
|
 |
New Member
|
|
Nov 27, 2008, 07:08 PM
|
|
|
I just spent the last few months finishing half of the basement too. I'm sure the sawdust & drywall dust haven't helped the issue.
|
|
|
 |
Ultra Member
|
|
Nov 27, 2008, 07:27 PM
|
|
|
You have two 2inch pvc pipes that exits the furnace, one is the exhaust and one is the intake. The intake should have a cap on the opposite side of the burners. Remove the 2 inch cap and see if it will burn. You may have a slight restriction in the intake or exhausts. A weak or sticking vent pressure switch or a cloged condensate drain will give the same symptom and fault code.
|
|
|
 |
New Member
|
|
Dec 1, 2008, 12:59 PM
|
|
|
I checked the vents for blockage and even ran the unit without the intake & exhaust attached for a few minutes without any change. Also cleaned of the AC coil.
I had someone look at it and they felt there was a good chance the problem was being caused by a blocked or bad inducer motor. Any thoughts on whether this diagnosis is consistent with my symptoms?
|
|
|
 |
Plumbing Expert
|
|
Dec 1, 2008, 04:25 PM
|
|
|
Not likely the inducer motor. If your inducer or vent/ intake were the problem, your pressure switch would fail to close, causing the gas to never actually come on.
You say you cleaned the ac coil? Did you clean it from the top or the bottom. It needs to be cleaned from the bottom if you have an upflow furnace.
It wouldn't hurt to check for carbon monoxide(cracked heat exchanger) Probably not the problem, but better to check and be safe.
In your original post, you say flame rollout or high limit. Really need to know if it is flame rollout OR high limit.
|
|
|
 |
Ultra Member
|
|
Dec 1, 2008, 05:29 PM
|
|
|
Your system may have a gas inlet pressure switch(used with L.P gas conversion kits) It wires inline with the vent pressure switch. Lack of gas pressure will cause the switch to open. The gas pressure switch is found on the gas inlet side of the gas valve small round device with 2 wires going to it. (I think yellow and orange but not sure)
|
|
|
 |
New Member
|
|
Dec 1, 2008, 07:38 PM
|
|
|
The ac coil was cleaned from the bottom- it was dirty, but not as bad as I had expected.
The flame rollout switch (on the side of the burner box) is the one causing the heat to shut down. I can reset it when things cool off.
Is it possible that the inducer motor functions enough to close the pressure switch but not enough to keep it from overheating?
Thanks
|
|
|
 |
New Member
|
|
Dec 1, 2008, 11:21 PM
|
|
|
Is this a high efficient furnace.also have the orifice size been adjusted i.e. has the unit been properly converted to lp.also gas pressures may be to high or a faulty gas valve .possibly more return air in the case of a high efficient it could be improper venting causing condensate to pool in the vent lines. Decreasing the flow of air that would probably be a pressur switch problem though
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Bryant Plus 80 Error code 33
[ 3 Answers ]
Hello! I'm new on here so bear with me. I found a similuar post on the Bryant 80 but I believe I have a different model... not sure how much that matters. The only model number I could find on the unit was CK5AXA036017AAAA
The Error code is 33 Limit or flame roll out switch is open. The furnace...
Bryant 330AAV Code 34.every now and then.
[ 2 Answers ]
Wanted to know if anyone could help me troubleshoot this problem..
This furnace will not fire up (every now and then), basically what happens is the igniter lights up, but will shut down after 5 seconds or so. It will do this three times until it goes into lock down, code 34 flashes. I reset...
Bryant Plus 80 Code 33
[ 10 Answers ]
I have a Bryant Plus 80 that is throwing a error of 33 (limit or flame roll out switch is open). The last time this happened was because the hot surface igniter was broken (frequent problem as my furnace has a tendency to short-cycle). I had picked up a couple extra ones so I had them on hand to...
Code 41 on Bryant air handler
[ 6 Answers ]
Equipment: Bryant Variable Spd 4-Way Multipoise Furnace Model 315AAV060110 package with Bryant Condensing Unit Mod 38HDC060-321. Unit in Florida and issue with cooling operation. Problem start: Odor elec burn at registers. Powered off unit and called repair. Tech did shallow/sloppy diagnostic...
Bryant 310AAV code 23
[ 8 Answers ]
I found your forum after having some issues with my furnace. Age is unknown because I rent and my landlords are out of town.
When I went to turn the furnace on tonight, nothing happened. House temp registering 68-69 at thermostat, furnace doesn't kick on when adjusted to 72.
Fan will turn...
View more questions
Search
|