Bryant plus 80t error code 31
Ok, the furnace stopped working this morning. Need some help. The flame goes on, but turns off after a minute. The LED flashing code on the motherboard says 3-1 (31 - which is the high heat pressure switch -- also says to refer to error code 32 which is the low heat pressure switch). I turned the power off on the unit, and back on, and it seems to be working again normally. Any thoughts>>?
|
|
|
 |
Ultra Member
|
|
Jan 20, 2009, 08:11 PM
|
|
|
Could be (in order of likelyhood): blocked flue, faulty pressure switch, faulty circuit board, faulty inducer motor. If it happened once, it will likely return if unaddressed.
|
|
|
 |
Ultra Member
|
|
Jan 20, 2009, 08:39 PM
|
|
|
If it's below freezing out,you may check to make sure there isn't ice build up on the exaust pipe outside.
|
|
|
 |
New Member
|
|
Jan 20, 2009, 09:26 PM
|
|
|
Thank you all for your help. The answer is: Faulty Circuit Board! -- replaced, and all is working perfectly. Apparently the technician said it is pretty common with this unit, and that the circuit board is sending false readings of it being the pressure switch. In fact the parts manager at the HVAC store said he rarely ever orders pressure switches.. in his opinion, he thought it was going to be the motor. One last note to anyone reading this - always replace your filters! That can cause a problems as well. Thanks again!
|
|
|
 |
New Member
|
|
Jan 27, 2009, 08:20 AM
|
|
|
Having same problem with bryant plus 80t error code 31. Furnace was installed in May 04. Had the installer out here 3 times in two years. First time they said it might be wind that caused the error code. They were here for the second time just 3 weeks ago and decided it was the pressure switch, which they replaced. Called them back yesterday for the same problem and they told us to replace the thermostat. Replaced thermostat... yesterday afternoon code 31 was flashing again and the gas would only stay on for about a minute. Then for some reason it stopped flashing code, the gas stays on while the furnace is running. However, the furnace checks on every 15 minutes, runs for 15 minutes and then shuts off. Called the company that installed the furnace, and they have no idea what the problem is and don't seem to really care to try to find out, even though the furnace is still under warranty.
|
|
|
 |
New Member
|
|
Jan 27, 2009, 03:47 PM
|
|
|
rwhoke
Called in a different company. Same problem you had... needed a new circuit board. Sure wish I had called them first. Could have saved $270!:(
|
|
|
 |
Ultra Member
|
|
Jan 27, 2009, 03:58 PM
|
|
|
You should pursue at least a partial refund from the installing dealer for their inability to correct the problem. Did you purchase any extra warranty coverage with the furnace?
|
|
|
 |
New Member
|
|
Jan 28, 2009, 07:43 AM
|
|
|
 Originally Posted by KC13
You should pursue at least a partial refund from the installing dealer for their inability to correct the problem. Did you purchase any extra warranty coverage with the furnace?
Furnace is still under original warranty... 5 years parts, 1 year labor. The company that finally fixed the problem only charged us for the labor.. parts were still under warranty.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Bryant Plus 80 Error code 33
[ 3 Answers ]
Hello! I'm new on here so bear with me. I found a similuar post on the Bryant 80 but I believe I have a different model... not sure how much that matters. The only model number I could find on the unit was CK5AXA036017AAAA
The Error code is 33 Limit or flame roll out switch is open. The furnace...
Bryant 395cav error code 31
[ 9 Answers ]
I have a Bryant CAV395024070 furnace that's taking a code 31. When I run a component test, the inducer motor comes on, sometimes for only a second, sometimes for the proper amount of time, sometimes not at all. The remainder of the components all go through the test no matter what the inducer motor...
Bryant 352MAV and error code 32
[ 49 Answers ]
Our furnace worked last night but this AM it didn't. It's a 3 year old Bryant 352MAV, installed horizontally.
It's giving error 32. I've spent much of the day working with it. I'm more than handy but don't really know much about hvac.
I found that the idiots that installed it (and who are now...
Bryant plus 80 error code 31
[ 1 Answers ]
Bryant Plus 80 furnace - Error code 31
What are the corrective measures to put this furnace back to producing heat? There is power, the fan works but there is no heat. We lost power recently but it worked after that. Last evening there were high winds which were indicated on the code...
Bryant 355MAV Error Code 31/32?
[ 67 Answers ]
Hi,
My 9-year-old Bryant 355MAV shut off after heating for about 15 minutes, even though the house is only about 60 degrees. I've been trying to figure it out all day.
If I turn the furnace off, then back on, it will start up OK, the inducer motor starts running, the burners light up and the...