New Member
|
|
Feb 11, 2009, 02:00 PM
|
|
|
Blower speed control Bryant 90 plus
Hi Ho: We have a Bryant 90 plus (350MAV) to which we recently added an electrostatic filter. Everything works well, but I don't know if the 4-speed motor has a really slow speed which I can leave running. I have the red wire (I think is low speed) plugged in so that turning the blower from auto to on runs on this wire. The problem is that there is very little difference between normal heating (about 8.5 amps) and the on position (about 7.2 amps). Is this really the lowest speed? Is there a simple way to get the motor to run slower i.e. use less power?
Thanks, Dirk
|
|
|
 |
Ultra Member
|
|
Feb 11, 2009, 03:55 PM
|
|
|
Check the diagram to be sure, but I think you will find the motor speed selections, from highest to lowest, are black, yellow, blue, and red. The "cool" terminal on the circuit board is only powered with a thermostat input to "G" and "Y" at the same time. The "heat" terminal is powered during heating cycles, or when only "G" is powered (with thermostat fan selector switch set to "on"). If using the low (red) motor speed for heating, check the temperature rise of the furnace to assure airflow is sufficient. Values are given on the unit rating label.
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 11, 2009, 03:58 PM
|
|
|
The red is usually the lowest speed. Check the wiring diagram on the back of the blower door.
There is no cheap way to get a blower motor to run slower without causing damage. There is a way but the units cost 400.00 to 500.00. They make the motors variable speed with auto ramp up control.
|
|
|
 |
New Member
|
|
Feb 12, 2009, 11:09 AM
|
|
|
Hi Ho: Thanks guys for the replys. Kind of what I expected, but I am still amazed that a 4-speed motor has so little difference between speeds. I assume the variable speed with ramp-up is like what the Trane system uses. Is there an after-market variable speed system that would work with the Bryant 90 plus?
Thanks again, Dirk
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 12, 2009, 01:12 PM
|
|
|
Yes there is a variable speed product but it is not sold to retail customers that I am aware of.
|
|
|
 |
New Member
|
|
Feb 12, 2009, 03:10 PM
|
|
|
Hi Ho: Thanks again for the quick response. Is that a Bryant system that you have in mind, and if so, what do they call it? I would assume that the controller would also have to be changed? I'm not concerned with having access if I know that it will do the job.
Dirk
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 12, 2009, 05:49 PM
|
|
|
It is a after market setup.
FanHandler.com
|
|
|
 |
Ultra Member
|
|
Feb 12, 2009, 08:19 PM
|
|
|
If you have to worry about the blower speed for your filtering system to work right, you bought the wrong filter system. They make a cartridge filter with a very high merv rating and works better than the electrostatic filter at any speed.
|
|
|
 |
New Member
|
|
Feb 13, 2009, 12:29 PM
|
|
|
Hi Ho: Many thanks HVAC1000. Just what I needed. The reason for reducing blower speed is not that the system won't work at high speed. It is just noisy, drafty and uses more energy than needed.
Thanks again, Dirk
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Bryant 90 plus I 398 Variable Speed Blower
[ 6 Answers ]
I have this Bryant Furnace Model 398BAZ036060 (90i) plus
This furnace has had its fair share of problems but this one I fear is going to put me in the poor house.
Here is the problem
This furnace will only run in emergency heat mode and it runs well and has for months this way
In normal mode...
Variable Speed vs. Single Speed Blower
[ 1 Answers ]
Questions:
Getting 2 new heat pump systems installed. 1.5 ton upstairs and 4 ton downstairs. Decided on Comfortmaker. Heat Load calc performed on sizes.
Going 2 stage with variable speed downstairs with Honeywell IQ Pro stat. Was going to go one stage with variable speed upstairs with...
Bryant blower
[ 1 Answers ]
My Bryant furnace and air conditioner does not work, turn the blower on manual and the blower does not rotate but, hear the motor humming. Does this mena the motor is burned out? Should I replace the motor and how involving is the procedure?
No blower on Bryant mdl plus 80t
[ 5 Answers ]
I have a 2 year old Bryant Plus 80 t unit the blower will not kick in after the burner lights up,
I've checked the fuse on control panel , not blown, a small led light on control panel blinks on and off.
Stat is digital and working, burners have bright blue flame and shut down after a minute or...
View more questions
Search
|