New Member
|
|
Jan 16, 2007, 08:52 PM
|
|
|
Back-up generator connections
I have a 3 yr old - 2 stage American Standard gas furnace. I tried to use a generator in an emergency, by disconnecting the hard wiring from the switch next to the furnace - and putting a good, 3 prong pigtail on the wires coming from the furnace.
All I got was clicking and a sound like it was 'trying' to light and a really cold night in the house.
It has been suggested that while the generator was big enough and the cords were big enough - the ground might have been insufficient. When I unhooked the white and ground from the house wires I was relying on the generator ground to complete the circuit? Does this make sense? Can poor grounding be my problem? When I reconnected to the house wires and the power was restored - everything worked great. The furnace is on its own 15 amp circuit...
Anybody out there who can help with this one.. :o
|
|
|
 |
Uber Member
|
|
Jan 19, 2007, 07:27 AM
|
|
|
See https://www.askmehelpdesk.com/electr...ral-55551.html
I have read some other reports here on furnaces refusing to run on a generator. Not fully sure what the problem is. I am concerned because I have a generator that I would want to use for that.
|
|
|
 |
New Member
|
|
Jan 19, 2007, 11:30 AM
|
|
|
I have friends who use generators to run their gas furnaces in emergencies, by rewiring the disconnect power switch to a short pigtail male plug and then using a good extension cord.
Theirs are all at least 10 yr old furnaces and all worked fine. I tried it with a newer model(3 yrs old) and it won't light. I admit that I probably didn't have an effective ground system after I disconnected the white from the furnace/house and hooked it to the pigtail's white wire - - same thing for the green/bare ground.
Others who had problems with furnaces may want to think about their hook-up and see if they may have done the same thing.
I plan on testing the connections again soon, with better ground connections.
Anyone who can add to this discussion - please do. I understand the emphasis on transfer switches, but - I'm using cords.
Can somebody answer this - - simply, for us thickheaded readers? ;)
|
|
|
 |
Uber Member
|
|
Jan 19, 2007, 07:23 PM
|
|
|
 Originally Posted by T-Top
I see on your wiring digram you sent you have to have an equipment ground on the gas valve if you do not have a good ground it will not work. the flame sensor can not sense the flame if the valve is not grounded.
Interesting question. This came up in a thread on a furnace that won't run on house power. I wonder if that is why some people have trouble getting their furnace to run off a generator. If the frame of the furnace is properly connected to the supply ground wire, and they use a good 3 wire pigtail, I don't understand why it wouldn't work. If whoever installed the furnace skipped or botched connecting the ground wire, it might, gack, ground through gas line. Then not be grounded to the generator.
|
|
|
 |
Junior Member
|
|
Jan 19, 2007, 09:45 PM
|
|
|
After an ice storm here in Ohio, we had several customers running their units on generators.
A few had trouble and I was called out, I found 1 needed an earth ground to work properly(flame sensing issues) and another that needed 60 cycles per second before the board would activate. The second one we adjusted the cycle rate and got temporary heat.
Another customer had run out of fuel and when he restarted his generator the control board failed, I'm guessing a brownout condition as the generator was stalling due to lack of fuel.
|
|
|
 |
New Member
|
|
Jan 20, 2007, 07:23 AM
|
|
|
As I indicated - I would admit I had the grounding bad. I had not grounded the generator - and I had removed the furnace from the house ground before I hooked it to the pigtail...
I could hear the igniter, but as you noted - the gas valve may not have been sensing and or calling for flame.. .
I hope my mistake makes it easier for the next guy. It sounds like there may be others out there wondering "why..?"
I appreciate the informed response from an HVAC guy, whom it seems has worked through this for someone else. I know the storms will continue, this time I think I might have it right...
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Question about back stab connections for light switches
[ 1 Answers ]
We are in a newly built home and after being there about 2 years we have noticed that some of the light switches have been popping. They are actually 3 switches that control the same light fixture. All 3 are in different boxes. I noticed these switches were installed using the back stabbed method....
Music Connections
[ 1 Answers ]
I really, really, like the bands Jack's Mannequin and Diffuser. Could someone give me a list of similar artist.
Thanks, Josh
Network connections
[ 2 Answers ]
Hi I have a good feeling that when I play an online game such as age of empires or fifa 06 etc the other computers on my network don't work, the internet we share seems to get unconnected for them. Im not sure if this is why, but it only seems to happen when I'm playing a game does anyone have any...
Valve connections
[ 1 Answers ]
Tom, do you prefer a threaded valve connection or a soulder joint? Is it recommended to remove the guts of the valve before welding joint? What is the terminoligy for valve connections? I have decided on a Moentrol valve with built in 3 way diverter so I can have a hand shower and body sprays. They...
View more questions
Search
|