My Carrier AC won't start when I turn it on using the thermostat (4-wire programmable). The furnace fan comes on but the ac fan/compressor is dead. I checked the breakers- they are all on. I checked the service disconnect- nothing seems wrong. I looked for loose wires in the fan/compressor unit- nothing seems wrong. Then I opened up the furnace and found a suspect conduit coming from the AC unit... this conduit has a two wires; a white wire connected to 'C' on the Honeywell control board, and red wire that is not connected anywhere! This seems like it may be the cause of the problem, but I'm not sure where this red wire should be connected, if even if it should be? Please help! :confused:
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 6, 2009, 03:22 AM
|
|
|
Usually the red wire is attached to the Y or yellow wire from the thermostat. It is thermostat cooling leg that tells the outside unit to turn on. Before you connect it I would check to see why someone disconnected it to start with. The unit could be experiencing a problem or the entire story of this unit has not been posted. Wires do not disconnect themselves usually.
|
|
|
 |
New Member
|
|
Jun 6, 2009, 06:32 AM
|
|
|
Thanks HVAC 1000! In the fall I had the furnace cleaned and I suspect that they accidentally knocked the wire loose. Nobody else has been in there since, and the AC worked fine before that. What you say also makes sense according to the wiring diagram, but I'm completely green when reading those so I didn't want to take any chances. As far as I know, that's the whole story. I think I'll reconnect- thanks again.
|
|
|
 |
New Member
|
|
Jun 6, 2009, 08:26 AM
|
|
|
Well, I connected it but it still won't turn on. What are the chances of 2 things going wrong at once?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 6, 2009, 01:00 PM
|
|
|
What are the chances of 2 things going wrong at once
Not the usual case but anything is possible. Are you sure you connected the wire to the correct location?
|
|
|
 |
New Member
|
|
Jun 6, 2009, 10:54 PM
|
|
|
I connected to the 'Y' terminal on the control board. Am I missing something?
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 7, 2009, 03:02 AM
|
|
|
The Y terminal should have done it. Looks like you are going to have to track down the low voltage circuit and see where the problem is. I would check to see if you have 24 volts across the C and Y terminals where the thermostat control circuit goes outside and work your way back from there.
|
|
|
 |
Ultra Member
|
|
Jun 7, 2009, 05:43 AM
|
|
|
Are/were there 2 wires connected to the "Y" terminal on the control board? There should be...
|
|
|
 |
New Member
|
|
Jun 7, 2009, 08:38 PM
|
|
|
Yes, there are two wires connected to the Y terminal... one from the thermostat, one from the outside.
|
|
|
 |
Ultra Member
|
|
Jun 10, 2009, 03:52 AM
|
|
|
If the outdoor unit is equipped with a low pressure switch AND you have experienced a loss of refrigerant, it may explain why the unit won't run. Try this: disconnect wires from "R" and "Y" at the thermostat and connect them together. Does the outdoor unit run? If so, the thermostat is the culprit. If not, the above suggestion gains some strength...
|
|
|
 |
New Member
|
|
Jun 11, 2009, 05:54 AM
|
|
|
Well, thanks everybody. I'm not sure why, but I tried the system again and it works. It seems that connecting the wire to the Y terminal was all it needed.
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 11, 2009, 08:26 AM
|
|
|
Glad you got it going.
|
|
|
 |
New Member
|
|
Aug 1, 2012, 06:11 AM
|
|
|
I just had the same problem. I replaced the motor with no luck. It turned out to be a bad capacitor. If it is a dual capacitor, three prongs on top, it also starts the compressor. It is recommended to replace the capacitor anytime you replace a motor. I would try replacing the capacitor first. It is a lot cheaper that a new motor. If that does not fix the problem then you can get a motor. No harm, no foul. The slow start of the motor is a common symptom of a bad capacitor. The motor is not getting enough voltage. The capacitor increases the voltage like a transformer. It will boost it to almost 400 volts, depending on your unit.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Air conditioner
[ 1 Answers ]
The vents are blowing but the ac unit outside isn't turning on. How would I fix that?
Outside Air Conditioner Unit Runs When The Air Conditioner Is Switched Off
[ 4 Answers ]
We bought a Panasonic split system inverter air conditioner (7.4kw) brand new over Christmas so it is only a couple of months old. We had it installed by a qualified air conditioner installer and everything works perfectly as it should. However we have noticed recently that when the air conditioner...
Bryant heater/air conditioner combo, heater does not start
[ 1 Answers ]
I have a Bryant heater/air conditioner combo that the heater has stopped working. Here is what happens when I turn it on manually-
Smaller fan kicks on
I can hear the gas come on for a few short seconds
I can hear the igniter trying to ignite
It seems like it is not igniting and after a...
Air conditioner won't come on at all
[ 1 Answers ]
The thermostat is on auto and set for cool, but the air conditioner unit won't come on. I don't know what the problem could be. The unit outside is about 4 years old and I have a new evaporator coil (maybe 3 months). I'm hot and frustrated!! Help.
Sun
Is my air conditioner start to not work
[ 4 Answers ]
My air conditioner goes from cold air and normal air and sometimes a little bit worm in, like 10 minutes cold and like 5 normal or worm does, that means that is it I have to buy a new one?
View more questions
Search
|