    I've installed a Honeywell RTH7400 thermostat on a heat pump system with electric resistance auxiliary heat. The thermostat is properly wired and programmed but would not operate properly. It would run the heat pump for less than a minute and shut the system down.

    After an hour with Honeywell's India call center we found the following. Pulling the 'C' wire from the thermostat base permits the system to run normally. In other words, the thermostat runs fine on internal 'AA' battery backup but not AC power.

    The tech says the thermostat is rated for 24-30VAC at 1A and questioned power quality which is not an issue. I ran a wire pair to the baseplate and measure 28.3 volts which sags to 26.5 with relay closures.

    For some reason this thermostat does not like to see AC power... which the old dual mercury switch model never minded.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 25, 2008, 01:15 PM
    Look here see page 12 number 4

    http://customer.honeywell.com/techli.../69-1900EF.pdf

    Something is wrong somewhere. Post your wiring from your heat unit to the thermostat and how you connected it.
    axialcompressor's Avatar
    axialcompressor Posts: 7, Reputation: 1
    New Member
     
    #3

    Feb 25, 2008, 01:58 PM
    hvac1000,

    Thanks for your quick response. Seven wires run from the heat pump with backup electric heat to (old) Janitrol mercury switch HPT18-60 thermostat as follows:

    Wire--->Thermostat
    Yel Y
    Grn G
    Red R
    Org O
    Brn C
    Blu E
    Wht W2

    Using jumpers and volt/ohm meter I've established function for these:

    Yel Heat pump
    Grn Fan
    Red 24VAC
    Org Cooling changeover valve
    Brn AC Common
    Blu Emergency heat
    Wht Aux heat

    Honeywell RTH7400 thermostat wired per the manual:

    Yel Y
    Grn G
    Red R
    Org O
    Brn C
    Blu E
    Wht Aux

    R and Rc are jumpered.

    Symptoms: With C wire disconnected, thermostat works properly but on AA battery backup power. With C wire connected, Emer heat does not function. Normal heat runs for less than a minute, systems tries to select aux heat and shuts down. This repeats after 5min compressor safety time.

    Honeywell tech support says the problem is with AC power quality and says unit requires 1 amp 24 to 30VAC. I measured voltage under thermostat load at 28.3V with sags to 26.5 with relay closure in heatpump. AC mains power quality is good with no spikes or dips.

    If you can steer me to a wiring or other error I would be most appreciative.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 25, 2008, 02:54 PM
    Quote Originally Posted by axialcompressor
    hvac1000,

    Thanks for your quick response. Seven wires run from the heat pump with backup electric heat to (old) Janitrol mercury switch HPT18-60 thermostat as follows:

    Wire--->Thermostat
    Yel Y
    Grn G
    Red R
    Org O
    Brn C
    Blu E
    Wht W2

    Using jumpers and volt/ohm meter I've established function for these:

    Yel Heat pump
    Grn Fan
    Red 24VAC
    Org Cooling changeover valve
    Brn AC Common
    Blu Emergency heat
    Wht Aux heat

    Honeywell RTH7400 thermostat wired per the manual:

    Yel Y
    Grn G
    Red R
    Org O
    Brn C
    Blu E
    Wht Aux

    R and Rc are jumpered.

    Symptoms: With C wire disconnected, thermostat works properly but on AA battery backup power. With C wire connected, Emer heat does not function. Normal heat runs for less than a minute, systems tries to select aux heat and shuts down. This repeats after 5min compressor safety time.

    Honeywell tech support says the problem is with AC power quality and says unit requires 1 amp 24 to 30VAC. I measured voltage under thermostat load at 28.3V with sags to 26.5 with relay closure in heatpump. AC mains power quality is good with no spikes or dips.

    If you can steer me to a wiring or other error I would be most appreciative.
    From instructions on page 12 number 3 red triangle

    If your old thermostat had separate O and B wires, attach the B wire to the C terminal. If another wire is attached to the C terminal, stop now and contact a qualified contractor for help.

    Remember yellow is for cooling and on your second post you said you used a ohm meter and determined that the old thermostat used it for the heat pump. That part of your diagnosis in incorrect.

    If this does not work you will need to follow the wires to the equipment and find exactly where the wires go. A ohm meter is of no use but you can look at the landing area in the furnace and see exactly what color goes where. I will work with you on this but I need factual information so follow the wires and post back what color lands on what terminal on the equipment.
    Attached Images
  1. File Type: pdf Air%20Conditioner%20or%20Heat%20Pump%20Sizing%20Chart.pdf (21.9 KB, 284 views)
  2. axialcompressor's Avatar
    axialcompressor Posts: 7, Reputation: 1
    New Member
     
    #5

    Feb 25, 2008, 04:22 PM
    hvac1000,

    Wish you could have been here... the best part was bringing the heat pump fan/coil cover down from the attic, carefully placing it on the copy machine and making the attached copy of the schematic. Referencing the terminal block (TB) on the left side, the thermostat wires are connected as follows:

    Thermostat-->Terminal Block
    Red R
    Grn G
    Org O
    Wht W2 (internally jumpered to W1/W2, E and OTC)
    Blu E (jumpered as above)
    Brn OTC (jumpered as above)
    Yel OTC2
    Blk Unused

    Of course there are also wires running to the compressor which are not shown above. A good wool cap and a LED headlamp have come in handy here.
    Attached Images
  3. File Type: pdf Heat Pump Schematic0001.pdf (57.3 KB, 329 views)
  4. hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 26, 2008, 12:53 AM
    See note 3 on the right side lower of the diagram. Do you still have the install instructions hanging on the unit or in the unit housing?

    See note 5 and confirm wiring of emergency heat relay.

    The wiring for the O terminal is not addressed on the diagram? It might be on the item mentioned in number 3 above.
    axialcompressor's Avatar
    axialcompressor Posts: 7, Reputation: 1
    New Member
     
    #7

    Feb 26, 2008, 07:23 AM
    hvac1000,

    Good suggestion, I've found the instruction manual and starting to go over the schematic.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 26, 2008, 07:28 AM
    You got lucky finding the manual. The main diagram you posted gives some info but not all.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #9

    Feb 26, 2008, 09:26 AM
    There is a possibility that there is a short in the wiring. If there are metal studs, it could even be in the wall.

    Try connecting the tsat to Rc/RH and (C). Leave all other connections open.
    Try with and without batteries and measure the voltage between these terminals.

    If the voltage is OK and the stat is operational (agreed it won't control anything), then try connecting one wire at a time.

    If you still suspect the wiring, you can always connact the stat directly to the furnace.

    Don't forget that the outside unint t-stat wiring could have shorts too.

    The shorts can be to ground or another terminal.

    I recently troubleshooted a system where a 4 conductor wire was run for an utside unit that required two, and there were two shorted pairs.
    axialcompressor's Avatar
    axialcompressor Posts: 7, Reputation: 1
    New Member
     
    #10

    Feb 26, 2008, 01:04 PM
    Gentlemen,

    I found the problem in the upstairs system... a 24-year old wiring error by the installing technician. In the air handler, the thermostat common wire (C) was connected to aux heat (W1/W2) on the terminal block. This meant that whenever the thermostat asked for aux heat, the thermostat common line would jump up to 24V.

    For 24 years the old mercury thermostat didn't mind this since it had only passive components. The Honeywell electronic thermostat did not like it all when what should be AC ground banged up to 24V - and it went tilt. This accounts for the fact that it ran okay on battery backup with the hot wire (R) disconnected.

    Now to figure out what's going on with the downstairs systems. Thank you for your advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Feb 26, 2008, 01:14 PM
    Great. It is always a good idea to address the drawings if you can when all else fails. LOL
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #12

    Feb 26, 2008, 01:17 PM
    Your welcome. I had to also deal with the idiot that splices the t-stat wire and changed the colors. So, you know that was tough.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a Honeywell RTH7400 Thermostat for heat pump [ 2 Answers ]

I'm replacing a 24 year old Bryant heat pump thermostat with two mercury switches, part number P271-3457 with a Honeywell RTH7400. It controls a heat pump/air conditioner with electric thermal storage (equivalent to electric resistance backup) as second stage heating. The Honeywell manual and...

No power to Honeywell Thermostat [ 2 Answers ]

The Honeywell thermostat for my Ac unit does not have any power. I checked all the breakers and they have not been tripped. I can not tell if it has a battery. Any suggestions?

Honeywell RTH7400 Thermostat Installation [ 1 Answers ]

I'm attempting to replace my old manual thermostat on a 2 stage heat pump with a Honeywell RTH7400 programmable unit. I'm having trouble matching up the wiring. I have: W2 R B Y G X The Honeywell thermostat has receptacles for the following:

Installing RTH7400 Honeywell Thermostat [ 1 Answers ]

I am replacing my (old) Honeywell T8411R thermostat with a (new)Honeywell RTH7400 programmable thermostat. I need help wiring to the new thermostat. My H/C system is a heat pump system. The old thermostat is wired to the following terminals: W1 - White W2 - Brown G - Green R - Red C - Blue...

Installed Honeywell RTH7400 Thermostat but get no power [ 2 Answers ]

I have tried to comb through the threads to find a problem that fits mine, but I didn't find it. So please forgive me if this is a repeat question for something that has already been presented. I have just installed 2 Honeywell programmable thermostats (RTH7000 series). The one for my...


View more questions Search