I wish to control the temp. in a small insulated area
I wish to control the temp. in a small insulated area (4'X4') with a Hunter 24v thermostat. I have purchased a Omron G2R 24v relay to control line voltage (120VDC) to simply turn off and on power to a heat lamp. I can't seem to get the contacts to operate in the relay with the thermostat. What else do I need and what is the wireing diagram for this setup?
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 23, 2012, 11:57 AM
|
|
|
So the heat lamp is the only source of heat, right?
|
|
|
 |
Uber Member
|
|
Mar 23, 2012, 01:27 PM
|
|
|
Have one wire from 24 volt power source, I assume you have a small 120 volt ac to 24 volt ac transformer, to stat, then to coil of relay, have the remaining contact on coil run back to remaining connection of the 24 volt source.
Be sure the coil voltage rating matches the 24 volt source.
|
|
|
 |
New Member
|
|
Mar 24, 2012, 09:16 AM
|
|
|
 Originally Posted by tkrussell
Have one wire from 24 volt power source, I assume you have a small 120 volt ac to 24 volt ac transformer, to stat, then to coil of relay, have the remaining contact on coil run back to remaining connection of the 24 volt source.
Be sure the coil voltage rating matches the 24 volt source.
The heatlamp is the only heat used to heat the (4'X4') space. My thermostst is powered by two 2AA batteries, same as used to control home AC. I have followed the (two wire heat only instructions) that came with the thermostat but I can't get it to open and close the points in the relay (which in turn would turn off and on the 120v power to the heat lamp. What am I doing wrong?
|
|
|
 |
New Member
|
|
Mar 24, 2012, 09:32 AM
|
|
|
The heatlamp is the only heat used to heat the (4'X4') space. My thermostst is powered by two 2AA batteries, same as used to control home AC. I have followed the (two wire heat only instructions) that came with the thermostat but I can't get it to open and close the points in the relay (which in turn would turn off and on the 120v power to the heat lamp. What am I doing wrong?
My thinking is ,if the 24v thermostat will control the AC for a home, why not for the smaller space (4'X4'). So I bought a 24v DC -120v/220v AC relay for the 24v thermostat to control as an off and on switch that would be turning on and off the heat lamp at a set temp.
Thanks so much for your first response, tkrussell.
|
|
|
 |
Electrical & Lighting Expert
|
|
Mar 24, 2012, 12:12 PM
|
|
|
Do you really think the two AA batteries are providing the 24v needed to operate the coil in the relay?
The AA batteries are to run the thermostat only, NOT the load it is controlling. The thermostat is basically just an automatic switch.
You need a 24v power source, such as a transformer like TK mentioned. The thermostat will control this 24v source to power the coil of the relay, the contacts in the relay will control the heat lamp.
The wiring diagram is on the relay itself. You just have to wire the coil power through the thermostat like we have been saying.
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 24, 2012, 12:43 PM
|
|
|
Stan is correct, two AA gives you either 1.5 volts or 3 volts, enough to make the chip in the stat work, not the 24 volts.
|
|
|
 |
New Member
|
|
Mar 24, 2012, 06:01 PM
|
|
|
Thanks Guys:
I am not knowleggable about voltage and such. That is the reason I came to you. You have been very helpful I will add a transformer and try it again. Thanks again.
|
|
|
 |
New Member
|
|
Mar 25, 2012, 02:54 PM
|
|
|
I would still need to know what kind/type of transformer I need to look for to finish my project. Again my thermostst is operated by two AA 1.5 batteries and I have a five pin 24V relay. What should I ask my electrical supply house to get the correct transformer?
The relay has two pins for 24V and three pins for choice of open or normally closed contacts.
|
|
|
 |
Electrical & Lighting Expert
|
|
Mar 25, 2012, 05:23 PM
|
|
|
If you hard wire the transformer to the relay the coil would be energized all the time. The thermostat will break one line between the trans and relay.
The diagram on the relay will tell you which terminals will be N-O and N-C. You want N-O, so when the t-stat makes it will energize the relay coil and close the "normally open" terminals.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Hiding in a closet or small area
[ 2 Answers ]
What do you think of someone who gets upset and wants to find a small place to go, (maybe hide) even though she is alone at the time.
It's almost like she wants to get away and that is the best she can find. No one else is with her in the home, but she still wants to go in the far back of the...
Temp control
[ 3 Answers ]
I bought a Maytag stainless french doorw/ water and ice dispenser on clearance at Lowe's. The problem is that the refrigerator section freezes the everything. It has on the front of the icebox a refrigerator and freezer temp. control. When I try to raise up the refrigerator temp. the refrigerator...
Grohe Grohtemp temp control
[ 5 Answers ]
Our new condo came with a Grohtemp shower unit. Is it possible to adjust the thermostat so the water will get hotter then it currently allows?
Paul
View more questions
Search
|