    Wiring a two wire 240volt breaker into a three speed motor
    I'm trying 2 hardwire my attic fam motor into a already installed 240 breaker.my fan motor is a 3peed 208/230 volt motor and the breaker is a 2 hot wire breaker how would I wire the 2 hot wires into the motor and would I need to run a wire from the netural bus bar and the ground bus bar of the fuse box to the motor?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Oct 20, 2017, 12:51 AM
    Is this the same motor you previously asked about? 2 hots and a ground for 240.
    minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #3

    Oct 20, 2017, 02:07 AM
    Yes I just need to know how to connect the two hot wires and do I need to add a ground and a netural wire
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Oct 20, 2017, 05:03 AM
    If you want exact instructions, you need to give us the model number of the motor. You will find that on the motor's nameplate. If I have the model number I can get the wiring specs from the Dayton or Grainger websites.

    Okay, your replacement motor should have come with installation instructions. Those instructions will show you how to connect the two Line wires and the Neutral and Ground wires to the motor for the 240V connection.

    What is the amperage of the installed circuit breakers? This is critical to the sizing of the cable from the breaker to the fan's junction box.

    The wires going to the fan motor from the panelboard, are they a cable or individual wires in conduit? If they are in conduit, then you can pull a Neutral (White) from the panelboard to the junction box.
    However, the wires are in a cable sheath, then you will have to pull a new cable from the panelboard to the junction box for the fan connections. You will need a cable sized for the fan motor's "FLC" and multiplied by 1.25.

    It looks like a "copper" 14/3 with ground would be sufficient, however, I would choose a 12/3 w ground if it was me doing the work. ********Also, if I looked at the correct motor in the Grainger catalog I would not use a circuit breaker larger than 10 amps.
    minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #5

    Oct 20, 2017, 10:23 AM
    Mfr mode#l4m101 at grangers the installed breaker is 40amp the motor wires individual
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Oct 21, 2017, 03:49 PM
    Okay, we were looking at the same motor at least.

    This motor does not require a Neutral. One conductor will go to the purple conductor and the other goes to the switch.

    A 40 amp circuit is way to high for this motor, given the horsepower of the motor I would not go over 15 Amp.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Oct 21, 2017, 08:35 PM
    There is no neutral on a 240 VAC setup for a motor, hot, hot, ground. A dryer 120/240 split uses a 4 wire hot, hot, neutral, ground. The wiring diagram for the motor should show hots to the switch and ground straight through. Wires from the switch go to the motor lugs. A 3 speed motor would have windings with taps. Ground goes to the motor frame. Is there a capacitor in this motor? This must be a very large attic fan motor. I have never seen a 240 in a residence, 2 speed 120VAC is most common. Do you have a 3 way switch too? Rotary lo-med-hi? No diagram on it?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Oct 22, 2017, 06:26 AM
    1. Here is the wiring doc from the Grainger website.
    Attached Images
  1. File Type: pdf 4M101_4.pdf (52.7 KB, 293 views)
  2. minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #9

    Oct 22, 2017, 08:30 AM
    My fuse box is full so can't add another fuse,so what I am doing is adding the attic fan to this 40amp breaker already installed with a load that pulls 27/27amps and the attic fan motor pulls 3.9-4.3amps. So would the breaker be able to handle both loads? there is no purple wire on this motor only(red,blk,blu,wht,brn,brn w/wht,yellow,and orange)
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #10

    Oct 22, 2017, 10:17 AM
    "Fuse box" or is this your usage term for a breaker box?
    1. My fuse box is full

    Sorry, your comment regarding attaching the new fan, with a 14 or 12AWG wire to a 40 Amp breaker, defies logic. No, you won't overload that circuit but your fan circuit will be totally unprotected since the fan can fail and the 40 Amp breaker will not trip. Great way to burn your house down. Please, get a local electrician to do the work.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #11

    Oct 22, 2017, 10:51 AM
    You need to stop here and get real honest with us. You indicated that you were replacing your existing fan motor, not extending an existing circuit.

    The 240V circuit you want to extend to this fan, what is it used for? There are some circuits that by definition are dedicated and there are some circuits that the appliance manufacturer will require a dedicated circuit for. If you are intending on extending a circuit from a dedicated circuit, that is a serious code violation. Also, it is very risky putting a 40 amp circuit to a motor that at worst case would only need 15 amps.

    I looked at this motor on the Grainger website and I do see a "Purple" conductor on the motor. I do not see an Orange conductor.

    The Brown & (Brown/White) conductors are for the capacitor. The Black (high) - Blue (Med) - Red (Low) are for the output of the switch.

    Rotation of the motor is controlled by switching the Yellow and Purple connection caps.

    Orange is not shown or pictured. It would be speculation at best but it appears to me that Purple has been swapped out for Orange. You really need to contact Dayton and / or Grainger to make sure.

    There are notes on the website directing you to review the installation instructions that are packaged with the motor. Do you have those instructions?

    FYI - the conductors for a 40 Amp circuit require a #8 AWG conductors. The motor's leads are to small for that amperage and will either melt or burn if an over amp occurs. Not to mention the switch, what amperage is it listed for?

    You might want to consider installing a secondary panelboard for these two circuits and feed that panelboard from that main panel. This would allow you to set up the two circuits from the secondary panelboard and protect each circuit with the proper breakers for the required conductors.
    minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #12

    Oct 22, 2017, 11:48 AM
    Nobody said anything about the wire size so please do not reply to any of my ouestions thanks
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #13

    Oct 22, 2017, 11:50 AM
    I'm sorry that you do not like the answer, however, would you rather have a fire because you placed 40 amps across a wire that is only listed for 15 amps?

    Because that is what will happen if you just tap onto a 40 amp circuit.
    minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #14

    Oct 22, 2017, 11:57 AM
    Understand nothing has been done am just asking question as I said before the manual says a purple wire but the motor does not have a purple wire only orange so I'm thinking the orange wire works the same as the purple wire would

    My reply was not to you donf
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #15

    Oct 22, 2017, 12:17 PM
    I agree that the purple wire may have been changed to Orange, however, that answer must come from Dayton.

    It may be as simple as running out of purple wire during a production run and Orange was substituted. I've seen that happen lots of times. However, Dayton should have either amended the instructions or put in an errata identifying the change.

    With respect to the wiring comment by MA061, he is absolutely correct. A #8 AWG copper and insulation wire is listed for 50 Amps. That's an incredible amount of heat from the current passing through it. On the other side of the spectrum is a "14 or #12 AWG wire. Neither of those wires can handle anywhere near that amount of heat and will melt and possibly burn. If those same conductors touch, the resulting spark can and will cause a fire.

    Setting a secondary panelboard and using it to fed two 240 volt circuits is the safest way to go.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #16

    Oct 22, 2017, 05:54 PM
    My point is this-SAFETY for you, your family and your home. What you are attempting to do is improper from a code standpoint and can be dangerous. The breaker or fuse protects the lowest amperage in a circuit, not the highest. You also need to understand that wiring for a motor is different than a straight resistive load. How do you plan to switch speeds? Is your controller designed for 240VAC? We would be remiss to tell you "sure, hook it up this way". The safest way to install this motor is to use a subpanel and run a new wire or, use a 2 pole breaker if it will fit. Don't be tempted to put 2 wires on 1 breaker, that is not code unless the breaker is specifically rated for same.
    minibike6969's Avatar
    minibike6969 Posts: 78, Reputation: 1
    Junior Member
     
    #17

    Oct 26, 2017, 07:39 AM
    I'm sorry had to call granger to the right diagram the motor I have is #4m101bg4M101_6.pdf now how would I wire the two hot wires and what size wire
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #18

    Oct 26, 2017, 01:17 PM
    Sorry, but there are no installation instructions in that document. The last page does show electrical connections but I believe these are internal to the moto.

    The motor you have should have a "Name Plate" on it, please either take a picture of the label or place the Model number from that label into this thread. I'll wait for your response.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #19

    Oct 26, 2017, 01:28 PM
    Question: Do you have a White conductor and A Black conductor going to the motor?

    It might be that Dayton just assumed a Black/White cable but you have a Black/Black.

    If that is true, then one of your Black wires will go to the White lead. The other Black would go to the black that feeds the switch.

    As to the wire size, the smallest household conductor you can use for this circuit is #14 AWG. This would allow up to 15 amp. As discussed earlier, if you put the 40 amp from those two breakers across those two 14 AWG conductors you will most likely create a fire situation.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #20

    Oct 26, 2017, 02:38 PM
    OKAY!! Sorry for the length of this response, but please read it.

    Stand the motor on its back with the Armature will be sticking up. Look at the label, over on the right side under the barcode you will see the wiring diagram.

    The top two wires are the source connections. The first wire (White) is listed as common, connect this wire to one of the black conductors from the breakers. The other black conductor from the breaker goes to the black from the motor.

    This motor will only draw about 4 amps when running. On a 40 amp circuit, it will still only pull 4 amps. The danger becomes extreme if for any reason the moto locks up. If that happens the motor will keep trying to run until it literally burns up. That's why you do not want it on a 40 amp circuit.

    Fortunately, this motor has internal "Overprotection" which wiil trip out to protect the motor.

    Now, how you get from the outlet to the fan is another story. You just cannot connect a #14 AWG conductor to a 40 amp circuit you have seriously compromised the safety of your home. So you would have to wire #8 conductors from the outlet to the fan and then connect the fan conductors to the supply conductors.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring help, 2 speed condenser motor to 1 speed motor... [ 0 Answers ]

Ok, I am replacing my condenser fan motor on a tempstar smart comfort 2000, the old motor(2speed) has 5 wires, red, black, brown, blue, and green the new motor(1speed) also has 5 wires, white, black, brown, brown/white, and green.the schematics I can find for the motors, show white-red,...

I have a Jandy 2 speed motor to replace a 1 speed motor - help with wiring [ 5 Answers ]

Hi, I have a Jandy 2 speed motor to replace a 1 speed motor and need help with wiring. Before removing the old motor, I wrote down the colors of the wires to the old motor terminals (L2 blue, l1 black). Both went to a timer (black on position 2 of timer, blue on position4 of timer). The new...

Emerson motor condenser wiring replacing 3 wire motor with 5 wire. [ 5 Answers ]

Any recommendations? New motor apparently is capable of running in either direction by switching brown and purple wires going to the capacitor. Looks like then either the remaining brown or purple is spliced to or hooked up to the same terminal as the yellow. Thanks.

How to wire an AC motor and 3 speed control? [ 1 Answers ]

I scavenged an AC 240V motor out of a desk fan and I'm trying to wire it to a 3 speed button control of a similar fan. Problem is the wiring is quite confusing. There are seven wires out of the motor white - brown - 2x red - 2x blue - ground How am I to wire it to the controller and the...

Wiring a 2 speed blower motor [ 1 Answers ]

I scavenged a working motor from our old furnace a/c unit and recently installed it (and ductwork) in my basement to draw excess hot air from around our fireplace insert on the main level. Unfortunately the motor only seems to be blowing in the a/c mode which is much too fast even for pulling hot...


View more questions Search