    Wiring to subpanels
    We are putting a large 2 story addition on the back of our house. I am installing 2 sub-panels; 1) a 60A panel upstairs for a few general lighting circuits and a 20A 2-pole circuit for a jet tub, and 2) a 125A panel downstairs to power general lighting, kitchen appliances (electric wall oven @ 40A but an all gas range), outside lighting, and 2 AC compressors @ 30A each. For the upstairs panel I ran #6-3 nm-b. Both panels will be fed from an existing 200A main panel with plenty of room for additional circuits. The run from the main to the upstairs panel is about 80 ft and the run for the downstairs panel is about 70 ft. I'm looking for advice/suggestions as to what to use for the supply run for the downstairs panel. From the charts it looks like I need either #1 or #1/0 depending on the conductor and insulation types. I am hoping to use a flexible conduit because the run between the panels is through a basement and a crawl space and is anything but straight and unobstructed. Any advice on the type of materials to use would be greatly appreciated. Also, if there are any red flags in my description please feel free to point them out.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 20, 2009, 03:27 PM
    I would use #2 Aluminum 4 wire SER Cable, and use a 2 pole 100 amp breaker to feed the downstairs panel.

    A local code may require to sleeve the conduit as it passes through floors .

    Read Article 338 of the:

    https://www.askmehelpdesk.com/electr...ne-270277.html

    To learn how to treat and install. See the attached manufacturers instructions for terminating aluminum wire.

    At the new panel, keep the neutral insulated form the equipment grounds, use a separate accessory equipment ground bar bolted to the metal panel box using machine screws for all green and bare equipment ground wires.
    Attached Images
  1. File Type: pdf Alcan RecommendationsforConnectors.pdf (9.1 KB, 502 views)
  2. rbs10's Avatar
    rbs10 Posts: 3, Reputation: 1
    New Member
     
    #3

    May 20, 2009, 06:06 PM

    Thanks, You threw a bunch of new stuff at me. Let me do some research based on your info and I will see if I need to ask for more help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp to 100 amp subpanels [ 1 Answers ]

I am upgrading the service to the residents from a 100 amp service to a 200 amp service. I am planning to install a 200 Amp Load Center at the service entrance in the house. Would I be within code specs if I make a 60 foot run of 1-1/2" PVC schedule. 40 conduit holding three #3 THHN conductors and...

200 amp main panel: 2 100 amp subpanels? [ 1 Answers ]

I was asked to by a homeowner to help with a wiring project. She has 1 200 amp main panel and 1 100 amp subpanel. Both are full yet she needs more circuits for a bed n' breakfast. Can another 100 amp subpanel be installed?

Trying to run 2 100 amp subpanels -what size wire? [ 3 Answers ]

Ok, I am new to the site, but I have looked and looked and not found the answer to my specific questions. Many questions are similar but do not have the same specific circumstances and I have asked many people including electricians and I get different answers from everyone I ask so I am seeking...

100amp and 50amp subpanels [ 4 Answers ]

I am looking into installing 2 sub panels. The reason for this is the location of the current box in a finished room, with a finished ceiling. And the rest of the basement is NOT finished, and I don't want to mess with running a bunch of stuff through a finished ceiling. So I figured I would run...