Can you downsize the whip on the hot tub?
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 2, 2013, 03:14 PM
|
|
|
"The" hot tub? Which hot tub is that?
How about you start by telling us something about this project? Then maybe someone can help you.
|
|
|
 |
New Member
|
|
Feb 2, 2013, 08:47 PM
|
|
|
220V 60 amp line (#6) to the 60 amp GFI disconnect. Can the whip to the tub be downsized at all? I know the ground is but what about the 8' whip?
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 2, 2013, 09:04 PM
|
|
|
Correct. If the disconnect had a 60A breaker then #6cu is the smallest wire you can use.
The tub may not require a 60A circuit though.
Tell us more about the tub and we can tell you if you have any other options.
|
|
|
 |
New Member
|
|
Feb 2, 2013, 09:17 PM
|
|
|
Just wondering because I seea lot of 220v 50a double ovens with an attached whip and it will be #10 wire.
|
|
|
 |
Uber Member
|
|
Feb 3, 2013, 04:11 AM
|
|
|
Whip on an appliance that is installed by the manufacturer is different than a whip that must be installed in the field. The whip on the appliance was present, tested and listed by UL as is.
The "whip" on a hot tub is installed in the field and is nothing more than a continuation of the branch circuit, and must be sized the same as the branch circuit.
Last call, please answer Stan's questions.
|
|
|
 |
New Member
|
|
Feb 3, 2013, 12:20 PM
|
|
|
 Originally Posted by tkrussell
Whip on an appliance that is installed by the manufacturer is different than a whip that must be installed in the field. The whip on the appliance was present, tested and listed by UL as is.
The "whip" on a hot tub is installed in the field and is nothing more than a continuation of the branch circuit, and must be
sized the same as the branch circui
Last call, please answer Stan's questions.
I understand UL listed, but you did not answer the question in theroy. What do you mean by " answer Stans questions?" He needs more info? FOR REAL?
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Feb 3, 2013, 01:42 PM
|
|
|
How is the hot tub labeled, what's its draw
|
|
|
 |
New Member
|
|
Feb 3, 2013, 02:40 PM
|
|
|
 Originally Posted by ballengerb1
How is the hot tub labeled, whats its draw
Thanks ballenberg. The jobs already done, I used #6. Don't know the draw, just specified 60 amps. I just though it was an easy question that could be easily explained... seems like if a double oven down sizes the whip because its tested and ul listed then they woiuld list it as the size of the whip. The whip is also just a continueation of the line. Stans not making since with his analogy.
Thanks anyway guys
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 3, 2013, 03:32 PM
|
|
|
Neither are you! Comparing an oven to a hot tub? How in the world are they similar? Because both are 120/240V loads? Sorry, that doesn't cut it.
It's only in your last post that you even told us the specs on the tub (that it calls for a 60A circuit). That is what I was asking. You just kept comparing it to an oven with giving us any details about this tub.
Sorry if our mind reading skills were a bit off today. I'll try and do better next time.
|
|
|
 |
New Member
|
|
Feb 3, 2013, 03:39 PM
|
|
|
Sorry Stan. I did say 60 amps in a couple of post ago. OK, lets change gears. How about an oven. I am asking why an oven is rated at 50 amps and has a #10 whip?
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 3, 2013, 05:13 PM
|
|
|
I am asking why an oven is rated at 50 amps and has a #10 whip?
Because an oven whip is not under the jurisdiction of the NEC. It is overseen by UL. As long UL testing considers it safe and adequate it gets a listing.
|
|
|
 |
New Member
|
|
Feb 3, 2013, 06:33 PM
|
|
|
Thanks Stan, now I get it. Never thought about it that way. I those cases the oven must never pull more than 30 amps for a long period huh? Same theroy as a 20 amp appliance circuit and using a 15 amp duplex, it's rated at 15amps but by code it's OK.
Go figure...
|
|
|
 |
New Member
|
|
Feb 3, 2013, 06:34 PM
|
|
|
[QUOTE=dcrigger;3387243]Thanks Stan, now I get it. Never thought about it that way. I those cases the oven must never pull more than 30 amps for a long period huh? Same theroy as a 20 amp appliance circuit and using a 15 amp duplex, it's rated at 15amps but by code it's OK.
Go figure...
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Size of wiring trough
[ 6 Answers ]
I'm unsure of what size wiring trough to use . I'm coming into the trough from the meter pan with 500 MCM (320 amp single phase service) I'll be coming out to two 200 amp service disconnects and using 3/0 wire. An electrician neighbor of mine recommended a 12" X 12" X 48" trough but the...
Electric wiring size for underground
[ 1 Answers ]
I am running underground from a 100 amp panel (in house) to my new garage approx 150 feet away. What size wire (would 10/3 work?) would work if I needed 220v as well as 110 lights and 110 v outlets ?
Range wiring - breaker and conductor size
[ 4 Answers ]
This weekend I will be wiring a 120/240v 8,800 watt range (oven with 4 burners on top). My questions concern wire and breaker size. I've asked about this before and I still cannot determine the best answer.
I understand that under the NEC, the minimum sized circuit for a range is 40 amp, using...
HVAC Wiring Size for Geothermal units
[ 6 Answers ]
I've found a number of these type of questions in here and I thought I'd post my own, with what I *think* my solution is.
I have two geothermal units
The first Geo unit has this...
Min CKT Ampacity = 25.6 A
Max HACR = 35 A
The second unit has this...