New Member
|
|
Dec 26, 2007, 07:24 PM
|
|
|
Wire Gauge?
I've been looking for 2 days for an online wire gauge calculator.
I'm going to relocate my meter to the side of my house (converting from overhead to underground service), then I'm going to remove the existing electrical panel (from the outside of the house) and install a breaker panel on the inside of the house, opposite of where the original service panel was located.
I need to know what gauge wire to run from the new meter to the new panel
200 Amp Service
30 foot run
|
|
|
 |
Uber Member
|
|
Dec 27, 2007, 05:34 AM
|
|
|
A residential 200 amp service can use a minimum of #2/0 copper or #4/0 aluminum wire.
There is no on line calculator that I know of, due to so many variables.
Keep in mind, the conductors feeding the meter, and the meter itself, needs to be rated 200 amps.
If the Main breaker will be in the panel, then use 3 wires from the meter to panel, if the Main is at the meter, then 4 wires are needed, the fourth being the equipment ground, which can be either a #6 copper or a #4 aluminum.
|
|
|
 |
New Member
|
|
Dec 27, 2007, 08:33 AM
|
|
|
 Originally Posted by tkrussell
A residential 200 amp service can use a minimum of #2/0 copper or #4/0 aluminum wire.
There is no on line calculator that I know of, due to so many variables.
Keep in mind, the conductors feeding the meter, and the meter itself, needs to be rated 200 amps.
If the Main breaker will be in the panel, then use 3 wires from the meter to panel, if the Main is at the meter, then 4 wires are needed, the fourth being the equipment ground, which can be either a #6 copper or a #4 aluminum.
Thanks - I was thinking of running #4/0 copper, just to be safe.
One more question - Do I need to run the wires through conduit from the meter to the panel, if the wires are going to be in the attic?
Also - I already have a uffer ground in the existing panel. Is there a reason why I cannot run the ground from the new meter (with a main) to the existing panel and tap into that uffer ground or do I need to run a new uffer ground?
|
|
|
 |
Uber Member
|
|
Dec 27, 2007, 04:33 PM
|
|
|
If you can afford to pay for more copper than needed, I have no problem with that. Exceeding the code is fine, and recommended.
Depends on what kind of wire your familiar with. If this is a multi-wire cable, such as SER, then no conduit will be needed unless it can be damaged.
If your planning on using something like THHN/THWN, or XHHW, individual wires, then a complete conduit system is needed, with all the fittings, locknuts, etc. so the entire run of wire is enclosed in raceway from box to box.
Your existing ufer ground system will be fine, From the neutral lug in the main switch run #4 copper to the ufer tail, and use a irreversible connection to join both wires. This can be a compression connector.
|
|
|
 |
New Member
|
|
Dec 27, 2007, 10:05 PM
|
|
|
 Originally Posted by tkrussell
If you can afford to pay for more copper than needed, I have no problem with that. Exceeding the code is fine, and recommended.
Depends on what kind of wire your familiar with. If this is a multi-wire cable, such as SER, then no conduit will be needed unless it can be damaged.
If your planning on using something like THHN/THWN, or XHHW, individual wires, then a complete conduit system is needed, with all the fittings, locknuts, etc. so the entire run of wire is enclosed in raceway from box to box.
Your existing ufer ground system will be fine, From the neutral lug in the main switch run #4 copper to the ufer tail, and use a irreversible connection to join both wires. This can be a compression connector.
Thanks so much for the info.
If you need any automotive advice, hollar. I'm a ASE Master Auto and ASE Master HD truck Technician with 30 yrs experience.
|
|
|
 |
Uber Member
|
|
Dec 28, 2007, 03:00 PM
|
|
|
Thanks for the offer, but at my age, I don't work on vehicles at all, period. What with all the computers and electronics in my Explorer, I know my limits, and will hire a pro for any work needed, short of changing light bulbs, filters, and air in the tire.
My wife lets me drive it once a week, so I can get it cleaned and LOF when due.
I will say, you kind of concerned me when asking if conduit is needed for the wires to the panel. What did you decide to do?
|
|
|
 |
New Member
|
|
Dec 28, 2007, 06:36 PM
|
|
|
 Originally Posted by tkrussell
Thanx for the offer, but at my age, I don't work on vehicles at all, period. What with all the computers and electronics in my Explorer, I know my limits, and will hire a pro for any work needed, short of changing light bulbs, filters, and air in the tire.
My wife lets me drive it once a week, so I can get it cleaned and LOF when due.
I will say, you kind of concerned me when asking if conduit is needed for the wires to the panel. What did you decide to do?
I bought 3 25' sections of #3/0 and 25' #6 bare copper.
I'm going to come into the new 200A Cutler-Hammer ranch panel underground (c/o local utility company) via 2" conduit.
Thru the meter and to the 200A main. The main feeds a set of lugs and 8 breaker spaces.
From the lugs, I'll run the #3/0 out the top of the panel and into 2" conduit up to the eaves.
I'll punch a hole in the eaves and turn the conduit into the attic via a 2" LB Access.
I'll run 2" conduit sitting on top of the rafters to another 2" LB and run the wire down the wall, through the wall top. Once I am in the wall, I'll not need to use conduit.
I'll then come into the new 200 AMP distribution panel (which is opposite of the original panel on the outside of the house).
Once I do this, I can have the local util company come and run a new service line from the pole, to my ranch panel.
Tomorrow, I'm renting a ditch witch to dig the 60'x3' trench for the new service line.
Monday, the util company is coming out to inspect the ditch - once they OK the ditch and conduit, I can fill the trench in and start working on the wiring.
I'm REALLY not looking forward to pulling 3 strands of #3/0 wire, 25' through conduit, laying on my belly in the attic. I'm going to try pulling from the attic to the eaves, which should make it a little easier.
|
|
|
 |
Uber Member
|
|
Dec 28, 2007, 09:08 PM
|
|
|
No, no, no, do you really mean: "Once I am in the wall, I'll not need to use conduit.".
This is not proper, do not do this.
As I stated before, the conduit system must be a complete run, using connectors and locknuts, from BOX TO BOX.
If you do what you stated, you have violated so many codes, and standard installation practices, your home will be a model of what not to do.
If you do what you stated, get it inspected by the local inspector see what he has to say, and be ready to rip it out and redo it.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Wire service, wire gauge 100 amp
[ 9 Answers ]
I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...
Wire gauge & breaker amp for A/C
[ 3 Answers ]
Would I need to change out my 40 amp to a 35 amp breaker if my a/c unit calls for those specs or will the existing be okay. Oh yea 10G wire is in place now. I'm talking about a 3 ton heat pump split unit.
Wire Gauge and Amperage
[ 8 Answers ]
If the wire gauge to a machine is changed, will the voltage/amperage to the machine automatically change? Or does it matter what the machine actually uses?
In my case, the amperage was already much lower than the original wire gauge, but now the wire gauge will match better with the actual...
Connecting 14 gauge wire and 12 gauge wires in the same blue box.
[ 2 Answers ]
I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire.
I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...
Gauge of wire?
[ 1 Answers ]
Thank you for responding.
I would like to know what size of wire I need to run a circuit 125 amp, 240V to a sub panel 244 feet away?
Or, what size of wire I need to run a circuit 60 amp, 240V to a sub panel 244 feew away?
Thank you in advance
View more questions
Search
|