Ask Experts Questions for FREE Help !
Ask
    BJB126's Avatar
    BJB126 Posts: 2, Reputation: 1
    New Member
     
    #1

    Dec 2, 2013, 03:17 PM
    Why does the breaker trip when I turn the light switch from on to off
    I am installing a light switch from ceiling lights to wall switch. I hooked up the white wire to one terminal and the back wire to the other terminal. The light switch in in the on position. I turned the breaker back on the lights are on. When I switch from the on position to the off position the breaker trips. Why?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Dec 2, 2013, 03:29 PM
    Where does the power come from? Only 2 wires in the switch box?
    sknowman's Avatar
    sknowman Posts: 31, Reputation: 1
    Junior Member
     
    #3

    Dec 2, 2013, 04:45 PM
    To be clear, you hooked the black wire and the white wire to the ceiling lights, and ONLY the black to the switch, right? The white wires should be securely twisted and nutted together inside the switch box, and the black wire broken across the switch
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Dec 2, 2013, 05:25 PM
    You have wired it wrong and are shorting the breaker. Answer my first post.
    BJB126's Avatar
    BJB126 Posts: 2, Reputation: 1
    New Member
     
    #5

    Dec 3, 2013, 07:57 AM
    I should nut the white wire in the switch box and connect the black wire to one of the terminals on the switch. Is this correct?


    Thanks
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Dec 3, 2013, 10:35 AM
    You should not do that. It sounds to me as if you are trying to create a switch loop that will control two lights.

    Find the supply cable to the original light. The black conductor of the supply cable will connect to the white conductor of the switch. Place a piece of black tape on the white conductor to show that it is now a hot conductor! The Black conductor returning from the switch will connect to the black fixture wire on the light and to the black conductor that feeds the second light The white conductor from the light, the white conductor from the supply cable and the white conductor from the second light get connected together.

    At the second light, the black from the light gets connected to the black feed from the first light. The white from the light gets connected to the white from the feed of the first light.

    All ground conductors get connected together t each of their locations.

    That should do it for you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why is my breaker switch turning off when I turn light switch to off posiion [ 1 Answers ]

The box where my kitchen light fixture is located has 4 wires (each with a black and white wire inside for a total of 6 wires). I have determined one wire (wire#1) is providing power, (wire#2) is the power to an outlet in the bathroom, (wire#3) is power to outlet in dinning room, and (wire#4) is...

Light switch will turn off under cabinet light, but won't turn light back on [ 1 Answers ]

Hi all: I recently installed under cabinet lighting in my kitchen. I added a single pole switch to an existing GFCI outlet, and then wired said switch to a surface mounted receptacle on top of my cabinets. I wired everything up, and the lights work great. The problem: When I turn...

I plug in a new microwave 120 vac, turn it on high it trip the breaker, why [ 1 Answers ]

I plug a new microwave, turn it on high power, it ran for a few minute that it trip, the breaker, what cause it to trip.

When I turn off the fan light it trip the circuit breaker [ 1 Answers ]

When I turn off the fan light it trip the circuit breaker