410.16 Luminaires in Clothes Closets.
(A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire
(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
(B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
|
|
|
 |
Uber Member
|
|
Jul 13, 2010, 06:32 PM
|
|
|
Stan, it bites that the Quick questions seldom have quick answers?
310.16 concerning ampacities is more interesting?
|
|
|
 |
Electrical & Lighting Expert
|
|
Jul 13, 2010, 07:16 PM
|
|
|
310.16 is a mine field to the uninformed. :P
|
|
|
 |
Uber Member
|
|
Jul 14, 2010, 07:30 AM
|
|
|
Which edition of the National Electric Code?
Stan quoted the current code in effect, 2008 edition.
The Section 410.16 in the 2005 edition was Means of Support.
This section is often mentioned in installation instructions of light fixtures that the installation of the fixture must comply with NEC Section 410.16.
The instructions may not have been updated.
|
|
|
 |
Electrical & Lighting Expert
|
|
Jul 14, 2010, 09:33 AM
|
|
|
Good point TK, I never thought of that.
You'd think they would leave a few more numbers in between rather than leaving the section number the same and changing the topic.
Gotto love the NEC... NOT!
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Are 410 flarin kit
[ 2 Answers ]
I have been a ac tech for 17 yrs . And now with the r 410 systems becoming more prevealt,I've been seeing a lot of new tools on the market. Can anyone tell me what the difference is between a r 22 flareing kit and a r410. I do not want to buy one if I don't need one. Thank you
410 probation
[ 2 Answers ]
I just recently pleaded guilty to a drug charge I live in government housing my question is would a 410 probation show up as a conviction or as a arrest?the
Wire for 410 ft. Run
[ 4 Answers ]
I am having some trenching done to add a waterline close to my garden. Since I will already have the trench, I'd like to also run an electric line to a utility shed.
Questions:
1. Since the water line will be plastic of some sort, and not a conductive metal, does it matter how much spacing there...
AC 410 is carcinogen?
[ 1 Answers ]
We would like to buy a AC system and a vendor told us that 410(puron for carrier system) is banned from Europe because it is dangerous for our health, and there is a new product 412 that is coming on the market??
R-22 will be no more available in 2020 and the 410 is not good but 412 is not yet...
410 vs 22, reciprocating vs scroll
[ 2 Answers ]
I live in South Florida and need to replace a Carrier heat pump. Don't know why I bought a heat pump 15 trs ago seeing as we run heat maybe 3 days a year. Anyway I will go with a straight cool w/ 10 KW heat strip now. I have a gable mounted package unit. I will probably go with local contractor who...
View more questions
Search
|