What circuit breaker size should I use?
I recent purchased a heater that is rated 42.2 amps @ 240 volts. I was told by a licensed electrician that 8 awg would be fine for the heater. I have read some forums and now am questioning that also. I am wiring it in @ 220v So my questions are. Will it pull more amps @ 220v and if so how much? And will 8awg wire be good for the install?
|
|
|
 |
Uber Member
|
|
Oct 24, 2008, 01:33 AM
|
|
|
#8 will likely be fine unless the distance is excessive.
Most services in the US is 120/240. 220 has gone by the wayside.
To answer your question though, the heater will draw less amps at 220 V.
|
|
|
 |
New Member
|
|
Oct 24, 2008, 01:36 AM
|
|
|
 Originally Posted by KeepItSimpleStupid
#8 will likely be fine unless the distance is excessive.
Most services in the US is 120/240. 220 has gone by the wayside.
To answer your question though, the heater will draw less amps at 220 V.
Ty for your reply... So are you saying a 40 amp breaker will hold?
|
|
|
 |
New Member
|
|
Oct 24, 2008, 01:38 AM
|
|
|
Guess that was my next question... olol will a 40 amp breaker hold or should I step up to a 50.. and If I go 50 will I have to drop to 6awg?
|
|
|
 |
New Member
|
|
Oct 24, 2008, 01:40 AM
|
|
|
Usually when you step up in volts on a multi-volt unit... the amps drop. So I figured goind from 240 to 220 would pull a few more amps.
|
|
|
 |
Uber Member
|
|
Oct 24, 2008, 02:26 AM
|
|
|
That's a disagree. Can't change it.
|
|
|
 |
Uber Member
|
|
Oct 24, 2008, 02:27 AM
|
|
|
It's not correct to use a 50 A breaker and #8.
EDIT: #6 and 60 A breaker because on more than 3 hrs/day and breaker has to be rated > 125% of load, rounded up to nearest breaker size. Thanks, stan
|
|
|
 |
Electrical & Lighting Expert
|
|
Oct 24, 2008, 03:57 AM
|
|
|
WHOA guys!
First off forget the 220-240v thing. "220" is an old term that we just can't seem to shake. It's 230 or 240 volt. Commercial and industrial setting will also have 208v, but 99.999% of the time in a home it is 120/240v and nothing else.
NOW... this heater draws OVER 40 amps. You can completely rule out #8 NM cable. In fact, you can also rule out a 50A circuit. You cannot even use #8THHN in conduit as that is only rated for a 50A circuit. If an electrician told you #8 he needs to brush up on his code.
You need a minimum of #6 on a 60A breaker. Electric heat MUST be figured at 125%. 42.2x125%=52.75A minimum circuit. This get rounded up to a 60 since there is no 55A breaker.
If you are running NM cable you can run 6/2NM for this "straight 240v" circuit.
|
|
|
 |
Uber Member
|
|
Oct 24, 2008, 04:12 AM
|
|
|
Oops. It's on more than 3 hrs/day. Stan's right.
|
|
|
 |
New Member
|
|
Oct 24, 2008, 04:43 AM
|
|
|
Ty very much for your replys... you guys have given me more info tonight than Ive gotten anywhere in the last week. Stan you said a minimum on 60 amp and #6 awg wire. Would you see it safer with a 70 amp breaker? If so would 6awg still be good for the install. My main concern if overheating and fire of course. I want to be as safe as possible. Thanks again guys... GREAT HELP!!
|
|
|
 |
Uber Member
|
|
Oct 24, 2008, 08:32 AM
|
|
|
 Originally Posted by KeepItSimpleStupid
Oops. It's on more than 3 hrs/day. Stan's right.
Has nothing to do with being on more than 3 hours per day.
Branch circuits for electric heat is always rated 125% of the load, period.
I saw this earlier, but had problems getting back online, glad that Stan picked up on this.
The electrician that said #8 was fine scares me.
|
|
|
 |
Electrical & Lighting Expert
|
|
Oct 24, 2008, 11:55 AM
|
|
|
 Originally Posted by SmokebTp
Stan you said a minimum on 60 amp and #6 awg wire. Would you see it safer with a 70 amp breaker?
No, 60 is more than enough "cushion".
|
|
|
 |
New Member
|
|
Oct 24, 2008, 11:59 AM
|
|
|
Thanks again guys great help!!
|
|
|
| Question Tools |
Search this Question |
|
|
|
Check out some similar questions!
Circuit breaker size for several 300 watt flood light
[ 10 Answers ]
I like to install 4 sets of flood lights. Each set is a pair of 150 watts bulb, for a total
Of 300 watts per set, for a grand total of 1,200 watts for all 4 sets.
Can I put all 4 sets of flood ligts on a 15A circuit?
This is the way I like to install them: 2 sets of flood lights for the back...
Replacing Circuit Breaker with Higher AMP Breaker
[ 8 Answers ]
Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...
Compatibilities between awg wiring, breaker amp size, outlet amp size
[ 4 Answers ]
Hi. Is there a resource out there, prefereably on the web, that outlines the compatibilities between awg wiring, the breaker amp size, outlet amp size, how many recepticles/outlets can be on x amp outlet, etc?
For example, it would be nice to see something that shows: you can use a 20 amp...
Replacing a circuit breaker with a GFI breaker- q on neutrals
[ 1 Answers ]
In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!
View more questions
Search
|