New Member
|
|
May 2, 2009, 05:36 PM
|
|
|
What is the blue 12awg wire attached to in the box?
I have a hot tub with 4 wires coming from the hot tub controls to be attached to the shut off box 8 feet away. Two wires, one blue, one red are 10awg, apparently 110volts each incoming. Two additional wires, one blue, one red are 12awg and would appear to be for the second cirucuit, with a 15 amp breaker associated. Additionally there is a white, grounded neutral conductor and a green grounding conductor wire. My question is which 12 awg goes to the hot side of the 15 amp circuit and which one goes to the neurtal bar? There are only two connection left so it has to be one or the other but the colors are throwing me. I though the grounded conductor (neutral) was supposed to be white or white with stripes or maybe gray - A little help would be appreciated.
Slim
|
|
|
 |
Uber Member
|
|
May 2, 2009, 05:51 PM
|
|
|
Not enough info to go on, but the following might be useful:
You seem to have a 4 wire spa. It will need L1, L2, G and N from the main panel.
Within the SPA box, the Neutral that will feed everything from that SPA box forward comes from the GFCI. The GFCI needs a line and load neutral if 120 circuits are provided.
|
|
|
 |
New Member
|
|
May 2, 2009, 06:17 PM
|
|
|
Yes, a 4 wire. L1 is a red 10awg, L2 is a blue 10awg, there is a neutral (white) and a green grounding wire. 2 more wires coming out of the spa control box that I want to also attach to the gfi are both 12awg (what I would expect for a simple 110 circuit. If one were red or black and the other white I would know just where it stick it - but one is red and the other is blue (same as the two 110 hots). I am trying to avoid attaching the neutral to the hot - It just occurred to me that it probably doesnot matter how I hook them up because, like in a duplex receptacle, it would still work(even though the neutral is supposed to be on the left). Ah, ha he said. What think you?
|
|
|
 |
Uber Member
|
|
May 2, 2009, 06:56 PM
|
|
|
I need better info. Even a pic of the inside of the spa box. You can post one using "Go Advanced/Manage Attachments".
The SPA likely has some 240 V circuits (heater) and some 120 V circuits (Pump and controls).
The way you wrote your last post suggests that the GFI is in the breaker box. Is it?
Read your first post again.
Best guess: The #10's are a 240 heater circuit
The #12's are for a 240/120 circuit for the pumps and controls when combined with the neutral.
For giggles check the voltages of the pumps by looking at the nameplates.
What does Additionally there is a white, grounded neutral conductor this mean in your original post.
|
|
|
 |
New Member
|
|
May 2, 2009, 07:42 PM
|
|
|
There is 3/4 liquid tite line attached to the spa, the other end is loose. Inside the liquid tite are 6 wires, 1 blue 10awg, 1 red 10awg, 1 blue 12awg, 1 red 12awg, 1 white and 1 green. The gfi is in the box I bought to mount on the wall of the house about 8 ft away (or as the code says more than 5 feet but less than 50 feet and in plain sight). The box has a double breaker gfi (60 amps) and a 15amp single breaker. Since there are 6 wires going in to the spa control box and the same 6 coming out of the unconnected end, my dilemma is what to do with the two 12awg wires. On the breaker box schematic it show two wires (a black going to the 15 amp breaker and a white going to the neutral bar inside the box). The big red and the big blue are the 110 each coming in, the white is the neutral (what the code calls the grounded conductor) and the green, the ground (what the code calls the grounding conductor). However, I have a smaller blue and a smaller red and if I connect them to the 15 amp breaker I would be protecting the 110 circuit assuming only one of them is hot. Forgive me if I seem to be making this complicated, I was really just looking to extra careful. Thanks for the help - Slim
|
|
|
 |
Uber Member
|
|
May 2, 2009, 07:56 PM
|
|
|
Ahhh:
Looks like you have the wrong SPA panel.
See here: Wiring a Hot Tub - Electrical Installation and Wiring Diagrams
Under SPAS requiring special dual 240 V GFCI Sub panels.
Based on what you said this makes lots of sense:
12 AWG good for 20 Amps
#10 AWG good for 30 Amps
Colors make sense also.
The leads that you are labeling 110. Drop the 110 and call it 120. Actually they are two wires 180 degrees out of phase with respect to ground. Connecting a meter from the blue to the red will result in 240 V.
|
|
|
 |
New Member
|
|
May 2, 2009, 08:13 PM
|
|
|
Thanks so much for the help. I was looking at that site when you replied. 120 it is and another panel. Thanks again. Slim
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
How I fixed my RTH230B 'blue wire'
[ 5 Answers ]
Hi All,
This seems like the hottest place for Honeywell RTH230B questions, so I thought I would post what worked for me after much reading on this forum and troubleshooting.
My old thermostat had five wires: read, white, yellow, green, blue
The Honeywell connections for: Rh, Rc, W, Y, G
...
X1 Wire, blue
[ 1 Answers ]
:confused: Hello, I am trying to change out my themostat, I have a white-rodgers 1F58W-72, and I can tie all the wires ecept for a "X1" wire, which I don't know what it will transfer to. I have the these ready to put on my new digital thermostat, Y, W2, R, O, B, G; but nothing for the blue X1...
Blue wire on a carrier AC 38CKC060300
[ 2 Answers ]
The fan on my A/C unit stopped working. Sometimes it will start and run for a few minutes and then stop another time it just doesn't start, it tries to start but doesn't seem to have enough torque to start, even if I turn it it still doesn't continue but it tries.
I purchased a replacement...
Does gauge of wire attached to thermostat matter?
[ 3 Answers ]
I have just moved into my home and I replaced the two thermostats. The one in the basement had smaller wires than the one in the living room and was easy to install.
However the thermostat in the living room has thicker wires and when I installed it, it actually melted a part of the thermostat....
Loose Blue Wire
[ 1 Answers ]
I need some help finding out where this loose wire should go. We have a 9 year old house and lennox gas furnace 80MGF series. Were not getting heat, it has a slow flash(no call for heat)on the LED code. The emergency heat will ignight the burners and we can get heat that way, but I don't want to...
View more questions
Search
|